Baxi 105e fault
Please Help,
I have Baxi 105e combi boiler approx 3 years old when you run the hot water for approx 3 mins it the flame cuts out and you then get cold water after approx 1min it then powers up starting the whole cycle again resulting in a luke warm bath. The central heating side seems ok could anyone please point me in the right direction.
Thanks.
Please Help,
I have Baxi 105e combi boiler approx 3 years old when you run the hot water for approx 3 mins it the flame cuts out and you then get cold water after approx 1min it then powers up starting the whole cycle again resulting in a luke warm bath. The central heating side seems ok could anyone please point me in the right direction.
Thanks.
over the years any diluted debris from the rads dry out and bake inside the plate heat exchanger. Power flushing doesn't prevent this. You could install a filter on the return to prevent it happening again. You are best off taking the plate heat exchanger out and buying some cleaner from your local B & Q and that will get you going.
You are best off taking the plate heat exchanger out and buying some cleaner from your local B & Q and that will get you going.
Until it blocks up again. IF the op can get the hex out, AND put it all back together again.
How long have you been a RGI?
Cleaning or replacing the hex will only work so long. The system needs to be thoroughly cleaned. If this is done with a powerflush, the hex will be unblocked at the same time. Provided the flush is done properly of course.[/b]
Joined: 14 Dec 2008 Posts: 121 Location: United Kingdom Thanked: 8 times
Posted: Sat Oct 31, 2009 11:46 am Post Subject:
Debris in the form of flakes appears to be particular culprit in blocking plate hex. Certainly can't think of an instance on own installations when powerflushed of any problems.
On questioning customers most will say system was 'flushed' at time of install, (except if NORTHERN GAS customer) however the specifics of what this flush entailed are usually quite vague.
I have known flakes to be present on newly piped systems, several years old, which I have put down to either poor qual' manufacturing of rads (cheap) or insufficient/incorrect dosing of inhibitor.
What do you mean. This is the quality of the newer Heateam engineers
I agree the Heateam engineers here in Newcastle are useless. I had one of my customers wait 4 weeks for a diverter valve under warranty because the engineer told her he had to order it and it was out of stock. PTS had 5 in stock and the engineer who eventualy came back had one as his van stock??????? Where have all the good engineers gone Baxpoti?