House to container - 6mm 2 core SWA, armour only connected at house end.
Container:
SWA into insulated enclosure (or metal one inside a plastic box) so that no part of the metal gland is exposed, and the armour/gland is NOT electrically connected to the container.
Consumer unit with 30mA RCD main incomer, MCBs as required.
Quote:
Earth rod(s) for the main earth connection
Bonding from container to earth bar in CU.
Do you mean earth rod to earth bar in cu and bonding from doors and casing to earth bar in cu ?
Why would you not just extend the houses earth outside to the container?
You could, but the container will then need bonding to the main earth terminal in the house, which means at least 10mm cable, possibly larger depending on distance and how it was installed.
Why would you not just extend the houses earth outside to the container?
Quote:
You could, but the container will then need bonding to the main earth terminal in the house, which means at least 10mm cable, possibly larger depending on distance and how it was installed.
Total distance would be no more than 12m.
If I did it this way I assume I wold not need to use 3 core ?
Should I still use the swa armor as earth ?
How should the main bonding be installed ?
Surely this would be the most ecenomical solution.
so doesnt that mean the armour on 2 core SWA acts as a 22mm CSA conductor already?
If you wanted more you could always use 3 core and double up the armour and a core as earth?
The armour is a different material hence when using the not smaller than half the CSA of the earthing conductor I'd be inclined to think that to compare them they'd need to be in the same material or apply a correction factor.