Extra socket in garage. Unsure if can be done..help? anyone

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
sweenytodd123

from United Kingdom

Joined: 03 Aug 2009
Posts: 9
Location: Buckinghamshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon Aug 03, 2009 1:45 pm    Post Subject:
Extra socket in garage. Unsure if can be done..help? anyone
Reply with quote Thanks

Hi,

I have power supplied to my garage, which was put in when the house went up some 10 years ago. The cable is buried and rises into the garage to a fuse box with trips. One trip for the one light and one for the one double socket.

I want to put another double socket on an opposite wall, I have the cable etc, but unsure of whether I can take power from the existing socket.

The existing socket has one cable (the usual 3 wires) going into it and thats it, can I run my new wire and socket from this or am I stuck.

Apart from the light and single double socket, there is no other electric in the garage.

Thanks for your help. Rich
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
ColJack

from United Kingdom

Joined: 16 Feb 2007
Posts: 7599
Location: West Midlands,
United Kingdom
Thanked: 129 times

PostPosted: Mon Aug 03, 2009 2:04 pm    Post Subject:
Reply with quote Thanks

should be no problem at all..
2.5 cable..

the breaker feeding the socket/s should be a 16 or a 20.. no more than a 20..

__________________
If you make everything idiot proof, evolution will just make a better idiot.
Back to top
The following user says thank you to ColJack for this useful post:
sweenytodd123 (12 Oct)
 Alert Moderators
sweenytodd123

from United Kingdom

Joined: 03 Aug 2009
Posts: 9
Location: Buckinghamshire,
United Kingdom
Thanked: 0 times

PostPosted: Sat Aug 08, 2009 2:00 pm    Post Subject:
Worked a treat..many thanks
Reply with quote Thanks

Many thanks ColJack for the advice, it worked a treat and is up and running as I type!!

Thanks again. Rich
Back to top
 Alert Moderators
sweenytodd123

from United Kingdom

Joined: 03 Aug 2009
Posts: 9
Location: Buckinghamshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 12, 2009 6:30 am    Post Subject:
Extra socket in garage. First part done..more help needed
Reply with quote Thanks

Hi again,

I have finally got atreound to running a further socket in the garage, but I could do with another.

Just to recap, power to garage from house into fusebox in garage, one light and one double socket from this fusebox, I have run a double socket from the original double socket.

Can I run another from the new socket I have put in or the original one. Just thought I could do with a socket on the far wall or are any further sockets too much.

Thanks again for any advice.

Cheers, Rich
Back to top
 Alert Moderators
PrenticeBoyofDerry

from United Kingdom

Joined: 30 Jun 2009
Posts: 2128
Location: Londonderry,
United Kingdom
Thanked: 54 times

PostPosted: Mon Oct 12, 2009 6:58 am    Post Subject:
Reply with quote Thanks

If it's a radial circuit you can string a line of sockets on 2.5mm cable. 3 sockets not a problem, providing the breaker is 20 or16A. Should be fine.

If you decide to use equipment such as welders which have a high inrush current you may need to think about upgrading cable and breaker size or using a type c breaker.

A radial circuit link
http://www.diynot.com/wiki/electrics:socket_circuits:a2_radial
part p link
http://www.diynot.com/wiki/electrics:part_p

__________________
Dum Spiro Spero
Back to top
The following user says thank you to PrenticeBoyofDerry for this useful post:
sweenytodd123 (12 Oct)
 Alert Moderators
sweenytodd123

from United Kingdom

Joined: 03 Aug 2009
Posts: 9
Location: Buckinghamshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 12, 2009 10:08 am    Post Subject:
Reply with quote Thanks

Thanks PrenticeBoyofDerry,

As for the ring, am I right in thinking as the power is supplied from the house underground to a fuse / circuit breaker unit in the garage, that the circuit in the garage now becomes a ring?

If thats the case I can put another spur in.

