I needed to remove all of the radiators in my house to paint them - I also changed the copper tank. When I put back the radiators - I noticed that the rads are hot downstairs, but cold up.

I have blead for ages - no luck - I only get water out - no air. I also noticed that the tank in the attic is hot - is this normal.

Any suggestions - thanks

Robert
 
Sponsored Links
Try closing downstairs rads and see if upstairs heats. If that doesn't work then also close all but one upstairs rads. If that one heats open others one at a time. You may have airlock somewhere so you will need to keep bleeding rads if air lock moves.

Hot water in Feed & expansion tank is due to "pumping over". It may be related to rad problem. It is a common problem in sludged systems which needs fixed. See many threads on this.
 
Thanks for the reply.

I have tried turning off all radiators except one - no joy.

I am sure there is no sludge in the system - because when the radiators were removed, I ran water through them - to clean them out. I got some black water - no sludge.

Any other suggestions??

Robert
 
Sponsored Links
I eventually found that there was a gate value in the system that had broken and couldn't be opened - I replaced it with a 310 [don't really need a gate valve] - everything works.

Thanks for the suggestions.