greenstar 42cdi combi faul

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
  View previous topic :: View next topic  
Author Message
bigdek

from United Kingdom

Joined: 19 Sep 2004
Posts: 126
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Jan 03, 2008 10:38 pm    Post Subject:
greenstar 42cdi combi faul
Reply with quote Thanks

Was working fine till today.

Now it lights and goes out for 3 or 4 times then reset and blue light flash and shows ea in the display .

Doesn't continually spark after its lit and flue appear to be fine.

Any help appreciated
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
gas4you

from United Kingdom

Joined: 23 Feb 2007
Posts: 14312
Location: Norwich,
United Kingdom
Thanked: 41 times

PostPosted: Fri Jan 04, 2008 6:23 pm    Post Subject:
Reply with quote Thanks

If its not sparking then you need to start at the beginning and see what is actually working correctly, eg fan, aps etc.

What does the MI's say about the ea fault code?

__________________
Dave
DRL Gas Services
Back to top
 Alert Moderators
nickso

from United Kingdom

Joined: 30 Oct 2006
Posts: 3813
Location: United Kingdom
Thanked: 21 times

PostPosted: Fri Jan 04, 2008 6:33 pm    Post Subject:
Reply with quote Thanks

ea is flame not detected.

flue
electrodes
supply pressure
burner
fan maybe
Back to top
 Alert Moderators
Whiter

from United Kingdom

Joined: 03 Feb 2003
Posts: 52
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Jan 04, 2008 7:43 pm    Post Subject:
Reply with quote Thanks

Check that the gas is on.
Back to top
 Alert Moderators
superdupergasman

from United Kingdom

Joined: 04 Jan 2008
Posts: 797
Location: Edinburgh,
United Kingdom
Thanked: 0 times

PostPosted: Fri Jan 04, 2008 8:13 pm    Post Subject:
Reply with quote Thanks

Common one I have had from flame detection error is the set up of min and max co levels....rare that there are faulty components on this boiler!
Back to top
 Alert Moderators
baxpoti

from United Kingdom

Joined: 15 Dec 2006
Posts: 2388
Location: United Kingdom
Thanked: 34 times

PostPosted: Thu Oct 29, 2009 9:36 pm    Post Subject:
Reply with quote Thanks

Any more info on this one?

Intermittent EA fault

COČ spot on 9.7% high 9.1% low
Spark gap 4.5mm
condense trap cleaned

Not working on arrival (EA fault) very poor spark, cleaned trap, closed electrodes, checked continuity on flue ad o/h stas then worked fine, called in tonight EA fault again!?
Back to top
 Alert Moderators
davebgas

from Canada

Joined: 09 Feb 2009
Posts: 1127
Location: Northwest Territories,
Canada
Thanked: 55 times

PostPosted: Thu Oct 29, 2009 10:24 pm    Post Subject:
Reply with quote Thanks

Baxpoti, was it the square heat ex block one or new cylindrical one?

Old ones were prone to moisture on electrodes.

Did ya check inlet gas pressures?

__________________
Incorporated Engineer with IGEM & Registered with the Engineering Council UK
Back to top
The following user says thank you to davebgas for this useful post:
baxpoti (30 Oct)
 Alert Moderators
baxpoti

from United Kingdom

Joined: 15 Dec 2006
Posts: 2388
Location: United Kingdom
Thanked: 34 times

PostPosted: Thu Oct 29, 2009 10:38 pm    Post Subject:
Reply with quote Thanks

Baxpoti, was it the square heat ex block one or new cylindrical one?
Quote:
Looked fairly square and round to me


Old ones were prone to moisture on electrodes.
Quote:
electrodes out and cleaned


Did ya check inlet gas pressures?
Quote:
15.06mb on high rate]
Back to top
 Alert Moderators
davebgas

from Canada

Joined: 09 Feb 2009
Posts: 1127
Location: Northwest Territories,
Canada
Thanked: 55 times

PostPosted: Thu Oct 29, 2009 10:45 pm    Post Subject:
Reply with quote Thanks

Sorry, old heat exchangers has 2 bolts on the front you could take off for access to clean, new cylinder style access is from top.

Any water on the electrodes connection to the board?

which WB model was it?
What was the spark like again today after you closed the gap?

__________________
Incorporated Engineer with IGEM & Registered with the Engineering Council UK
Back to top
 Alert Moderators
APHSLTD

from United Kingdom

Joined: 05 Feb 2009
Posts: 89
Location: Aberdeen,
United Kingdom
Thanked: 13 times

PostPosted: Fri Oct 30, 2009 12:18 am    Post Subject:
Reply with quote Thanks

42CDi has a square WB5 heat exchanger the round WB3 heat exchanger is found on cheaper models like the Si, i Junior and Ri.

