Using earth as a neutral.
Reply with quote Thanks

Got asked to look at fixing a spotlight on one of the machines at work today. Its a 'Dynamic Balancer' used for balancing armatures/rotors and the guy said the spotlight has started blowing the bulbs more often. The light is one of these 'security' lights without the PIR. Anyway as one of the end prongs was badly burnt I decided to look for a loose connection when I discovered the earth from the lamp in the back of the fitting was connected to the neutral of the incoming supply (240v)and vice versa. icon_eek.gif
Looking further into it I discovered the 240v supply had been picked up from one of the 415v phase supplies and the main incoming earth as there was no neutral.
Now I'm not the hottest on industrial wiring, (I'm an armature winder/electrical fitter), so to me this is totally wrong. Is this a common method though as it was done by the people who installed the safety covers around the machine.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Fri Oct 23, 2009 9:23 pm    Post Subject:
Reply with quote Thanks

Absoloutly not!!

It is very dangerous, completely against BS7671, and must be disconnected immediately.

If for any reason the earth to the machine, or worse still, the whole building were to fail, ALL the metalwork upto the point of failure will instantly become live icon_eek.gif

You need to either get a neutral to the machine, or install a stepdown transformer and run the light on two of the phases.

__________________
I downlights
Back to top
The following user says thank you to RF Lighting for this useful post:
conny (24 Oct)
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Fri Oct 23, 2009 10:02 pm    Post Subject:
Reply with quote Thanks

Whoever did that has broken the law.

You need to speak to the duty holder and/or other persons in charge and tell them that they've got a serious breach of the EAWR on their hands.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
The following user says thank you to ban-all-sheds for this useful post:
conny (24 Oct)
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 10887
Location: Cumbria,
United Kingdom
Thanked: 39 times

PostPosted: Sat Oct 24, 2009 4:11 am    Post Subject:
Reply with quote Thanks

If there is no neutral present then use a 415v to 240v single phase transformer, not rocket science.
Like BAS says it is illegal (ESQCR) for a consumer to combine the neutral and earth in a single conductor.
Back to top
The following user says thank you to Spark123 for this useful post:
conny (24 Oct)
 Alert Moderators
ColJack

from United Kingdom

Joined: 16 Feb 2007
Posts: 7599
Location: West Midlands,
United Kingdom
Thanked: 129 times

PostPosted: Sat Oct 24, 2009 10:47 am    Post Subject:
Reply with quote Thanks

would you then earth one side of the transformer secondary to reference the "neutral" to earth? icon_wink.gif

__________________
If you make everything idiot proof, evolution will just make a better idiot.
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Sat Oct 24, 2009 3:27 pm    Post Subject:
Reply with quote Thanks

It's not a neutral icon_lol.gif

(here we go again)

__________________
I downlights
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 10887
Location: Cumbria,
United Kingdom
Thanked: 39 times

PostPosted: Sat Oct 24, 2009 5:31 pm    Post Subject:
Reply with quote Thanks

You can reference it to earth or you can leave it floating if you wish - normal design procedures apply of course.
Back to top
 Alert Moderators
conny

from United Kingdom

Joined: 30 Jun 2008
Posts: 2644
Location: Liverpool,
United Kingdom
Thanked: 20 times

PostPosted: Sat Oct 24, 2009 7:35 pm    Post Subject:
Reply with quote Thanks

Sorry to take so long to get back to you guys, had a busy day.
Thanks very much for the info, I suspected it was illegal but wanted to make sure before I told the supervisor to shut it down till it is rectified. We had some company come in and build a 'Wendy House' affair around the machine to stop anyone getting hurt if bits flew off a rotor when it was being balanced and these are the people who wired up the light. They also wired in various interlocks so the enclosure had to be closed before the machine would start. Frightening to think how they may be wired up! icon_eek.gif

Once again, thank you and I'll get onto the supervisor first thing Monday morning.
Back to top
 Alert Moderators
bernardgreen

from United Kingdom

Joined: 03 Nov 2006
Posts: 3611
Location: Bedfordshire,
United Kingdom
Thanked: 22 times

