Worcester 24CDi - 3.5 bar pressure when not in use....?

Joined
9 Oct 2006
Messages
26
Reaction score
0
Location
Hampshire
Country
United Kingdom
Hi,

My mums boiler is a worcester 24CDi and for some reason when not in use the pressure goes up to 3.5 Bar. When in use it usually drops or sometimes the pressure just drops off over night or over a few hours.

At the weekend I tested it. When not in use it started at 1 bar. I turned on a hot tap and the central heating. The pressure got up to about 1.5 bar in 20 mins or so which seemed pretty normal to me so I switched the central heating off and the hot water. A few hours after I had left mum was back on the phone saying the boiler was at 3.5 bar again.

I have checked the water inlet valve which seemed ok as it can only let water in the system when the small white T clamp is in place, which isnt at the moment, and it does let water through when opened and stops when shut off.

Seems a bit odd to me, can anyone help? She has had several people attempt to fix it with no luck so far.

Thanks

Ben
 
Sponsored Links
For some reason the plate heat exchanger on your model is prone to leaking from the mains water to the system water.

Its a bit of a palava to change.

Tony
 
Thanks.

So is it a case of just change the seals/o-rings or a new heat exchanger? I think a plumber did 'fix' the leak before but obviously not good enough.

Thanks for your help

Ben
 
The seals could always leak and may have been bodged without replacing them by your "plumber". Those would normally leak to the outside rather than cross linking the water and heating.

All those I have encountered have been caused by internal leaks inside the plate HE itself.

Tony
 
Sponsored Links
As I recall there is a fiddly series of little plastic bits in front which comprise the filling loop which have to be carefully removed in sequence.

Of course "one of the simplest" may be comparitive with that dreadful Worcester with the diverter across the back which is a real pig to change.

Tony
 
Agile said:
As I recall there is a fiddly series of little plastic bits in front which comprise the filling loop which have to be carefully removed in sequence.
No; it's the other way around - you have to remove the heat exchanger to replace the charging link. :rolleyes:
 