Water Coming out of vent pipe

Goto page 1, 2, 3  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
kiltedcamel

from United Kingdom

Joined: 27 Oct 2012
Posts: 32
Location: Hertfordshire,
United Kingdom

PostPosted: Wed Feb 27, 2013 10:23 pm Reply with quote

Hi,
My boiler is currently cutting out after a minute or so. It starts banging and sputtering and throwing water out of the vent pipe.

System - Gloworm fuelsaver 35f, hot water cylinder, 3 port valve, grundfos pump, 4 rads.

So I'm thinking a couple of things;
1 - Air lock, but no air is coming out of any of the rads.

2 - Sludge or other type of blockage. We have an air separator just after the flow pipe comes into the airing cupboard. When the banging starts, I notice the heat travelling up the vent pipe and not towards the pump. Once the banging stops, there is a lot of gurgling in the pipes and the heat eventually travels along to the pump. However by this time the boiler has overheated and cut off, and then the process just repeats itself like this!

So does anyone have an idea if its no 1 or no 2, or maybe something completely different?

If it is a sludge blockage, can I do anything about it myself. I have tried to search for a how to on cleaning system.

Is it drain some water off with hose pipe, add cleaner into small tank, let it run for a few days, then drain and refill with inhibitor?

Also I'm in a 1st floor flat, the drain valve is at the floor level at bottom of airing cupboard but this is not the lowest point as the boiler flow and return go under the floor.

Any help much appreciated.
Gloworm Fuelsaver F
Gloworm Fuelsaver F
Hot water Cylinder
Hot water Cylinder
feeder tank
feeder tank
honeywell thermostat
honeywell thermostat
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Breesey

from United Kingdom

Joined: 11 Jan 2006
Posts: 860
Location: Sussex,
United Kingdom
Thanked: 28 times

PostPosted: Wed Feb 27, 2013 10:38 pm Reply with quote

Is the vent pipe the tee nearest to and before the pump or does the cold water feed pipe come in between the vent and the pump?

Btw are you talking about the drain cock on the bottom of the cylinder? in that picture I mean.


Last edited by Breesey on Wed Feb 27, 2013 10:40 pm, edited 1 time in total
Back to top
 Alert Moderators
seco services

from United Kingdom

Joined: 03 Dec 2007
Posts: 15605
Location: Essex,
United Kingdom
Thanked: 1240 times

PostPosted: Wed Feb 27, 2013 10:40 pm Reply with quote

Sounds like your air separator is sludged up.

Try holding a magnet around the air separator see if it sticks.
Back to top
 Alert Moderators
kiltedcamel

from United Kingdom

Joined: 27 Oct 2012
Posts: 32
Location: Hertfordshire,
United Kingdom

PostPosted: Wed Feb 27, 2013 10:52 pm Reply with quote

I have taken a pic but its a bit hard to see.
The flow from boiler comes in to the air separator. The vent pipe goes straight up from the separator. The other side of the separator (going towards pump) has a feed coming from small tank a couple of inches along, from below.
If you look in between the 2 pipes in the foreground you can see the pipe exiting the air seperator, then the feed from small tank coming from underneath.

The pipe then goes to the pump, then to 3 port valve.

The drain valve is on the heating pipe, i'm not talking about cylinder drain valve

Back to top
 Alert Moderators
kiltedcamel

from United Kingdom

Joined: 27 Oct 2012
Posts: 32
Location: Hertfordshire,
United Kingdom

PostPosted: Wed Feb 27, 2013 11:04 pm Reply with quote

seco services wrote:
Sounds like your air separator is sludged up.

Try holding a magnet around the air separator see if it sticks.


Just tried the magnet and it didn't stick.

The flow pipe from boiler goes under the floor then about 3 metre along before re appearing at the airing cupboard. Could this lower section be where the blockage might be? As the system was drained a few months ago when replacing 3 port valve. But as this section of pipe is lower than the drain pipe, anything could be in there right?
I'm just trying to think logically but i'm no heating engineer!
Back to top
 Alert Moderators
Breesey

from United Kingdom

Joined: 11 Jan 2006
Posts: 860
Location: Sussex,
United Kingdom
Thanked: 28 times

PostPosted: Wed Feb 27, 2013 11:13 pm Reply with quote

Didn't read 'air seporator' on first read - naughty me!
Back to top
 Alert Moderators
kiltedcamel

from United Kingdom

Joined: 27 Oct 2012
Posts: 32
Location: Hertfordshire,
United Kingdom

PostPosted: Thu Feb 28, 2013 1:51 pm Reply with quote

Back to top
 Alert Moderators
Breesey

from United Kingdom

Joined: 11 Jan 2006
Posts: 860
Location: Sussex,
United Kingdom
Thanked: 28 times

PostPosted: Thu Feb 28, 2013 11:43 pm Reply with quote

Most likely place for a blockage or restriction is the air seporator.
Back to top
 Alert Moderators
kiltedcamel

from United Kingdom

Joined: 27 Oct 2012
Posts: 32
Location: Hertfordshire,
United Kingdom

PostPosted: Fri Mar 01, 2013 12:15 am Reply with quote

Ok so today I bought a system cleaner.
I drained the system, then before refilling I decided to check the small tank.
Oh my goodness it had so much gunk in it. Lots of flaky bits, about an inch deep covering most of the floor of the tank, see pic.