Thanks, Rich
Back to top
 Alert Moderators
PrenticeBoyofDerry

from United Kingdom

Joined: 30 Jun 2009
Posts: 2128
Location: Londonderry,
United Kingdom
Thanked: 54 times

PostPosted: Mon Oct 12, 2009 1:57 pm    Post Subject:
Reply with quote Thanks

It depends how it's configured.
If the circuit in the garage goes from one socket to the next and so on and then stops at the last socket it's a radial.(which I believe yours is by your previous post)
If it continues from the last socket back to the consumer unit in the garage it is then a ring final circuit, so it will create one whole loop and a pair of lives with be terminated into the breaker a pair of neutrals to the neutral bar and a pair of cpc(earths) to earth bar.
This a ring final circuit (aka a ring)
http://www.diynot.com/wiki/_detail/electrics:socket_circuits:ringcct.jpg?id=electrics%3Asocket_circuits%3Aa1_ring_final_circuit&cache=cache

__________________
Dum Spiro Spero
Back to top
The following user says thank you to PrenticeBoyofDerry for this useful post:
sweenytodd123 (12 Oct)
 Alert Moderators
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 4940
Location: Oxfordshire,
United Kingdom
Thanked: 63 times

PostPosted: Mon Oct 12, 2009 3:10 pm    Post Subject:
Reply with quote Thanks

The amount of current you can draw from the circuit will depend on the fuse/contact beaker,

There will be more than one fuse/breaker in the supply to the garage sockets.

Where does the garage feed come from in the house?
From the fuseboard on its own breaker? What size is that?
Then you have the breaker in the db in the garage. If that is (say) 16A when that's the total current limit for the sockets.

You could make it a ring in the garage and put in a 32amp breaker, but that would be pointless if the garage is fed from a fused spur in the house with a 13A fuse in it!

__________________
TTC

When you get to the end of your rope, tie a knot and hang on. - F.D.R.
Back to top
The following user says thank you to Taylortwocities for this useful post:
sweenytodd123 (12 Oct)
 Alert Moderators
sweenytodd123

from United Kingdom

Joined: 03 Aug 2009
Posts: 9
Location: Buckinghamshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 12, 2009 4:54 pm    Post Subject:
Reply with quote Thanks

Thanks all for your replies.

The garage feed from the house comes from my main box in the house with its own fuse/trip, then into another fuse box in the garage, currently supplying one light, a double socket and another double I have run from that original one, so the idea is to run one final one from the extra one I put in.

Ive had a look for the fuse ratings but its not marked or written on the box.

Thanks again for all your help. Rich
Back to top
 Alert Moderators
PrenticeBoyofDerry

from United Kingdom

Joined: 30 Jun 2009
Posts: 2128
Location: Londonderry,
United Kingdom
Thanked: 54 times

PostPosted: Mon Oct 12, 2009 5:06 pm    Post Subject:
Reply with quote Thanks

The fuse rating will be on the MCB in the house CU for the cable powering the garage and garage CU rating will be on the isolator switch, this will tell what that unit can safely carry,
each circuit normally two in a standard garage CU. Will be rated again on the MCBs.
It will be marked something like B6, B16 etc.... or could be a C6/16 etc.....

__________________
Dum Spiro Spero
Back to top
The following user says thank you to PrenticeBoyofDerry for this useful post:
sweenytodd123 (12 Oct)
 Alert Moderators
davelx

from United Kingdom

Joined: 26 Sep 2006
Posts: 672
Location: London,
United Kingdom
Thanked: 6 times

PostPosted: Mon Oct 12, 2009 5:14 pm    Post Subject:
Reply with quote Thanks

But note that you cannot just increase the rating of the MCB feeding the garage circuit in the house CU without checking that the cable can support the additional current. This will depend on the size of the cable, the length of the run and the physical environment and method of installation.

