Soil Pipe Fall - advice please
Reply with quote Thanks

Hi

I'm moving the WC in our bathroom which is on the ground floor. The soil pipe currently drops vertically about 850mm to the bottom of the crawl space under the floor where it is connected to a 90 deg bend taking the waste outside.

The new toilet outlet will be approx 2m away from the existing outlet. Am I better to run the new soil pipe from the WC to the existing 90 deg bend (ie at about 25 deg) or am I better to have a slight fall from the WC outlet until it is over the 90 deg bend and then drop vertically?

If its the latter what is the correct fall? I think I read somewhere else on the forum 1 in 40 is right?

Thanks

F
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 9933
Location: Bath,
United Kingdom
Thanked: 240 times

PostPosted: Fri Nov 06, 2009 7:39 pm    Post Subject:
Reply with quote Thanks

Best to run it at 40degs and drop vertically into the bend.
Back to top
The following user says thank you to doitall for this useful post:
Pickup (7 Nov)
 Alert Moderators
Richard C

from United Kingdom

Joined: 26 Apr 2005
Posts: 4325
Location: Norfolk,
United Kingdom
Thanked: 51 times

PostPosted: Fri Nov 06, 2009 8:19 pm    Post Subject:
Re: Soil Pipe Fall - advice please
Reply with quote Thanks

Pickup wrote:
Hi
I think I read somewhere else on the forum 1 in 40 is right?

That’s fine; 18mm per metre is the minimum for soil but a fall of 25 degrees is far too steep let along 40 degrees icon_confused.gif

It maybe me but I think there might be some confusion here; if the fall is too great over a run of any appreciable distance the s***te won’t flow away with the water, possibly leading to the obvious nasty results. icon_eek.gif

As it's on the ground floor, do you have a vented soil stack or an AAV fitted? If not you then it won’t comply with Building Regs.

__________________
Richard C
Back to top
The following user says thank you to Richard C for this useful post:
Pickup (7 Nov)
 Alert Moderators
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 9933
Location: Bath,
United Kingdom
Thanked: 240 times

PostPosted: Fri Nov 06, 2009 9:04 pm    Post Subject:
Reply with quote Thanks

Yes I did mean 1-40 icon_redface.gif
Back to top
 Alert Moderators
Richard C

from United Kingdom

Joined: 26 Apr 2005
Posts: 4325
Location: Norfolk,
United Kingdom
Thanked: 51 times

PostPosted: Fri Nov 06, 2009 10:42 pm    Post Subject:
Reply with quote Thanks

doitall wrote:
Yes I did mean 1-40 icon_redface.gif

An unusual one for you m8 icon_lol.gif icon_wink.gif

__________________
Richard C
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 24311
Location: London,
United Kingdom
Thanked: 193 times

PostPosted: Fri Nov 06, 2009 10:46 pm    Post Subject:
Reply with quote Thanks

On this occasion I will agree that DIA will have known it was 1:40 and it was a brain to keyboard interface error!

Tony

__________________
ARGI Registered Engineer
Back to top
 Alert Moderators
doitall

from United Kingdom

Joined: 08 Jan 2005
Posts: 9933
Location: Bath,
United Kingdom
Thanked: 240 times

PostPosted: Fri Nov 06, 2009 10:47 pm    Post Subject:
Reply with quote Thanks

Richard C wrote:
doitall wrote:
Yes I did mean 1-40 icon_redface.gif

An unusual one for you m8 icon_lol.gif icon_wink.gif


Not thinking what the fingers are doing, I just read 25deg, and typed no, it should be 40 degs An head banging emoticon. icon_lol.gif
Back to top
 Alert Moderators
Richard C

from United Kingdom

Joined: 26 Apr 2005
Posts: 4325
Location: Norfolk,
United Kingdom
Thanked: 51 times

PostPosted: Fri Nov 06, 2009 11:06 pm    Post Subject:
Reply with quote Thanks

Wish Agile was my wingman icon_wink.gif

__________________
Richard C
Back to top
 Alert Moderators
Pickup

from United Kingdom

Joined: 28 Oct 2009
Posts: 11
Location: Aberdeen,
United Kingdom
Thanked: 0 times

PostPosted: Sat Nov 07, 2009 6:30 pm    Post Subject:
Thnak you.
Reply with quote Thanks

Guys,

many thanks, existing soil pipe is vented outside (2 pipe system?) so hopefully no problems.

Thanks again.

F
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Back fall on soil pipe 3 200 Tue Jan 06, 2009 9:33 am
What fall do I need on a soil pipe from a toilet? 2 520 Mon Feb 13, 2006 8:09 am
Toilet plumbing fall: Running pipe across concrete roof 2 340 Fri May 28, 2004 11:02 pm
waste water pipe, lenght and fall 6 580 Tue Jul 31, 2007 5:07 am
Hot Water Options - Likely Fall in Mains Pressure 10 580 Wed Sep 28, 2005 9:12 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.