Gas pipework is undersized but the boiler should still work fine with 15mbar inlet pressure just not give full performance.

Check the bearing plate hasn't split in the air/gas manifold.

Check both gas valve coils they should read between 120 and 200 Ohms

If the boiler is connected to an old gas pipe it may be worth checking the gas valve inlet filter.

You can check ignition by turning on permanent spark in service mode. Hold service button till it turns orange (roughly 10 secs) press eco button till 8F is displayed, press chimney sweep button, press eco till 1 is displayed, press and hold chimney sweep till ignition starts DO NOT RUN FOR MORE THAN 2 MINUTES. To turn off press eco till 0 is displayed, press and hold chimney sweep button.

Hope this helps.
Back to top
The following 4 users say thank you to APHSLTD for this useful post:
bengasman (30 Oct), ChrisR (30 Oct), baxpoti (30 Oct), davebgas (30 Oct)
 Alert Moderators
davebgas

from Canada

Joined: 09 Feb 2009
Posts: 1127
Location: Northwest Territories,
Canada
Thanked: 55 times

PostPosted: Fri Oct 30, 2009 12:20 am    Post Subject:
Reply with quote Thanks

Good man!!! will be making a note of that, cheers ! icon_biggrin.gif

__________________
Incorporated Engineer with IGEM & Registered with the Engineering Council UK
Back to top
 Alert Moderators
baxpoti

from United Kingdom

Joined: 15 Dec 2006
Posts: 2388
Location: United Kingdom
Thanked: 34 times

PostPosted: Fri Oct 30, 2009 5:36 pm    Post Subject:
Reply with quote Thanks

Arrived to find EA and flashing lights.

Tried to get the boiler into service mode..

Couldn't get 8F it stopped at 7... returned to 1

Removed siphon bowl and pint of coondense it fired up!

Blew down condense pipe, all clear

Washed siphon trap and tube refitted switched on and no ignition spark..Gas OK

Closed spark gap down to 3-4mm and away it went. icon_evil.gif

Ran heating and hot water, left heating running.

Waiting for the knock on the door.......................
Back to top
 Alert Moderators
APHSLTD

from United Kingdom

Joined: 05 Feb 2009
Posts: 89
Location: Aberdeen,
United Kingdom
Thanked: 13 times

PostPosted: Fri Oct 30, 2009 6:13 pm    Post Subject:
Reply with quote Thanks

baxpoti wrote:
Arrived to find EA and flashing lights.

Tried to get the boiler into service mode..

Couldn't get 8F it stopped at 7... returned to 1

Removed siphon bowl and pint of coondense it fired up!

Blew down condense pipe, all clear

Washed siphon trap and tube refitted switched on and no ignition spark..Gas OK

Closed spark gap down to 3-4mm and away it went. icon_evil.gif

Ran heating and hot water, left heating running.

Waiting for the knock on the door.......................



Oop's am I bad 8F is in service level 2 which you get to by going into service level 1 (holding service button for 10 secs) then pressing and holding eco and holiday buttons for 3 secs.

My apologies.
Back to top
 Alert Moderators
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 10099
Location: London,
United Kingdom
Thanked: 188 times

PostPosted: Fri Oct 30, 2009 8:02 pm    Post Subject:
Reply with quote Thanks

Great as this stuff may be, it should be in the CC.

__________________
Don't feed the troll.
Back to top
 Alert Moderators
baxpoti

from United Kingdom

Joined: 15 Dec 2006
Posts: 2388
Location: United Kingdom
Thanked: 34 times

PostPosted: Fri Oct 30, 2009 8:32 pm    Post Subject:
Reply with quote Thanks

bengasman wrote:
Great as this stuff may be, it should be in the CC.


I will m'lord
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
How Can I Verify My Landis & Gyr RWB2 Programmer Is Faul 2 600 Tue May 27, 2008 10:26 am
worchester bosch greenstar 42cdi combi problem. 12 740 Wed Jul 08, 2009 10:46 am
WORCESTER GREENSTAR 42CDi Combi 8 760 Sat May 23, 2009 7:55 pm
wooster bosch 42cdi greenstar 3 400 Sun Apr 05, 2009 6:28 am
Low inlet gas pressure - Worcester Greenstar 42CDI bolier 171 19620 Sun Aug 12, 2007 9:22 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.