Ideal Isar


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
  View previous topic :: View next topic  
Author Message
compheat

from United Kingdom

Joined: 22 Nov 2005
Posts: 156
Location: Lancashire,
United Kingdom
Thanked: 1 time

PostPosted: Tue Nov 03, 2009 9:21 pm    Post Subject:
Ideal Isar
Reply with quote Thanks

Customer phoned to say boiler display as gone off and boiler no longer working in heating or hot water modes. fuses have been checked and there is 240v at boiler terminals. Any idea's icon_confused.gif

__________________
Keep the faith.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
petit_pablo

from United Kingdom

Joined: 18 Nov 2007
Posts: 1171
Location: Lincolnshire,
United Kingdom
Thanked: 39 times

PostPosted: Tue Nov 03, 2009 9:24 pm    Post Subject:
Reply with quote Thanks

PCB

__________________
BG Engineer just trying to help for a change!
Back to top
 Alert Moderators
compheat

from United Kingdom

Joined: 22 Nov 2005
Posts: 156
Location: Lancashire,
United Kingdom
Thanked: 1 time

PostPosted: Tue Nov 03, 2009 9:29 pm    Post Subject:
Reply with quote Thanks

thats what i thought but the last time i changed PCB Ideal then told me i should of changed the fan as well. (different fault)

__________________
Keep the faith.
Back to top
 Alert Moderators
petit_pablo

from United Kingdom

Joined: 18 Nov 2007
Posts: 1171
Location: Lincolnshire,
United Kingdom
Thanked: 39 times

PostPosted: Tue Nov 03, 2009 9:38 pm    Post Subject:
Reply with quote Thanks

What model Isar is it? HE or M series? Make a good check of boiler for water leaks too. AAV on M series can drip down onto connecting cable from PCB to user control and short board.

__________________
BG Engineer just trying to help for a change!
Back to top
 Alert Moderators
compheat

from United Kingdom

Joined: 22 Nov 2005
Posts: 156
Location: Lancashire,
United Kingdom
Thanked: 1 time

PostPosted: Tue Nov 03, 2009 9:49 pm    Post Subject:
Reply with quote Thanks

Its approx 3 years old, I think its an HE.dont think its been serviced since new.

__________________
Keep the faith.
Back to top
 Alert Moderators
gas4you

from United Kingdom

Joined: 23 Feb 2007
Posts: 14314
Location: Norwich,
United Kingdom
Thanked: 41 times

PostPosted: Tue Nov 03, 2009 10:13 pm    Post Subject:
Reply with quote Thanks

Fans are notorious for taking out pcb's on these.

You will need to check the fan before switching on with the new pcb fitted.

Follow MI's to do this.

__________________
Dave
DRL Gas Services
Back to top
 Alert Moderators
compheat

from United Kingdom

Joined: 22 Nov 2005
Posts: 156
Location: Lancashire,
United Kingdom
Thanked: 1 time

PostPosted: Wed Nov 04, 2009 9:57 pm    Post Subject:
Reply with quote Thanks

Went to have a look today, Isar24HE 3 years old this month. 240v either side of rocker switch, 240v going to main PCB but no display and nothing working, Spoke to tech they said its main board, I've checked resistance across fan 110 ohms they said thats ok so just replace board. phoned curzons been quoted £130 plus vat icon_sad.gif so back tomorrow and hope it does the job the customer is 76years old and p****d off.

__________________
Keep the faith.
Back to top
 Alert Moderators
petit_pablo

from United Kingdom

Joined: 18 Nov 2007
Posts: 1171
Location: Lincolnshire,
United Kingdom
Thanked: 39 times

PostPosted: Wed Nov 04, 2009 9:59 pm    Post Subject:
Reply with quote Thanks

compheat wrote:
Went to have a look today, Isar24HE 3 years old this month. 240v either side of rocker switch, 240v going to main PCB but no display and nothing working, Spoke to tech they said its main board, I've checked resistance across fan 110 ohms they said thats ok so just replace board. phoned curzons been quoted £130 plus vat icon_sad.gif so back tomorrow and hope it does the job the customer is 76years old and p****d off.


They had best get used to it, wont be the last time they need a repair.

__________________
BG Engineer just trying to help for a change!
Back to top
 Alert Moderators
compheat

from United Kingdom

Joined: 22 Nov 2005
Posts: 156
Location: Lancashire,
United Kingdom
Thanked: 1 time

PostPosted: Thu Nov 05, 2009 10:15 pm    Post Subject:
Reply with quote Thanks

changed the PCB today boiler is now workig icon_smile.gif but what a job getting PCB into the 2 brackets at either side I must of been doing something wrong really struggled icon_confused.gif

__________________
Keep the faith.
Back to top
 Alert Moderators
Garfeild

from Netherlands

Joined: 19 Jan 2007
Posts: 338
Location: Netherlands
Thanked: 4 times

PostPosted: Thu Nov 05, 2009 11:54 pm    Post Subject:
Reply with quote Thanks

compheat wrote:
changed the PCB today boiler is now workig icon_smile.gif but what a job getting PCB into the 2 brackets at either side I must of been doing something wrong really struggled icon_confused.gif


You probably got the alloy "elbows" round the wrong way they are handed
Back to top
 Alert Moderators
kevindgas

from United Kingdom

Joined: 28 Mar 2006
Posts: 2461
Location: Southampton,
United Kingdom
Thanked: 37 times

PostPosted: Fri Nov 06, 2009 12:07 am    Post Subject:
Reply with quote Thanks

just undo the two screws on one side and its easy (i should know the amount of these F******g boards i've had to change)
heap of s***te!

__________________
don't buy an ideal as they won't honour the guarantee!!
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
ideal isar problem 2 120 Tue Jan 20, 2009 9:33 pm
Problem with Ideal Isar HE30 boiler 21 2220 Tue Jun 12, 2007 6:26 pm
ideal isar he30 12 260 Fri Jan 16, 2009 8:11 pm
ideal Isar prob (join the queue) 2 140 Wed Jan 14, 2009 10:11 pm
Ideal Isar He 30 6 440 Tue Jul 17, 2007 9:11 pm