I have an electro magnetic door lock, it is rated 24 volts 3 watts, can anyone advise of a suitable transformer to run this from?

Thanks
 
Sponsored Links
coopersim said:
I have an electro magnetic door lock, it is rated 24 volts 3 watts, can anyone advise of a suitable transformer to run this from?

Thanks


First two questions ?

Is it an AC ( alternating current ) or DC ( direct current ) lock ?

Is it energised to lock ( fails to open on power failure ) or energised to release ( cannot be opened remotely during a power failure )
 
RS Components Stock No 310 2014 or 541 7560

Battery backed 24 volt 24 volt 1 amp ( more than you need but means the unit is not stressed and expansion is possible )

Other sources are available but for speed and convenience RS is worth the extra cost.
 
Sponsored Links
Thanks for the info - however I'm not bothered about the battery backup element - just a cheapy transformer !! I'll have a look on RS Spares though, thanks again.
 
coopersim said:
Thanks for the info - however I'm not bothered about the battery backup element - just a cheapy transformer !! I'll have a look on RS Spares though, thanks again.

It is NOT a transformer you need. You need a power supply with transformer and rectifier and smoothing capacitor. Without the capacitor the lock may buzz as the rectifier will be giving raw DC ( on-off 100 times a second ).
 
Dont they sell proper power kits for these locks? All the mag locks i've seen have a white box on the wall above the door, with power healthy, battery healthy lights.

The box contains all the electronics for the system, and releases the door on closing an external contact (push to release switch or numeric keypad)
 
coopersim said:
what about this one - 418-2443
or this one - 347-7144 ??


My only concern with switch mode power supplies is there is more to go wrong in them. And they can be a source of interference to nearby electronic equipment. Sometimes they have to have a minimum load and removing all load can cause them to lock up. The data for these two does not mention a minimum load requirement

Sometimes the back EMF from a switched inductive load will trigger the over voltage protection. You will need a back EMF diode across the coil and maybe some additional suppression in the form of a capacitor on the output of the power module
 
This isn't as simple as I first thought! I'm prepared to spend about £30, what would you suggest in this instance? It is only for domestic installation, but there is sensitive electronic equipment in the area where it will be installed - namely a wireless ADSL router and a wireless alarm system
 
coopersim said:
This isn't as simple as I first thought! I'm prepared to spend about £30, what would you suggest in this instance? It is only for domestic installation, but there is sensitive electronic equipment in the area where it will be installed - namely a wireless ADSL router and a wireless alarm system

Nothing is as simple as it looks. As Crafty mentioned the makers of the lock may have something in their range.

I will have a think and get back tomorrow.
 
I agree! However, there is no make on the lock, it is a simple lock that I bought from a local electronics shop with no box, the chap I spoke to suggested a 'laptop style' transformer, but I really want something that I know will be adequate.

Any ideas would really help.
 
any chance of a pic?

or more info?

is it really a mag lock?

does it have2 parts or one?

does it look like

images


or

images
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top