A hob can be any where between 2.7Kw for a domino to 10kw for an induction and an oven anywhere between 2.2kw to 5kw with fan plus top and bottom elements. Some have timers to alternate between top element and fan element and are still under 3kw others are well over.
The hob and oven will have a minimum requirement but also may have a maximum and with the latter it is some times impossible to supply them both from the same automatic disconnection device. (Fuse/MCB)
With most houses having a 32A supply to cooker point with 6mm cable giving a max of 7.4kw allowing for diversity (i.e. not induction hob) then likely you can use a 6kw hob and 3kw oven together from a 32A supply but with induction hobs 1) they are often fan cooled so you don't want the supply to trip and 2) often well over 6kw 3) because of boost diversity can't be used in same way.
Having said that my stand alone oven and hob states it needs a 32A supply and has two 3kw rings a 3.7kw ring and a 2.3kw ring and top oven with single element and bottom oven with three elements back (fan) top and bottom. There are some interlinks to stop you using all rings on max and maybe there are other interlinks to stop overloading which does point out why you have to read what the manufacture recommends.
If your oven is over 3kw likely you will need second supply. Under 3kw likely you will need a fused connection unit.