I have been looking at a commercial dishwasher attached by a 13amp fused spur to a 32amp rcbo protected ring circuit. The site is a village hall kitchen with a fridge, water heater, 6 double sockets and the commercial dishwasher on the ring.
The dishwasher had not worked for 4 years. I found the 13amp fuse in the spur dead, replaced it, tried the dishwasher and the fuse blew again. I contacted the manufacturer and discovered that it has a 2.8kw water heater and a 735 watt water pump. Both can operate together giving a 3.535 kw load for short periods (20 second bursts, about half a dozen before the washer gets up to temperature in about 40 minutes). My sums say this will generate 15 amps or so hence blown fuses.
I fitted a 20amp dp switch in place of the fused spur. Dishwasher works fine and the rcbo stands up with fridge, water heater, 3kw kettle on as well.
I'm uncomfortable with the loading however because the dishwasher is at one end of the ring. The ring is cabled in 2.5mm T&E.
I'm at a loss as to how best to protect the ring from overload with just the dp switch in place. I'm thinking that I may need to run a radial cable to serve the dishwasher. I would prefer to keep the job simple however.
Am I being over concerned? How can I simply introduce over current protection at say 16amps at the dishwasher?
The dishwasher had not worked for 4 years. I found the 13amp fuse in the spur dead, replaced it, tried the dishwasher and the fuse blew again. I contacted the manufacturer and discovered that it has a 2.8kw water heater and a 735 watt water pump. Both can operate together giving a 3.535 kw load for short periods (20 second bursts, about half a dozen before the washer gets up to temperature in about 40 minutes). My sums say this will generate 15 amps or so hence blown fuses.
I fitted a 20amp dp switch in place of the fused spur. Dishwasher works fine and the rcbo stands up with fridge, water heater, 3kw kettle on as well.
I'm uncomfortable with the loading however because the dishwasher is at one end of the ring. The ring is cabled in 2.5mm T&E.
I'm at a loss as to how best to protect the ring from overload with just the dp switch in place. I'm thinking that I may need to run a radial cable to serve the dishwasher. I would prefer to keep the job simple however.
Am I being over concerned? How can I simply introduce over current protection at say 16amps at the dishwasher?