double switch problem


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
indiaregina

from United Kingdom

Joined: 19 Oct 2009
Posts: 5
Location: Liverpool,
United Kingdom
Thanked: 0 times

PostPosted: Tue Oct 20, 2009 4:16 pm    Post Subject:
double switch problem
Reply with quote Thanks

i have removed an old brass double switch from the hall. this switch opperates the upstair light and hall. i have replaced it with a new double switch and the upstair light will not go off if the switch upstais is left on.. i have put the two red wires in to the com and connected them and the two black wires in to L1 on both switches any suggestions what i have done wrong
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 10887
Location: Cumbria,
United Kingdom
Thanked: 39 times

PostPosted: Tue Oct 20, 2009 4:24 pm    Post Subject:
Reply with quote Thanks

Can you remember how the old one was wired? Was there a link wire in there between the two switches?
Back to top
 Alert Moderators
sparkwright

from United Kingdom

Joined: 20 Aug 2009
Posts: 253
Location: Dorset,
United Kingdom
Thanked: 25 times

PostPosted: Tue Oct 20, 2009 4:50 pm    Post Subject:
Reply with quote Thanks

don't you have a 3 core and earth cable (red, yellow, blue and earth) running between the up switch and the down switch?
Back to top
 Alert Moderators
ColJack

from United Kingdom

Joined: 16 Feb 2007
Posts: 7599
Location: West Midlands,
United Kingdom
Thanked: 129 times

PostPosted: Tue Oct 20, 2009 5:15 pm    Post Subject:
Reply with quote Thanks

only one of the reds is a live feed, the other is a strapper along with one black that goes upstaris to the other switch..

with the power off, open the upstairs switch and connect together the red and black that are in L1 and L2 ( or L2 and L3 if your switch is marked L1, L2, L3 rather than C, L1, L2. )

now using a multimeter on the continuity setting, check at the downstairs switch between the red and black from each cable..
one pair will read continuity.. those are the strappers..

now, they go into L1 and L2 on one switch, the black from the other cable goes to the other L1, and the red goes to C or Com, and is linked to the other C or Com too..

put the upstairs switch back how it was..
turn the power back on..

__________________
If you make everything idiot proof, evolution will just make a better idiot.
Back to top
The following user says thank you to ColJack for this useful post:
indiaregina (2 Nov)
 Alert Moderators
indiaregina

from United Kingdom

Joined: 19 Oct 2009
Posts: 5
Location: Liverpool,
United Kingdom
Thanked: 0 times

PostPosted: Tue Oct 20, 2009 7:50 pm    Post Subject:
switch
Reply with quote Thanks

Spark123 wrote:
Can you remember how the old one was wired? Was there a link wire in there between the two switches?
there was two red wires and a com port with red wire i earth and two black cables. i have connected the switch as follows red wire in com port with com wire crossing between them also the black wire in L1 in both switchs. you can turn the upstairs light off from downstairs but not upstairs.....
Back to top
 Alert Moderators
sparkybird

from United Kingdom

Joined: 19 Jan 2005
Posts: 594
Location: United Kingdom
Thanked: 2 times

PostPosted: Tue Oct 20, 2009 7:56 pm    Post Subject:
Reply with quote Thanks

did your old switch have 3 terminals per switch - L1, L2 and Comm?

Does your new switch have 3 terminals per switch or just L1 and Comm?

SB
Back to top
 Alert Moderators
indiaregina

from United Kingdom

Joined: 19 Oct 2009
Posts: 5
Location: Liverpool,
United Kingdom
Thanked: 0 times

PostPosted: Tue Oct 20, 2009 8:13 pm    Post Subject:
Reply with quote Thanks

sparkybird wrote:
did your old switch have 3 terminals per switch - L1, L2 and Comm? no there was com A B1 B2
UPPER, AND LOWER IS A1 A2 B
Does your new switch have 3 terminals per switch or just L1 and Comm?

SB
yes but the layout is different on the new one.
Back to top
 Alert Moderators
indiaregina

from United Kingdom

Joined: 19 Oct 2009
Posts: 5
Location: Liverpool,
United Kingdom
Thanked: 0 times

PostPosted: Tue Oct 20, 2009 8:15 pm    Post Subject:
Reply with quote Thanks

indiaregina wrote:
sparkybird wrote:
did your old switch have 3 terminals per switch - L1, L2 and Comm? no there was com A B1 B2
UPPER, AND LOWER IS A1 A2 B
Does your new switch have 3 terminals per switch or just L1 and Comm?

SB
yes but the layout is different on the new one.
IT ALSO HAS THREE TERMINALS
Back to top
 Alert Moderators
ColJack

from United Kingdom

Joined: 16 Feb 2007
Posts: 7599
Location: West Midlands,
United Kingdom
Thanked: 129 times

PostPosted: Wed Oct 21, 2009 2:47 pm    Post Subject:
Reply with quote Thanks

I've told you what to do above..
try that then report back to us..

__________________
If you make everything idiot proof, evolution will just make a better idiot.
Back to top
 Alert Moderators
indiaregina

from United Kingdom

Joined: 19 Oct 2009
Posts: 5
Location: Liverpool,
United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 26, 2009 3:35 pm    Post Subject:
Reply with quote Thanks

ColJack wrote:
I've told you what to do above..
try that then report back to us..
no the swithch i am putting on has 1 way AND 1-2 way port per switch and a com. i have tried what you said but being quite new to diy as my husband is working away i thought i would impress him and i think it has been made worse HELP!!!!!!!
Back to top
 Alert Moderators
ColJack

from United Kingdom

Joined: 16 Feb 2007
Posts: 7599
Location: West Midlands,
United Kingdom
Thanked: 129 times

PostPosted: Mon Oct 26, 2009 10:54 pm    Post Subject:
Reply with quote Thanks

just post a photo of the switches and the connections of the existing and we'll advise further..

__________________
If you make everything idiot proof, evolution will just make a better idiot.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
double switch problem 2 200 Sat Apr 25, 2009 8:33 am
double switch problem 2 460 Tue Sep 27, 2005 10:15 am
Double/Single Oven Problem 3 800 Sun Feb 27, 2005 12:00 am
Double to single socket problem 5 320 Tue Sep 11, 2007 7:11 pm
Is the problem the wiring or the appliance (double oven) 10 260 Tue Oct 13, 2009 8:46 pm