Water leaking through tundish
Reply with quote Thanks

We're really confused by this problem:
We have a Tribune HE unvented system which is roughly 3 years old. A while ago we noticed cold water dripping through the tundish. We replaced the Pressure relief valve & that temporarily cured the problem. Then within a week or so, we noticed hot water dripping through the tundish. The plumber changed the valve attached to side of water tank & that also temporarily cured the problem.
However, cold water has once again started dripping through the tundish. On advice of a plumber, we were advised that the pressure expansion vessel (potable) needed replacing. We have replaced that, but water is still dripping through. It varies from a drip, to a continual stream. Our plumber advised us to keep the mains turned off (unless we needed it for short periods of time) & we've turned the boiler off so we don't have any hot water.
We've also replaced the valve from the CH expansion vessel (red one) & the valve seems okay, as well as it's pressure.
Does anyone have any other suggestions. I'm at a loss of what is causing this problem.
I'm not very clued up on plumbing so any suggestions is 'lay-mans' terms would be appreciated.
Thank you
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 19149
Location: Tennessee,
United States of America
Thanked: 400 times

PostPosted: Sat Nov 07, 2009 3:41 pm    Post Subject:
Reply with quote Thanks

Quote:
we were advised that the pressure expansion vessel (potable) needed replacing.


was the precharge pressure in the new one 3 bar icon_question.gif

__________________
a little thanks

goes a long way
Back to top
 Alert Moderators
picasso

from United Kingdom

Joined: 08 Apr 2008
Posts: 500
Location: Essex,
United Kingdom
Thanked: 66 times

PostPosted: Sat Nov 07, 2009 3:44 pm    Post Subject:
Reply with quote Thanks

as above or the pressure reducing valve is crackered.
Back to top
 Alert Moderators
gaigy

from United Kingdom

Joined: 07 Nov 2009
Posts: 6
Location: Berkshire,
United Kingdom
Thanked: 0 times

PostPosted: Sat Nov 07, 2009 3:44 pm    Post Subject:
Reply with quote Thanks

Thanks for your reply.

Yes it was, we got a like for like replacement & checked the pressure with a foot pump.
Back to top
 Alert Moderators
kevindgas

from United Kingdom

Joined: 28 Mar 2006
Posts: 2461
Location: Southampton,
United Kingdom
Thanked: 37 times

PostPosted: Sat Nov 07, 2009 3:49 pm    Post Subject:
Reply with quote Thanks

as piccasso says look at the pressure reducing valve (fitted to cold inlet pipe) as that is most likely failing to regulate the pressure.

A G3 unvented qualified person should be dealing with this and should have the necessary guage to check the water pressure.

__________________
don't buy an ideal as they won't honour the guarantee!!
Back to top
 Alert Moderators
gaigy

from United Kingdom

Joined: 07 Nov 2009
Posts: 6
Location: Berkshire,
United Kingdom
Thanked: 0 times

PostPosted: Sat Nov 07, 2009 3:55 pm    Post Subject:
Reply with quote Thanks

Would there be something causing the valve to fail? We only replaced this about 4 - 6 weeks ago, so I guess there must be something causing them to continually fail. Would there be too much pressure in the system?
Back to top
 Alert Moderators
kevindgas

from United Kingdom

Joined: 28 Mar 2006
Posts: 2461
Location: Southampton,
United Kingdom
Thanked: 37 times

PostPosted: Sat Nov 07, 2009 4:09 pm    Post Subject:
Reply with quote Thanks

gaigy wrote:
Would there be something causing the valve to fail? We only replaced this about 4 - 6 weeks ago, so I guess there must be something causing them to continually fail. Would there be too much pressure in the system?


are you sure? there are 2 items on the cylinder 1. a reducing valve and 2. a relief valve
1. limits the pressure enteringthe cylinder
2. limits the temp and pressure already in the cylinder

the pressure reducing valve can have up to 10 bar inlet and around 3 bar outlet to the cylinder

__________________
don't buy an ideal as they won't honour the guarantee!!
Back to top
 Alert Moderators
gaigy

from United Kingdom

Joined: 07 Nov 2009
Posts: 6
Location: Berkshire,
United Kingdom
Thanked: 0 times

PostPosted: Sat Nov 07, 2009 4:22 pm    Post Subject:
Reply with quote Thanks

okay - sorry, I misunderstood earlier (as I said I'm not technically minded about this, I only learnt the term 'pressure reducing valve' 6 weeks ago...)

No, we haven't replaced the 3 bar pressure reducing valve.

We've only replaced the Expansion relief valve (6 bar) & the Temp & Pressure relief valve, oh & of course the expansion vessel.

