Distibution board

This topic originated from the How to page called Installing a electrical mounting box
Click here to return to the page called Installing a electrical mounting box.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
Oscar_Whild

from United Kingdom

Joined: 25 Nov 2004
Posts: 84
Location: United Kingdom

PostPosted: Thu Nov 25, 2004 7:52 pm Reply with quote

I am trying to fit a 10.5Kw shower. My current board is old and I can't get new MCB for it. I have just bought a new Crabtree 5 + 5 split load which I want to set up as follows:
Incoming 100A (unprotected) with cooker (32A), Heater (16A), Lighting (6A), Lighting (6A) = 60A.
63A RCCB (protected) with Shower (50A), Sockets (32A), Sockets (32A), Pond (16A) = 130A.
I am worried that the rating of the MCBs is greater than the main switches. Can anyone tell me if this is OK ?

Thanks,
Oscar.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
ZenStalinist

from United Kingdom

Joined: 08 Apr 2004
Posts: 386
Location: United Kingdom

PostPosted: Thu Nov 25, 2004 7:58 pm Reply with quote

Yes, It should be okay. But you say incoming is unprotected? You mean just the switch is unprotected? I mean, you have a service fuse rated at 100A in the meter cabinet right?
Back to top
 Alert Moderators
Oscar_Whild

from United Kingdom

Joined: 25 Nov 2004
Posts: 84
Location: United Kingdom

PostPosted: Thu Nov 25, 2004 8:13 pm Reply with quote

Thanks for the quick response. The electricity board wires come from the metre into the main incoming device on the Crabtree (100A). As a split board the first 5 MCB are not covered by the RCCB only the last 5 are.

It would be a great help to me if you could briefly, and simply icon_smile.gif explain why it doesn't matter about the apparently quite large difference between the MCB total (60A + 130A = 190A total) and the ratings of the Incoming device (100A) and the RCCB (63A) = 163A.

Thanks.
Back to top
 Alert Moderators
ZenStalinist

from United Kingdom

Joined: 08 Apr 2004
Posts: 386
Location: United Kingdom

PostPosted: Thu Nov 25, 2004 8:22 pm Reply with quote

Well, you see, not all of the circuits are going to be in use at once. And since the incomer must be protected by a service fuse of the same value, we allow for some diversity, based upon this assumption. It's perfectly safe, in fact most houses have three socket circuits or so, and many only have a 60A supply. For example, in the kitchen, one could have the washing machine, the tumble drier and the dishwasher going, if one only had up to the service fuse amount for the protective devices to add up to, one would most likely only have one circuit, and therefore if someone were doing a spot of vacuuming, or plugged in an electric heater elsewhere, you'd overload it. Now if we have more circuits, rated at 30A, this problem is far less likely to occur, yet it is very unlikely that one would draw the maximum amount of power, since it is highly unlikely for there to be that much power in use at once. That's basically one of the reasons, sometimes you more power in some places, and are usually less likely to need the power in others. I probably did a lousy job of explaining that, but I hope I more or less made at least part of the reason clear. Also, that way we can have smaller supplies, since 190A would be a heck of a capacity to install, if we did things this way we'd end up with pylons and huge wires all over.

It might be a good idea to upgrade your RCD, given that your shower is 50A.
Back to top
 Alert Moderators
Oscar_Whild

from United Kingdom

Joined: 25 Nov 2004
Posts: 84
Location: United Kingdom

PostPosted: Thu Nov 25, 2004 8:56 pm Reply with quote

Thanks very much for that, I had hoped as much. I don't like the last line about the RCD though. This bloody shower is rapidly becoming the "job from hell"!!
Back to top
 Alert Moderators
andy

from United Kingdom

Joined: 14 Sep 2004
Posts: 3971
Location: United Kingdom
Thanked: 2 times

PostPosted: Thu Nov 25, 2004 9:18 pm Reply with quote

it should be higher because the shower is 50A, giving you 13A spare. say someone then starts the hoovering. gettin close to the limit. the TV computer is also on. even closer. then someone decides to have a cup of tea..
Back to top
 Alert Moderators
Oscar_Whild

from United Kingdom

Joined: 25 Nov 2004
Posts: 84
Location: United Kingdom

PostPosted: Thu Nov 25, 2004 9:39 pm Reply with quote

Do you think that the best way forward would be to take the 50A MCB (shower) from the non RCCB side of the box and use a separate stand alone RCD solely for the shower then ?
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 8443
Location: United Kingdom
Thanked: 199 times

PostPosted: Thu Nov 25, 2004 9:47 pm Reply with quote

yes

i would have suggested a rcbo but a 2 module would be a bit big in your CU and all the crabtree 1 modules ones are type C (which you really don't want on a 50A cuircuit domestically)
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 46280
Location: London,
United Kingdom
Thanked: 1666 times

PostPosted: Fri Nov 26, 2004 12:48 am Reply with quote

Oscar_Whild wrote:
Thanks very much for that, I had hoped as much. I don't like the last line about the RCD though. This b****y shower is rapidly becoming the "job from hell"!!

Then perhaps you shouldn't have gone out and bought a CU without knowing what you were doing.

If you'd bothered to find out some more, you might not have bought something unsuitable.

What are you replacing? And do you have a TN-S or TN-C-S supply, or is it TT?

What size cable are you using for the shower circuit?
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 46280
Location: London,
United Kingdom
Thanked: 1666 times

PostPosted: Fri Nov 26, 2004 12:54 am Reply with quote

Oscar_Whild wrote:
Do you think that the best way forward would be to take the 50A MCB (shower) from the non RCCB side of the box and use a separate stand alone RCD solely for the shower then ?

Dear God.

You haven't even, or have only just, installed a brand new CU, and already you're having to bodge a solution to a problem caused by bad design and product selection.

Bite the bullet - swap the 63A RCD for an 80A and/or buy a bigger board.
Back to top
 Alert Moderators
Oscar_Whild

from United Kingdom

Joined: 25 Nov 2004
Posts: 84
Location: United Kingdom

PostPosted: Fri Nov 26, 2004 7:17 am Reply with quote

Er, yes I have !! Bought but not yet fitted. I had no idea that this was going to be such a difficult job. On reflection I would not have started this one !
I am getting a 80A rcd for it today and will fit that before swapping the boards.
Cable size is 10mm and runs direct from the new shower to the CU. As to the type of supply, I have had a good read at some of the posts in other topics and will have to take a look at that and get back to you.
The intention is to swap the boards one for one.
Back to top
 Alert Moderators
Oscar_Whild

from United Kingdom

Joined: 25 Nov 2004
Posts: 84
Location: United Kingdom

PostPosted: Fri Nov 26, 2004 8:44 am Reply with quote

The supply is either TN-C-S or TN-S. I can't see which without taking stuff out.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Tripping Circuit Board (constant) 11 320 Sat Oct 30, 2010 1:36 pm
Split Board General Question 14 741 Wed Jun 02, 2010 11:21 am
RCD Board 13 1340 Sat Dec 04, 2010 8:47 am
Temporary electric supply to new fuse board 5 340 Tue Dec 07, 2010 7:31 pm
CHANGING A DOMESTIC FUSE BOARD 65 4100 Sat Jan 08, 2011 7:37 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.