__________________
Electricity can kill! Before working on any circuit, be sure to ISOLATE & TEST FOR DEAD.
Back to top
The following user says thank you to davelx for this useful post:
sweenytodd123 (12 Oct)
 Alert Moderators
sweenytodd123

from United Kingdom

Joined: 03 Aug 2009
Posts: 9
Location: Buckinghamshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 12, 2009 5:30 pm    Post Subject:
Reply with quote Thanks

PrenticeBoyofDerry wrote:
The fuse rating will be on the MCB in the house CU for the cable powering the garage and garage CU rating will be on the isolator switch, this will tell what that unit can safely carry,
each circuit normally two in a standard garage CU. Will be rated again on the MCBs.
It will be marked something like B6, B16 etc.... or could be a C6/16 etc.....


The MCB in the garage fusebox for the power is marked B16 and the one for the light B6 and the one in the house at the CU is marked B16 to supply the garage. Any help ?
Back to top
 Alert Moderators
Filo

from United Kingdom

Joined: 17 Mar 2008
Posts: 31
Location: Yorkshire,
United Kingdom
Thanked: 1 time

PostPosted: Mon Oct 12, 2009 5:38 pm    Post Subject:
Reply with quote Thanks

sweenytodd123 wrote:
PrenticeBoyofDerry wrote:
The fuse rating will be on the MCB in the house CU for the cable powering the garage and garage CU rating will be on the isolator switch, this will tell what that unit can safely carry,
each circuit normally two in a standard garage CU. Will be rated again on the MCBs.
It will be marked something like B6, B16 etc.... or could be a C6/16 etc.....


The MCB in the garage fusebox for the power is marked B16 and the one for the light B6 and the one in the house at the CU is marked B16 to supply the garage. Any help ?



Naughty, you`ve got a 16A mcb supplying a combined mcb of 22A
Back to top
The following user says thank you to Filo for this useful post:
sweenytodd123 (12 Oct)
 Alert Moderators
sweenytodd123

from United Kingdom

Joined: 03 Aug 2009
Posts: 9
Location: Buckinghamshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 12, 2009 5:54 pm    Post Subject:
Reply with quote Thanks

Filo wrote:
sweenytodd123 wrote:
PrenticeBoyofDerry wrote:
The fuse rating will be on the MCB in the house CU for the cable powering the garage and garage CU rating will be on the isolator switch, this will tell what that unit can safely carry,
each circuit normally two in a standard garage CU. Will be rated again on the MCBs.
It will be marked something like B6, B16 etc.... or could be a C6/16 etc.....


The MCB in the garage fusebox for the power is marked B16 and the one for the light B6 and the one in the house at the CU is marked B16 to supply the garage. Any help ?



Naughty, you`ve got a 16A mcb supplying a combined mcb of 22A



Naughty...no not me, thats why I come here to ask the questions before getting under way with work, naughty yes to the so called professional electrician, who would have done this in the first place, this is the only extra work (sockets in the garage)that has been done electrically since the house was built 10 years ago. Just hope he's not amongst you all on here giving the advice icon_smile.gif

Anyway, I take it the answer is no then to the extra socket without upping the CU fuse...
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Mon Oct 12, 2009 5:57 pm    Post Subject:
Reply with quote Thanks

Filo wrote:
Naughty, you`ve got a 16A mcb supplying a combined mcb of 22A

So?

What is the total of the MCB ratings in your CU, and what is the rating of your service fuse?

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
The following user says thank you to ban-all-sheds for this useful post:
sweenytodd123 (12 Oct)
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Unsure about safety of lighting circuit 4 400 Mon Apr 03, 2006 6:07 pm
EXTRA SOCKET IN GARAGE 2 320 Sat Oct 29, 2005 9:07 am
Extra supply and meter for garage ? 9 280 Fri Apr 03, 2009 8:31 pm
Extra sockets in garage and additional power to patio 10 560 Mon Mar 28, 2005 5:43 pm
Extending a ring main for extra socket chock block 7 660 Mon Feb 05, 2007 9:10 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.