Baxi 105e fault
Reply with quote Thanks

Please Help,
I have Baxi 105e combi boiler approx 3 years old when you run the hot water for approx 3 mins it the flame cuts out and you then get cold water after approx 1min it then powers up starting the whole cycle again resulting in a luke warm bath. The central heating side seems ok could anyone please point me in the right direction.
Thanks.
icon_mad.gif
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 19155
Location: Tennessee,
United States of America
Thanked: 400 times

PostPosted: Wed Oct 28, 2009 3:48 pm    Post Subject:
Reply with quote Thanks

plate heat ex full of carp icon_eek.gif

__________________
a little thanks

goes a long way
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 24311
Location: London,
United Kingdom
Thanked: 193 times

PostPosted: Wed Oct 28, 2009 4:52 pm    Post Subject:
Reply with quote Thanks

The installer evidently did not properly clean the system when installing the boiler. Thats often done by power flushing.

Unfortunately after three years its a bit late to blame him and expect him to do anything about it.

Presumably you have never had it serviced?

Tony

__________________
ARGI Registered Engineer
Back to top
 Alert Moderators
mrbaxi2009

from United Kingdom

Joined: 29 Oct 2009
Posts: 3
Location: Newcastle upon Tyne,
United Kingdom
Thanked: 0 times

PostPosted: Thu Oct 29, 2009 4:38 pm    Post Subject:
Re: Baxi 105e fault
Reply with quote Thanks

baxi105e wrote:
Please Help,
I have Baxi 105e combi boiler approx 3 years old when you run the hot water for approx 3 mins it the flame cuts out and you then get cold water after approx 1min it then powers up starting the whole cycle again resulting in a luke warm bath. The central heating side seems ok could anyone please point me in the right direction.
Thanks.
icon_mad.gif


over the years any diluted debris from the rads dry out and bake inside the plate heat exchanger. Power flushing doesn't prevent this. You could install a filter on the return to prevent it happening again. You are best off taking the plate heat exchanger out and buying some cleaner from your local B & Q and that will get you going.
Back to top
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 19155
Location: Tennessee,
United States of America
Thanked: 400 times

PostPosted: Thu Oct 29, 2009 4:51 pm    Post Subject:
Reply with quote Thanks

Quote:
You are best off taking the plate heat exchanger out and buying some cleaner from your local B & Q and that will get you going.


yeah right icon_confused.gif

__________________
a little thanks

goes a long way
Back to top
 Alert Moderators
mrbaxi2009

from United Kingdom

Joined: 29 Oct 2009
Posts: 3
Location: Newcastle upon Tyne,
United Kingdom
Thanked: 0 times

PostPosted: Thu Oct 29, 2009 5:35 pm    Post Subject:
Reply with quote Thanks

kevplumb wrote:
Quote:
You are best off taking the plate heat exchanger out and buying some cleaner from your local B & Q and that will get you going.


yeah right icon_confused.gif


don't knock it until you have tried it
Back to top
 Alert Moderators
scatmanjohn

from Colombia

Joined: 02 Nov 2005
Posts: 2554
Location: Colombia
Thanked: 4 times

PostPosted: Thu Oct 29, 2009 9:54 pm    Post Subject:
Reply with quote Thanks

mrbaxi2009 wrote:
kevplumb wrote:
Quote:
You are best off taking the plate heat exchanger out and buying some cleaner from your local B & Q and that will get you going.


yeah right icon_confused.gif


don't knock it until you have tried it


I've tried it. It didn't work icon_cry.gif

Although i have to admit the stuff didn't come from B&Q icon_lol.gif

A diyer's best bet is to stick a new one in IMHO
Back to top
 Alert Moderators
baxpoti

from United Kingdom

Joined: 15 Dec 2006
Posts: 2389
Location: United Kingdom
Thanked: 34 times

PostPosted: Thu Oct 29, 2009 10:28 pm    Post Subject:
Reply with quote Thanks

mrbaxi2009 wrote:
kevplumb wrote:
Quote:
You are best off taking the plate heat exchanger out and buying some cleaner from your local B & Q and that will get you going.


yeah right icon_confused.gif


don't knock it until you have tried it


If you are mrbaxi why are you using B&Q
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 24311
Location: London,
United Kingdom
Thanked: 193 times

PostPosted: Fri Oct 30, 2009 3:20 pm    Post Subject:
Re: Baxi 105e fault
Reply with quote Thanks

mrbaxi2009 wrote:


over the years any diluted debris from the rads dry out and bake inside the plate heat exchanger.



I dont see that !

How can anything "dry" when its full of water ?

