I live in a first floor flat and want to alter the lighting on the stairs. (Mainly so I can fit an extra draught proof door as it is freezing).
I need to move one of the existing light fittings and am thinking that if I replace the existing fluorescent with a maintained LED fitting like this: http://www.beamled.com/biard-7w-emergency-led-bulkhead-maintained I could use it as an ordinary light but have an emergency light too.
Can I still switch it on and off and basically use it as an ordinary light but have the security of knowing in the event of a power failure my stairs will have some light? As it is one a circuit with another light on 2-way switching is that a problem.
 
Sponsored Links
The existing lighting point would need to have a PERMANENT supply as well as the existing SWITCHED supply, this is to keep the batteries charged.
A majority of lighting points would have both but it would need confirming
 
The existing lighting point would need to have a PERMANENT supply as well as the existing SWITCHED supply, this is to keep the batteries charged.
A majority of lighting points would have both but it would need confirming

That is not a problem as there is a permanent live at the light fitting.
 
If this is your own private property i cant see a problem, if it was a communal stairs or a commercial area then, emergency lighting would have to conform to standards and usually include test facilities.
Changing a normal light to an emergency in a private dwelling dont have any special regs as far as i know
 
Sponsored Links
Cannot see your fitting in the above link.
Normally there would be 4 terminals if it is a switched maintained
Perm live
Switched live
Neutral
Earth
The fitting will go on/off ok as before with the existing switch
1 or 2 way switching wont make no distance it will still work as you desire

You can get some maintained fittings though that have only 3 terminals
Perm live
Neutral
Earth
These would stay lit 24hour and no facility to switch them
 
Do you want/need/have to have an emergency light?

Not sure how doors are relevant?

Leasehold? Freehold? Legal concerns over what you may do/who may do it?
 
Do you want/need/have to have an emergency light?
Not sure how doors are relevant?
I only said that the door is at the ground floor level to show that it is an inside staircase.
We do not have to have an emergency light, I do have to reposition the existing light as we want an inner door fitted to stop draughts. I thought that it would be a safe idea to have an emergency light on the stairs so that in the event of a power failure of any sort we can still safely use the stairs, possibly to go down to the consumer unit which is at ground level. I thought a neat maintained emergency light on the ceiling would give all the light we need.
 