Hot Tub Problem

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
pkmjm

from United Kingdom

Joined: 13 Jul 2006
Posts: 15
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Nov 01, 2009 2:02 pm    Post Subject:
Hot Tub Problem
Reply with quote Thanks

Hi There,

I wonder if you would be able to help me with a problem with our hot tub.

We have had our hot tub for about a year and a half and everything has worked fine. But last week the mcb to the hot tub kept tripping and I'm not sure why.

When you reset the mcb the hot tub will have power and all the jets etc work fine, but when it has finished it's priming cycle and (I assume) the motor kicks in the mcb trips out.

Do you think the motor might be faulty, or could there be another reason. Any advise would be appreciated
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
bongos

from United Kingdom

Joined: 07 Jul 2007
Posts: 424
Location: Sheffield,
United Kingdom
Thanked: 9 times

PostPosted: Sun Nov 01, 2009 2:47 pm    Post Subject:
Reply with quote Thanks

What size/type of cable has the hot tub been installed on? Is it on its own circuit?

What is its power rating of the hot tub? What size is the MCB protecting the circuit?

Was there any paperwork supplied when you had it installed?

Much more info needed! If you can post a pic of your CU then this would also help. icon_wink.gif
Back to top
 Alert Moderators
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 4943
Location: Oxfordshire,
United Kingdom
Thanked: 63 times

PostPosted: Sun Nov 01, 2009 4:11 pm    Post Subject:
Re: Hot Tub Problem
Reply with quote Thanks

He said
pkmjm wrote:


We have had our hot tub for about a year and a half and everything has worked fine. But last week the mcb to the hot tub kept tripping and I'm not sure why.

Bongos, so that would imply the problem is not due to overload!

Are you absolutley sure the thing that trips is an MCB?
Perhaps it is an RCD or RCBO.

Does it have a test button on it? what is written on it?
Does it say BS61009-1 or BS61008-1??
Post a picture.

__________________
TTC

When you get to the end of your rope, tie a knot and hang on. - F.D.R.
Back to top
 Alert Moderators
pkmjm

from United Kingdom

Joined: 13 Jul 2006
Posts: 15
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Nov 01, 2009 5:51 pm    Post Subject:
Reply with quote Thanks

Hi and thanks for your reply's

I hope these pictures help

This is the small fuse box near to the hot tub, the mcb that trips to the right of the Red switch

Fuse Box Next to Hot Tub
Fuse Box Next to Hot Tub


These are of the main fuse box in the house

Fuse Box House
Fuse Box House
Fuse Box House
Fuse Box House
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 10888
Location: Cumbria,
United Kingdom
Thanked: 39 times

PostPosted: Sun Nov 01, 2009 6:02 pm    Post Subject:
Reply with quote Thanks

The device which is tripping is an RCBO which is an MCB combined with an RCD.
This means the problem could be associated with an earth leakage as opposed to an overcurrent.
I take it the motor works during priming?
Could be the heating element has gone down.

btw whoever installed the main consumer unit needs to look at section 314 of the regs - it doesn't comply having all the lights and sockets on a single RCD.
It wouldn't have been rocket science to put lights on RCBOs on the other side of the board.
Back to top
 Alert Moderators
electronicsuk

from United Kingdom

Joined: 07 May 2007
Posts: 1464
Location: Lincolnshire,
United Kingdom
Thanked: 23 times

PostPosted: Sun Nov 01, 2009 6:02 pm    Post Subject:
Reply with quote Thanks

Those are RCBOs, not MCBs, and they combine the function of an RCD and MCB into a single unit. Chances are that water/dampness has worked its way into some electrical part in the hot tub, causing an earth fault and the RCBO to trip. Best not to use it at all until you can get it checked over and sorted out.

