Shipping container.

Goto page Previous  1, 2, 3, 4  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
barcelona

from United Kingdom

Joined: 28 May 2003
Posts: 44
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Nov 01, 2009 8:31 pm    Post Subject:
Reply with quote Thanks

flameport wrote:
House to container - 6mm 2 core SWA, armour only connected at house end.

Container:
SWA into insulated enclosure (or metal one inside a plastic box) so that no part of the metal gland is exposed, and the armour/gland is NOT electrically connected to the container.
Consumer unit with 30mA RCD main incomer, MCBs as required.
Quote:
Earth rod(s) for the main earth connection
Bonding from container to earth bar in CU.


Do you mean earth rod to earth bar in cu and bonding from doors and casing to earth bar in cu ?
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Sun Nov 01, 2009 8:34 pm    Post Subject:
Reply with quote Thanks

Yep. The rod provides the main earth, and all the metal work is bonded back to the MET, as with any normal installation.

The only difference is that the container is the extraneous conductive part(s) it this instance, rather than the water and gas supply as normal.

Obviously standard TT regs apply such as DP RCDs etc.

__________________
I downlights
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21983
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Sun Nov 01, 2009 8:50 pm    Post Subject:
Reply with quote Thanks

barcelona wrote:
My fist thought was 4mm but then thought 2.5 would be adequate.

Absolutely no way.

Please spend some time learning about circuit design and cable sizing before trying to do it in anger.

Here's a good start, but I also recommend getting some good electrical installation textbooks:

http://web.archive.org/web/20080213151445/http://www.kevinboone.com/cableselection_web.pdf

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
flameport

from United Kingdom

Joined: 10 Mar 2007
Posts: 1004
Location: Bournemouth,
United Kingdom
Thanked: 55 times

PostPosted: Sun Nov 01, 2009 8:53 pm    Post Subject:
Reply with quote Thanks

Aragorn84 wrote:
Why would you not just extend the houses earth outside to the container?

You could, but the container will then need bonding to the main earth terminal in the house, which means at least 10mm cable, possibly larger depending on distance and how it was installed.
Back to top
 Alert Moderators
barcelona

from United Kingdom

Joined: 28 May 2003
Posts: 44
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Nov 01, 2009 8:54 pm    Post Subject:
Reply with quote Thanks

ban-all-sheds wrote:
barcelona wrote:
My fist thought was 4mm but then thought 2.5 would be adequate.

Absolutely no way.

Please spend some time learning about circuit design and cable sizing before trying to do it in anger.

Here's a good start, but I also recommend getting some good electrical installation textbooks:

Quote:
http://web.archive.org/web/20080213151445/http://www.kevinboone.com/cableselection_web.pdf


I did read that article and worked out 2.5 was ok. Obviously I went wrong somewhere.
I also underestimated how much power I might use I think.

Cheers for all the reply's from everyone btw, very helpful.[/quote]
Back to top
 Alert Moderators
barcelona

from United Kingdom

Joined: 28 May 2003
Posts: 44
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Nov 01, 2009 9:07 pm    Post Subject:
Reply with quote Thanks

flameport wrote:
Aragorn84 wrote:
Why would you not just extend the houses earth outside to the container?

Quote:
You could, but the container will then need bonding to the main earth terminal in the house, which means at least 10mm cable, possibly larger depending on distance and how it was installed.


Total distance would be no more than 12m.
If I did it this way I assume I wold not need to use 3 core ?
Should I still use the swa armor as earth ?
How should the main bonding be installed ?
Surely this would be the most ecenomical solution.

Cheers.
Back to top
 Alert Moderators
Aragorn84

from United Kingdom

Joined: 03 Sep 2008
Posts: 333
Location: West Lothian,
United Kingdom
Thanked: 26 times

PostPosted: Sun Nov 01, 2009 9:20 pm    Post Subject:
Reply with quote Thanks

If you kept it TN-S and required a 10mm cable for keeping the house earth, how does the CSA of the cable armour compare with 10mm earthing cable?
Back to top
 Alert Moderators
barcelona

from United Kingdom

Joined: 28 May 2003
Posts: 44
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Nov 01, 2009 9:28 pm    Post Subject:
Reply with quote Thanks

Aragorn84 wrote:
If you kept it TN-S and required a 10mm cable for keeping the house earth, how does the CSA of the cable armour compare with 10mm earthing cable?


