Joined: 02 Jun 2005 Posts: 10887 Location: Cumbria, United Kingdom Thanked: 39 times
Posted: Thu Oct 22, 2009 4:05 pm Post Subject:
Wonder if you'll get away with just swopping the 100mA RCD for a 30mA RCD??
The 100mA wont have been installed for protection on a TT system as everything to the left of it wont have been protected.
Joined: 15 Nov 2005 Posts: 24037 Location: Hampshire, United Kingdom Thanked: 54 times
Posted: Thu Oct 22, 2009 4:09 pm Post Subject:
it is probably seized. If you buy a new part you will see how it fits in. An MCB will be a lot cheaper than an RCBO. I don't know if they can be lubricated safely. If it was me I would probably try to lever it out. You must put pressure on the busbar to resist your pull or it might break out of the CU. The busbar is thickish copper with a plastic jacket and fairly rigid. You can take the whole assembly out but I don't think you can safely do with with incoming power connected.
Other brands, and the previous model of Starbreaker, fasten the MCBs to the busbar with screws so you can undo them and release the clip. This is easier but will not fit your CU.
It does not sound like a DIY job, I think you will have to save up for a pro.
Last edited by JohnD on Thu Oct 22, 2009 4:18 pm, edited 2 times in total
Joined: 05 Aug 2009 Posts: 42 Location: Devon, United Kingdom Thanked: 1 time
Posted: Thu Oct 22, 2009 5:04 pm Post Subject:
Ban All sheds. Was there a requirement in the 16th edition, (is this what was in place say 9 years ago), for electric showers to be on a 30ma RCD.
If not why would whoever it was that did this bother to put a RCD in at all. Wouldnt it have been cheaper just to stick a rack of MCBs in or maybe even a 30ma RCD as it would have been cheaper than a 100ma.
I am genuinely interested in understanding why the 100ma RCD is there.
Joined: 02 Jun 2005 Posts: 10887 Location: Cumbria, United Kingdom Thanked: 39 times
Posted: Thu Oct 22, 2009 5:14 pm Post Subject:
The 16th edn IEE regs didn't require an RCD for a shower. Of course, if the manufacturer specified one then this over-rules the IEE regs and one had to be installed.
In anycase, a 100mA RCD does not provide any supplementary protection against direct contact, only 30mA or below and not Type S devices can be used for that.
The only time I can think of in domestics that 100mA TD RCDs were used is where there is a 30mA normal type device downstream so they will discriminate.