Tony[/b]

__________________
ARGI Registered Engineer
Back to top
 Alert Moderators
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 10130
Location: London,
United Kingdom
Thanked: 189 times

PostPosted: Fri Oct 30, 2009 9:40 pm    Post Subject:
Re: Baxi 105e fault
Reply with quote Thanks

mrbaxi2009 wrote:

over the years any diluted debris from the rads dry out


Inside a wet central heating system?

mrbaxi2009 wrote:
Power flushing doesn't prevent this.


Are you sure? I have never had this problem on heating systems I powerflushed before I installed the new boiler.


mrbaxi2009 wrote:
You could install a filter on the return to prevent it happening again.


The water circulates inside the boiler in dhw mode, a filter on the return will do little in that case.

mrbaxi2009 wrote:
You are best off taking the plate heat exchanger out and buying some cleaner from your local B & Q and that will get you going.


Until it blocks up again. IF the op can get the hex out, AND put it all back together again.
How long have you been a RGI?



Cleaning or replacing the hex will only work so long. The system needs to be thoroughly cleaned. If this is done with a powerflush, the hex will be unblocked at the same time. Provided the flush is done properly of course.[/b]

__________________
Don't feed the troll.
Back to top
 Alert Moderators
baxpoti

from United Kingdom

Joined: 15 Dec 2006
Posts: 2389
Location: United Kingdom
Thanked: 34 times

PostPosted: Sat Oct 31, 2009 8:20 am    Post Subject:
Re: Baxi 105e fault
Reply with quote Thanks

bengasman wrote:

How long have you been a RGI?




What do you mean. This is the quality of the newer Heateam engineers
Back to top
The following user says thank you to baxpoti for this useful post:
Timd01 (31 Oct)
 Alert Moderators
Timd01

from United Kingdom

Joined: 24 Apr 2008
Posts: 19
Location: Berkshire,
United Kingdom
Thanked: 0 times

PostPosted: Sat Oct 31, 2009 10:12 am    Post Subject:
Reply with quote Thanks

I agree. icon_eek.gif
Back to top
 Alert Moderators
rojaca

from United Kingdom

Joined: 14 Dec 2008
Posts: 121
Location: United Kingdom
Thanked: 8 times

PostPosted: Sat Oct 31, 2009 11:46 am    Post Subject:
Reply with quote Thanks

Debris in the form of flakes appears to be particular culprit in blocking plate hex. Certainly can't think of an instance on own installations when powerflushed of any problems.
On questioning customers most will say system was 'flushed' at time of install, (except if NORTHERN GAS customer) however the specifics of what this flush entailed are usually quite vague.
I have known flakes to be present on newly piped systems, several years old, which I have put down to either poor qual' manufacturing of rads (cheap) or insufficient/incorrect dosing of inhibitor.
Back to top
 Alert Moderators
Newcastle88

from United Kingdom

Joined: 31 Oct 2009
Posts: 10
Location: Newcastle upon Tyne,
United Kingdom
Thanked: 0 times

PostPosted: Sat Oct 31, 2009 11:47 am    Post Subject:
Re: Baxi 105e fault
Reply with quote Thanks

baxpoti wrote:
bengasman wrote:

How long have you been a RGI?




What do you mean. This is the quality of the newer Heateam engineers


I agree the Heateam engineers here in Newcastle are useless. I had one of my customers wait 4 weeks for a diverter valve under warranty because the engineer told her he had to order it and it was out of stock. PTS had 5 in stock and the engineer who eventualy came back had one as his van stock??????? Where have all the good engineers gone Baxpoti?
Back to top
 Alert Moderators
davebgas

from Canada

Joined: 09 Feb 2009
Posts: 1127
Location: Northwest Territories,
Canada
Thanked: 55 times

PostPosted: Sat Oct 31, 2009 11:50 am    Post Subject:
Reply with quote Thanks

Quote:
(except if NORTHERN GAS customer)


What is this supposed to mean?????? WTF do the transporter have to do with flushing???

__________________
Incorporated Engineer with IGEM & Registered with the Engineering Council UK
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2, 3  Next
Page 1 of 3

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Baxi 105e hot water fault 3 140 Wed Dec 31, 2008 7:51 pm
Baxi Instant 105e CH Fault 2 760 Fri Nov 25, 2005 10:56 am
Baxi 105e fault light flashing 26 3000 Mon Mar 03, 2008 7:45 pm
baxi combi 105e flashing light ( sensor fault light 11 ) 3 760 Thu Dec 20, 2007 12:37 am
Baxi 105e - Fault on fan or flue? 4 400 Fri Nov 14, 2008 6:02 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.