PIR-No Gas bond present


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
BigJon

from United Kingdom

Joined: 18 Jun 2006
Posts: 250
Location: Glasgow,
United Kingdom
Thanked: 1 time

PostPosted: Sun Sep 06, 2009 6:12 pm    Post Subject:
PIR-No Gas bond present
Reply with quote Thanks

Hi, after carrying out a Periodic test I found there to be no main bond to the gas, only one 10mm leaving the DB and going to the incoming water.
So, I was just wondering what number this would correspond to in the observations & recommendations i.e.

1. requires urgent attention
2.requires improvement
3.requires further investigation
4.does not comply with 7671:2008

There is a gas cooker and combi, not that i'd imagine makes any difference

Thanks.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4538
Location: United Kingdom
Thanked: 10 times

PostPosted: Sun Sep 06, 2009 6:20 pm    Post Subject:
Reply with quote Thanks

It always used to be code one, but the NICEIC guidence now is that its a code 2 (and as soon as you have a code 2, thats automatically an unsatisfactory verdict on the condition of the installation)
Back to top
The following user says thank you to Adam_151 for this useful post:
BigJon (6 Sep)
 Alert Moderators
widdler

from United Kingdom

Joined: 20 Mar 2007
Posts: 255
Location: Berkshire,
United Kingdom
Thanked: 15 times

PostPosted: Sun Sep 06, 2009 6:31 pm    Post Subject:
Reply with quote Thanks

'Absence of main equipotential bonding (except for a lightning protection system conductor, where a recommendation code 3 may be appropriate)'

Code 2

Quoted from the NICEIC 5th Edition Inspection, Testing & Certification Practical Advise & Guidance Book.

...oh and yes, I know the NICEIC arn't gospel.
Back to top
The following user says thank you to widdler for this useful post:
BigJon (6 Sep)
 Alert Moderators
BigJon

from United Kingdom

Joined: 18 Jun 2006
Posts: 250
Location: Glasgow,
United Kingdom
Thanked: 1 time

PostPosted: Sun Sep 06, 2009 6:32 pm    Post Subject:
Reply with quote Thanks

thanks for the info, appreciated
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Sun Sep 06, 2009 6:55 pm    Post Subject:
Reply with quote Thanks

It does not pose an immediate danger which is likely to injure someone or start a fire in the near future, so it can not be a code 1.

If you are doing a PIR and you see something which makes you draw a sharp intake of breath say to yourself "ooh jeez, thats baaad." and then call to your coleague "'ere mate, have you seen the state of this" then a code 1 might well be justified.

__________________
I downlights
Back to top
The following user says thank you to RF Lighting for this useful post:
BigJon (6 Sep)
 Alert Moderators
ricicle

from United Kingdom

Joined: 14 Sep 2006
Posts: 3485
Location: Gloucestershire,
United Kingdom
Thanked: 19 times

PostPosted: Sun Sep 06, 2009 8:19 pm    Post Subject:
Reply with quote Thanks

Presence of Main Bonding should be one of the first things that you check for as Zs tests should not be carried out without it in place icon_wink.gif

__________________
Empty barrels make the most noise.
Back to top
 Alert Moderators
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 4932
Location: Oxfordshire,
United Kingdom
Thanked: 63 times

PostPosted: Sun Sep 06, 2009 10:30 pm    Post Subject:
Reply with quote Thanks

There is an excellent guide to PIRS issued by the Electrical Safety Council and can be downloaded free from here

It includes typical problems and the codes that can be assigned to them.
Missing main bonding is code 2
A code 1 would be something like absence of an effective means of earthing for the installation.

Vive la difference!

__________________
TTC

When you get to the end of your rope, tie a knot and hang on. - F.D.R.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
SPLIT LOAD CONSUMER UNIT now with photos of present consumer 24 2400 Wed Aug 15, 2007 4:04 pm
SWA how to present 6 600 Sat Dec 23, 2006 11:43 am
MEBC not present. 8 380 Fri Apr 17, 2009 8:06 am
Supplementary bond to junction box 4 260 Thu Apr 17, 2008 3:01 pm
Where to bond the water. 2 120 Tue Feb 26, 2008 7:22 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.