__________________
Matthew

"I told you, I only wrote that poem to test my printer!"
Back to top
 Alert Moderators
flameport

from United Kingdom

Joined: 10 Mar 2007
Posts: 1004
Location: Bournemouth,
United Kingdom
Thanked: 55 times

PostPosted: Sun Nov 01, 2009 6:03 pm    Post Subject:
Reply with quote Thanks

That device is an RCBO, so the problem is most likely an earth fault within the hot tub. Probably the heating element.
Back to top
 Alert Moderators
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 4943
Location: Oxfordshire,
United Kingdom
Thanked: 63 times

PostPosted: Sun Nov 01, 2009 7:13 pm    Post Subject:
Reply with quote Thanks

HA just as i thought! icon_cool.gif

__________________
TTC

When you get to the end of your rope, tie a knot and hang on. - F.D.R.
Back to top
 Alert Moderators
pkmjm

from United Kingdom

Joined: 13 Jul 2006
Posts: 15
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon Nov 02, 2009 7:50 pm    Post Subject:
Reply with quote Thanks

Thanks to everyone who posted a reply.

I have arranged for an electrician to take a look.
Back to top
 Alert Moderators
sparkysm

from United Kingdom

Joined: 30 Apr 2009
Posts: 21
Location: Northamptonshire,
United Kingdom
Thanked: 0 times

PostPosted: Tue Nov 03, 2009 10:03 pm    Post Subject:
Reply with quote Thanks

sparky123 how can you say the installation doesn`t comply when you know nothing about the installation, at least ask questions before slagging off someone elses work....how do you know it doesn`t comply?????
Back to top
 Alert Moderators
333rocky333

from United Kingdom

Joined: 12 Jan 2008
Posts: 2174
Location: Essex,
United Kingdom
Thanked: 16 times

PostPosted: Tue Nov 03, 2009 10:12 pm    Post Subject:
Reply with quote Thanks

Spark123 wrote:


btw whoever installed the main consumer unit needs to look at section 314 of the regs - it doesn't comply having all the lights and sockets on a single RCD.



pkmjm wrote:

These are of the main fuse box in the house

Fuse Box House
Fuse Box House
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 10888
Location: Cumbria,
United Kingdom
Thanked: 39 times

PostPosted: Wed Nov 04, 2009 5:06 pm    Post Subject:
Reply with quote Thanks

Do you think that complies with section 314 of the regs sparkysm?
Back to top
 Alert Moderators
pkmjm

from United Kingdom

Joined: 13 Jul 2006
Posts: 15
Location: United Kingdom
Thanked: 0 times

PostPosted: Sat Nov 07, 2009 1:42 pm    Post Subject:
Reply with quote Thanks

Just an update

I have now found that the problem was due to a faulty ozone generator.

Thank you for your help and advise. icon_biggrin.gif
Back to top
 Alert Moderators
pkmjm

from United Kingdom

Joined: 13 Jul 2006
Posts: 15
Location: United Kingdom
Thanked: 0 times

PostPosted: Sat Nov 07, 2009 2:10 pm    Post Subject:
Reply with quote Thanks

Spark123 wrote:
Do you think that complies with section 314 of the regs sparkysm?


Hi Spark123,

I had a word with my electrician regarding your comments about the new consumer unit.

I won't print everything he said, as there could be children reading this. But his main point was the each of the curcuits is protected by an RCBO and this meets all relevant regs.
Back to top
 Alert Moderators
electronicsuk

from United Kingdom

Joined: 07 May 2007
Posts: 1464
Location: Lincolnshire,
United Kingdom
Thanked: 23 times

PostPosted: Sat Nov 07, 2009 3:13 pm    Post Subject:
Reply with quote Thanks

pkmjm wrote:
Spark123 wrote:
Do you think that complies with section 314 of the regs sparkysm?


Hi Spark123,

I had a word with my electrician regarding your comments about the new consumer unit.

I won't print everything he said, as there could be children reading this. But his main point was the each of the curcuits is protected by an RCBO and this meets all relevant regs.


Sorry, but your electrician seems to be talking bull, as the main fuse box picture does not show ANY RCBOs at all. It's a split load board with a single RCD and main switch, and there is almost no way to install one of these (without RCBOs) and have a compliant installation since the 17th edition of BS7671 came into force.

__________________
Matthew

"I told you, I only wrote that poem to test my printer!"
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Security Light problem – Always on 3 280 Mon Jan 07, 2008 4:58 pm
New light fitting problem 2 220 Wed Jan 09, 2008 8:26 am
Problem with ring main 30 1520 Wed Jan 02, 2008 1:02 pm
cooker/kitchen ciruit problem 4 300 Sat Dec 22, 2007 7:27 pm
electronic problem i think, tv not getting power ! 6 380 Mon Dec 10, 2007 4:55 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.