I mean would I use both or just the 10mm Earth cable.
Back to top
 Alert Moderators
barcelona

from United Kingdom

Joined: 28 May 2003
Posts: 44
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Nov 01, 2009 9:56 pm    Post Subject:
Reply with quote Thanks

If I used 6mm 3 core swa and doubled a core up with the armour would this be ok ?
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21983
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Sun Nov 01, 2009 10:29 pm    Post Subject:
Reply with quote Thanks

barcelona wrote:
I did read that article and worked out 2.5 was ok. Obviously I went wrong somewhere.

Where does it say that 2.5mm˛ is OK for 32A?


Aragorn84 wrote:
If you kept it TN-S and required a 10mm cable for keeping the house earth, how does the CSA of the cable armour compare with 10mm earthing cable?

See the tables here:

http://www.diynot.com/wiki/electrics:earthing_supply_types_and_bonding:swa_earthing

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Aragorn84

from United Kingdom

Joined: 03 Sep 2008
Posts: 333
Location: West Lothian,
United Kingdom
Thanked: 26 times

PostPosted: Sun Nov 01, 2009 10:40 pm    Post Subject:
Reply with quote Thanks

so doesnt that mean the armour on 2 core SWA acts as a 22mm CSA conductor already?

If you wanted more you could always use 3 core and double up the armour and a core as earth?
Back to top
 Alert Moderators
barcelona

from United Kingdom

Joined: 28 May 2003
Posts: 44
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Nov 01, 2009 10:46 pm    Post Subject:
Reply with quote Thanks

ban-all-sheds wrote:
barcelona wrote:
I did read that article and worked out 2.5 was ok. Obviously I went wrong somewhere.

Quote:
Where does it say that 2.5mm˛ is OK for 32A?


I got the calculation wrong.

Aragorn84 wrote:
If you kept it TN-S and required a 10mm cable for keeping the house earth, how does the CSA of the cable armour compare with 10mm earthing cable?

See the tables here:

Quote:
http://www.diynot.com/wiki/electrics:earthing_supply_types_and_bonding:swa_earthing


I read that.
Back to top
 Alert Moderators
Aragorn84

from United Kingdom

Joined: 03 Sep 2008
Posts: 333
Location: West Lothian,
United Kingdom
Thanked: 26 times

PostPosted: Sun Nov 01, 2009 10:50 pm    Post Subject:
Reply with quote Thanks

the other earthing page in the wiki shows the diameters of the earth conductors compared with the supply cables.

which suggests you only need a 10mm^2 earth, i just dont know if the earth is allowed to be provided by the SWA armour.

Might be worth running three core and using an extra core as earth as well just to ensure you've got plenty?
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 10887
Location: Cumbria,
United Kingdom
Thanked: 39 times

PostPosted: Sun Nov 01, 2009 10:53 pm    Post Subject:
Reply with quote Thanks

Aragorn84 wrote:
so doesnt that mean the armour on 2 core SWA acts as a 22mm CSA conductor already?

If you wanted more you could always use 3 core and double up the armour and a core as earth?


The armour is a different material hence when using the not smaller than half the CSA of the earthing conductor I'd be inclined to think that to compare them they'd need to be in the same material or apply a correction factor.
Back to top
 Alert Moderators
shetland

from United Kingdom

Joined: 25 Aug 2007
Posts: 19
Location: United Kingdom
Thanked: 1 time

PostPosted: Sun Nov 01, 2009 11:09 pm    Post Subject:
Reply with quote Thanks

Back to top
The following user says thank you to shetland for this useful post:
Spark123 (2 Nov)
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page Previous  1, 2, 3, 4  Next
Page 2 of 4

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Shipping container as a workshop 29 1100 Wed Oct 05, 2005 3:00 pm
earth needed in workshop (metal container) 17 600 Mon Dec 15, 2008 10:35 pm
240v supply into metal storage container 6 440 Tue Nov 21, 2006 9:07 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.