So anyway I cleaned it out as best as I could but its very difficult as there is only a few inches between top of tank and the ceiling!

I have refilled the system and poured in the cleaner, just letting it circulate now.
The boiler is still cutting off after 1 min, but the pump is running so I will just leave it circulating overnight.

What are the chances that this will work?

Sludge
Sludge
Back to top
 Alert Moderators
seco services

from United Kingdom

Joined: 03 Dec 2007
Posts: 15605
Location: Essex,
United Kingdom
Thanked: 1240 times

PostPosted: Fri Mar 01, 2013 12:24 am Reply with quote

kiltedcamel wrote:


What are the chances that this will work?




None if it's gone hard like this.
Back to top
 Alert Moderators
kiltedcamel

from United Kingdom

Joined: 27 Oct 2012
Posts: 32
Location: Hertfordshire,
United Kingdom

PostPosted: Fri Mar 01, 2013 8:52 am Reply with quote

So what needs to be done? Powerflush?
Back to top
 Alert Moderators
algas

from United Kingdom

Joined: 18 Oct 2008
Posts: 388
Location: Devon,
United Kingdom
Thanked: 48 times

PostPosted: Fri Mar 01, 2013 9:06 am Reply with quote

Are you sure that your pump is running, just because its making a noise it doesn't always mean that its ok the impeller could not be turning so not circulating the water, it boils & shoots up the vent pipe.
Back to top
 Alert Moderators
kiltedcamel

from United Kingdom

Joined: 27 Oct 2012
Posts: 32
Location: Hertfordshire,
United Kingdom

PostPosted: Fri Mar 01, 2013 9:41 am Reply with quote

algas wrote:
Are you sure that your pump is running, just because its making a noise it doesn't always mean that its ok the impeller could not be turning so not circulating the water, it boils & shoots up the vent pipe.


yes pretty sure its working, I take off screw and insert screwdriver can fell it grinding as it spins.
plus heat does get through to 3 port after all the banging and gurgling subsides.
Back to top
 Alert Moderators
kiltedcamel

from United Kingdom

Joined: 27 Oct 2012
Posts: 32
Location: Hertfordshire,
United Kingdom

PostPosted: Fri Mar 01, 2013 10:49 am Reply with quote

Does anyone think using a hose to flush with mains water would help.
If yes, where would I connect hose and where to drain? I want to try and get the flow pipe from boiler that goes under the floor then into airing cupboard. I have 2 small bleeding points on top of boiler, one on flow one on return. Can I connect hose there?
also as there was so much crud in feeder tank, how do I know if cold feed is gunked up?
Back to top
 Alert Moderators
TheGasMan26

from United Kingdom

Joined: 06 Dec 2008
Posts: 698
Location: Caithness,
United Kingdom
Thanked: 107 times

PostPosted: Fri Mar 01, 2013 11:00 am Reply with quote

kiltedcamel wrote:
algas wrote:
Are you sure that your pump is running, just because its making a noise it doesn't always mean that its ok the impeller could not be turning so not circulating the water, it boils & shoots up the vent pipe.


yes pretty sure its working, I take off screw and insert screwdriver can fell it grinding as it spins.
plus heat does get through to 3 port after all the banging and gurgling subsides.


The bit behind the screw still turns when pumps are broken, if its sludged the impellor can become detatched.

Heat could still make it to the 3 port by heat circulation, or the pump is sometimes just working.

Id put my money ion your air sep being blocked though, this requires you to cut the pipe out and clear manually, highly unlikely chemicals will work at this stage fella.

If youv got microbore pipework it could be your manifold(the bit all the pipes come off, will be under floowboards) thats blocked.

But again, the most likely cause is that your air sep is blocked, needs chopping out, blasting through with a hose/jet washer, and stabbing about with summat long. You will see the s**t.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2, 3  Next
Page 1 of 3

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Water coming out of vent pipe into central heating F&E t 8 1500 Sat Dec 26, 2009 11:49 pm
HELP!! - RAIN WATER COMING IN VIA BOILER VENT! 11 360 Sun Jul 08, 2012 10:49 am
Ants coming in through boiler vent. 4 120 Tue Aug 14, 2012 9:03 am
Bathwater coming out of under sink vent!!!! 6 100 Sun Jan 02, 2011 11:08 pm
Mains Water pipe coming into the house. 6 900 Sat Nov 29, 2008 2:29 am


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.