Is this a potentially hazardous situation? And are we right to keep the water turned off most of the time? Are we safe running the central heating? We've been keeping that off apart from short bursts when it gets too cold.

Thank you very much for all your assistance with this.
Back to top
 Alert Moderators
gaigy

from United Kingdom

Joined: 07 Nov 2009
Posts: 6
Location: Berkshire,
United Kingdom
Thanked: 0 times

PostPosted: Sun Nov 08, 2009 10:13 am    Post Subject:
Reply with quote Thanks

Also, is there anyway we can test to see if it is the 3 bar pressure reducing valve that's faulty.

they've changed the part a bit from the original one which is going to require some changes to the pipework in order to get it fitted. I would hate to go to all that expense if it's not going to fix the problem.

I've uploaded a picture - just to be sure - it's the grey valve that you're suggesting needs replacement? The pipe it's on comes up from where the cold water main tap is. We've replaced the red one above it already.
[/img]
Back to top
 Alert Moderators
rojaca

from United Kingdom

Joined: 14 Dec 2008
Posts: 120
Location: United Kingdom
Thanked: 8 times

PostPosted: Sun Nov 08, 2009 10:25 am    Post Subject:
Reply with quote Thanks

Deleted. realised was talking carp
Back to top
 Alert Moderators
rojaca

from United Kingdom

Joined: 14 Dec 2008
Posts: 120
Location: United Kingdom
Thanked: 8 times

PostPosted: Sun Nov 08, 2009 10:56 am    Post Subject:
Reply with quote Thanks

Sounds like you've already changed quite a few parts unecessarily.
Without wanting to sound melodramatic the PRV and TPRV are safety devices. If either of these are dripping then you have a safety issue. As your cylinder does not have an internal baffle then i'm sure the M.I would advise you to contact a suitable qualified (unvented hot water) engineer straightaway.
Do not be misled by the fact that your cylinder is "only plumbing", the safety issues involved regarding UVHS in my opinion should be taken as seriously as those regarding gas work.
Back to top
 Alert Moderators
picasso

from United Kingdom

Joined: 08 Apr 2008
Posts: 500
Location: Essex,
United Kingdom
Thanked: 66 times

PostPosted: Sun Nov 08, 2009 11:00 am    Post Subject:
Reply with quote Thanks

to answer your question, yes the grey valve is the prv and needs to be changed, also ok to use your heating but probably not a good idea to use your hot water until its fixed.
Back to top
 Alert Moderators
kidgreen61

from United Kingdom

Joined: 08 Mar 2009
Posts: 473
Location: Staffordshire,
United Kingdom
Thanked: 15 times

PostPosted: Sun Nov 08, 2009 11:02 am    Post Subject:
Reply with quote Thanks

I recently came across a similar problem to yours.

After a bit of headscratching, I realised the cause of the dripping was mains cold water passing through a mixer valve somewhere in the house.

The solution is to fit a checkvalve on the hot water outlet of your cylinder.

__________________
"The Morning Sun When It's In Your Face Really Shows Your Age"
Back to top
 Alert Moderators
picasso

from United Kingdom

Joined: 08 Apr 2008
Posts: 500
Location: Essex,
United Kingdom
Thanked: 66 times

PostPosted: Sun Nov 08, 2009 11:09 am    Post Subject:
Reply with quote Thanks

kidgreen61 wrote:
I recently came across a similar problem to yours.

After a bit of headscratching, I realised the cause of the dripping was mains cold water passing through a mixer valve somewhere in the house.

The solution is to fit a checkvalve on the hot water outlet of your cylinder.


if you look at the picture you will see there is a balanced take off for the showers, so its very unlikely that unbalanced pressures are causing this problem.
Back to top
 Alert Moderators
kidgreen61

from United Kingdom

Joined: 08 Mar 2009
Posts: 473
Location: Staffordshire,
United Kingdom
Thanked: 15 times

PostPosted: Sun Nov 08, 2009 11:15 am    Post Subject:
Reply with quote Thanks

if you look at the picture you will see there is a balanced take off for the showers, so its very unlikely that unbalanced pressures are causing this problem.[/quote]

Kitchen tap?

__________________
"The Morning Sun When It's In Your Face Really Shows Your Age"
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Drip from tundish - OSO unvented water heater? 2 1880 Mon May 07, 2007 4:46 pm
Hot water from tundish - unvented system 11 540 Wed Nov 12, 2008 11:45 am
Unvented Cylinder Dripping into tundish 6 360 Wed Jun 11, 2008 8:30 am
Visible tundish 4 480 Sun Aug 05, 2007 11:05 pm
Tundish Overflow 6 200 Mon Jul 27, 2009 3:40 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.