PostPosted: Sat Oct 24, 2009 7:56 pm    Post Subject:
Reply with quote Thanks

The "Wendy House" is a useful safety device but the machine itself should detect any dangerous un-balance when the shaft is rotating at slow speed and then prevent itself from increasing speed to a point where the item being tested has any risk of shattering.
Back to top
 Alert Moderators
conny

from United Kingdom

Joined: 30 Jun 2008
Posts: 2644
Location: Liverpool,
United Kingdom
Thanked: 20 times

PostPosted: Sat Oct 24, 2009 8:22 pm    Post Subject:
Reply with quote Thanks

Good point Bernard, trouble is it is a second hand machine and quite old, (70's or 80's maybe)so although calibrated and checked regularly it is analogue meters etc so doesn't have the modern sophisticated safety features, its upto the operator to stop it if he thinks something is too far out of balance.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Sat Oct 24, 2009 10:14 pm    Post Subject:
Reply with quote Thanks

I can hear the HSE lawyers licking their lips and counting their bonuses from here...

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Stoday

from United Kingdom

Joined: 04 Oct 2004
Posts: 567
Location: United Kingdom
Thanked: 4 times

PostPosted: Sun Oct 25, 2009 3:11 am    Post Subject:
Reply with quote Thanks

I can remember wiring a whole farm up with no neutral anywhere — neither on three nor single phase circuits. All in pyro, the earth and neutral being common.

This was allowed for pme installations at the time - 1965 I think. Moreover, when the NICEIC inspector came around for his visit he made a beeline for my farm. Passed 100%. icon_mrgreen.gif
Back to top
 Alert Moderators
conny

from United Kingdom

Joined: 30 Jun 2008
Posts: 2644
Location: Liverpool,
United Kingdom
Thanked: 20 times

PostPosted: Mon Oct 26, 2009 10:20 pm    Post Subject:
Reply with quote Thanks

Just to bring you up to date.
Mentioned this to manager this morning, supervisor wasn't interested, and his immediate reaction was, "Do what ever it takes to make it safe and legal, don't give a s**t about the cost."
So contacted 'Wendy House' installers and asked them to come and have a look immediately, can't get here till Friday at earliest.
I told them I would take pictures before disconnecting as proof of fault, they didn't seem too bothered. Got a feeling I will be chasing them to come out and investigate.
In the meantime I have run a length of 4mm SY cable through some 25mm conduit from a local dis board to supply a 2 gang metalclad socket fixed to the structure and plugged a new light into this. It is protected by a b16 mcb in the board and a 3A fuse in the plug. Is this acceptable for a temporary supply? If not I'll tell the manager we need to get someone in in the meantime to fix it properly.
Thanks in advance.
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 10887
Location: Cumbria,
United Kingdom
Thanked: 39 times

PostPosted: Tue Oct 27, 2009 12:23 am    Post Subject:
Reply with quote Thanks

It is fine as a temp supply however some labels making it clear that the socket is fed from a separate source wouldn't go amiss.
Back to top
 Alert Moderators
conny

from United Kingdom

Joined: 30 Jun 2008
Posts: 2644
Location: Liverpool,
United Kingdom
Thanked: 20 times

PostPosted: Tue Oct 27, 2009 6:28 pm    Post Subject:
Reply with quote Thanks

Thanks Spark123, I have put signs at both ends and also one stating that the installation is to be removed no later than 26/01/2010.
This information has also been entered into the branch safety log.
Once again thank you.


Last edited by conny on Tue Oct 27, 2009 8:37 pm, edited 1 time in total
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Earth and Neutral swapped on shower unit 3 340 Fri Feb 16, 2007 1:05 pm
old CU, bad earth, fused neutral (photo) advice 40 5080 Wed Dec 20, 2006 1:09 pm
combi boiler 240v between neutral and earth 3 240 Wed Jan 23, 2008 8:03 pm
LIVE live, LIVE neutral, LIVE earth all showing current?? 10 600 Sat Feb 17, 2007 4:25 pm
Neutral Earth Fault ?? 24 4520 Mon May 15, 2006 8:39 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.