how radiator thermostat valves work with room thermostats


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
riffraff

from United Kingdom

Joined: 28 Dec 2009
Posts: 33
Location: Armagh,
United Kingdom

PostPosted: Mon Aug 16, 2010 10:24 pm Reply with quote

Hi All (again),

Last winter we were tortured with constantly adjusting the two thermostats we have for central heating.
One is for upstairs and the the other for downstairs.

Trouble was that (as expected i suppose) with the doors shut some rooms were either too hot or too cold compared with were the thermostats are.

My father in law said i should get individual valve thermostats for each radiator but i cant figure out in my head how that would work with the room thermostats because they ultimately control whether or not the central heating comes on.

Say i install the thermostat valves and set each room radiator to 22 degrees, what do i set the room thermostats to? If i set those to 22 as well then there's every chance that it'll knock off the heating when it detects 22 meaning the radiator valves wont be able to much. If i set the room thermostats to something really high to avoid that...like 30 degrees then even though the room radiators will be shutoff at 22 degrees the heating will still be burning away to try and maintain the 30 degree setting for the room thermostats.

The other reaon I'm asking is because i was thinking of replacing the analog room thermostats with digital (for quicker responses to temperatures) but i dont want to spend the money if installing radiator thermostats would mean i dont need to.

I guess i dont understand how the system is supposed work.
Any comments?

Thanks in advance.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 23673
Location: Georgia,
United States of America
Thanked: 918 times

PostPosted: Mon Aug 16, 2010 11:29 pm Reply with quote

you dont put a trv on the rad in the room with the stat icon_wink.gif
Back to top
The following user says thank you to kevplumb for this useful post:
riffraff (17 Aug 2010)
 Alert Moderators
croydoncorgi

from United Kingdom

Joined: 06 Jun 2004
Posts: 4024
Location: London,
United Kingdom
Thanked: 333 times

PostPosted: Tue Aug 17, 2010 12:43 am Reply with quote

The basic idea of room stat(s) isto control the BOILER so that it provides heat until ALL the building is warmed up. With no TRVs, in theory the flows through the rads should be balanced and the rads themselves sized accurately, so that all the rooms warm up nicely (with the doors shut) and then the boiler shuts down until everything has cooled down and needs to be warmed up again. And yes, there WILL be a cycle of warmer - hot - cooler - cold - warmer, etc. in some or all of the rooms. Correct positioning of the room stats is critical to avoid cold rooms when the heating cuts off too early or everything getting too hot because the room with the stat is under-heated and lags behind the rest.

If you have TRVs on all the rads, they will (supposedly) close when each room reaches its individual setpoint. The trick then is to ensure that the roomstat stops heating boiler as soon as there's no demand from anywhere and restarts it as soon as ONE of the rooms requires heat. Almost as difficult as balancing the old way! TRVs can get confused eg. by having curtains draped over them and sometimes just don't work very well anyway.

If you currently have NO TRVs, a better investment might be a boiler capable of modulation with a weather compensator or room compensating controller.
Back to top
The following user says thank you to croydoncorgi for this useful post:
riffraff (17 Aug 2010)
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 8677
Location: Sussex,
United Kingdom
Thanked: 999 times

PostPosted: Tue Aug 17, 2010 8:27 am Reply with quote

Reply edited 24/8/10 - see below

riffraff wrote:
Last winter we were tortured with constantly adjusting the two thermostats we have for central heating. One is for upstairs and the the other for downstairs.

So your house is zoned with two motorized valves, one controlling upstairs and the other downstairs?

Where are the two thermostats located - in the hall and on the landing? The problem with that arrangement is that the upstairs stat will receive heat from the rad on the landing and from the rad in the hall (heat rises).

Quote:
I can't figure out in my head how that would work with the room thermostats because they ultimately control whether or not the central heating comes on.

That's why you do not have a TRV on the rad in the same area as the wall thermostat. If you set stat to 20C and TRV to 22V, the boiler will cut off before the TRV has reached temperature. If you set stat to 22C and TRV to 20C, the thermostat will never reach 22C, so the boiler will run continuously.

For TRVs to work properly, (a) the system must be properly balanced, and (b) the area with the room stat must be the last to reach temperature, so the TRVs have a chance of working. This usually means having the room stat in the coldest area. Although some advocate having it in the living area on the assumption that will be the hottest area of the house (21C) and the other rooms will be at a lower temperature.

If you install wireless thermostats you can easily experiment with the location - before fitting the TRVs, of course.

If you find that the room stat turns the boiler off before the TRVs have operated, you should close down, a bit at a time, the wheel valve on the radiator without a TRV. This will reduce the output from that rad so the area takes longer to heat up.
Back to top
The following user says thank you to D_Hailsham for this useful post:
riffraff (17 Aug 2010)
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Drayton ZA5 valves and Danfoss room thermostats 3 60 Sat Mar 02, 2013 1:22 pm
Boiler thermostats - how exactly do they work? 5 200 Tue Dec 17, 2013 4:53 pm
Do Optimum Start Thermostats Work? 43 2200 Mon Aug 23, 2010 10:25 am
Room Thermostat v Valve Thermostats 25 2060 Mon Jul 21, 2008 10:19 am
Problems with Osma RT-NV2 room thermostats 3 80 Sat Feb 11, 2012 4:00 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.