DIYnot
Local | Network
   DIYnot > Forums
Local | Network
Consumer Unit Positioning
Goto page 1, 2  Next
Author Message
ryanj
from United Kingdom
PostPosted: Tue Jun 01, 2004 6:10 pm Reply with quote
During my rewire, I plan to move my consumer unit to a new position. Currently, it is in a room with a concrete floor, I propose to move it to allow me to get cables into the crawlspace easier.
My supply is an overhead TT supply. Would it be acceptable to simply run 25mm sqr metre tails from the metre in the old position to the new consumer unit, or would I have to contact the power company to move the metre beside the consumer unit?
Also, is it fine to have earth rods driven from the crawlspace, rather than have them taken outside? And must I use a "whole-house" RCD, if I can get the earth fault loop impedance low enough?
And, is it acceptable to use a flush consumer unit in domestic situations, as it'd help keep everything neat?
And, is it acceptable to run cables in the crawl space without clipping them to the joists, or running them through the joists?
Finally, where the cables leave the consumer unit, do the cable grouping de-rating factors take effect for 1-2metres down the wall?
Back to top
 Alert Moderators
plugwash
from United Kingdom
Thanked: 251 times
PostPosted: Tue Jun 01, 2004 6:49 pm Reply with quote
you aren't meant to run tails more than 3m without having your own isolation and protection
the main rcd for a TT must be in a plastic enclosure
you could use a plastic 4 module enclosure with the 100ma type S rcd and a 100A mcb (http://www.tlc-direct.co.uk/Products/CMDK401.html)
then run from that to a normal split load CU preferablly using 25mm swa
Back to top
 Alert Moderators
securespark
from United Kingdom
Thanked: 466 times
PostPosted: Tue Jun 01, 2004 9:05 pm Reply with quote
2m for Norweb.
Back to top
 Alert Moderators
ryanj
from United Kingdom
PostPosted: Wed Jun 02, 2004 7:51 pm Reply with quote
Back to top
 Alert Moderators
il78
from United Kingdom
Thanked: 1 time
PostPosted: Wed Jun 02, 2004 10:28 pm Reply with quote
Go for what plug suggested, creating a distribution circuit, have the position where you want then.....
Back to top
 Alert Moderators
ryanj
from United Kingdom
PostPosted: Thu Jun 03, 2004 9:01 pm Reply with quote
Thanks! Got that problem sorted out.
Any advice on the others?
Back to top
 Alert Moderators
il78
from United Kingdom
Thanked: 1 time
PostPosted: Thu Jun 03, 2004 10:16 pm Reply with quote
You can have the rod in the crawl space as long as its <100Ohms. (Make a label stating the location)
Not to sure what you mean about the RCD, but a TT system requires that the installation is protected by an RCD usually 100mA although a 30mA is required for supplementary protection.
Cant see a problem with using a flush mount DB
Clip the cables in the crawl space
Grouping factors for that amount of lenght shouldn't be a problem.
Back to top
 Alert Moderators
ryanj
from United Kingdom
PostPosted: Thu Jun 03, 2004 10:41 pm Reply with quote
Are you sure the whole installation must be protected?
The only thing I can find in the regulations states that all socket outlets on a TT system must be RCD protected. Nothing else.
Quote:
471-08-06 - Where the measure is used in an installation forming part of a TT system, every socket-outlet circuit shall be protected by a residual current device and shall comply with Regulation 413-02-16
Back to top
 Alert Moderators
plugwash
from United Kingdom
Thanked: 251 times
PostPosted: Thu Jun 03, 2004 10:55 pm Reply with quote
yes but you will never meet disconnect times otherwise
the impedcence of the earth limits the current flow down it to a value insufficint to trip a fuse or mcb
that is why you need the main rcd
Back to top
 Alert Moderators
ryanj
from United Kingdom
PostPosted: Tue Jun 08, 2004 9:42 pm Reply with quote
But, if i could reach required disconnection times, would I need to use a main RCD?
Also, could I run meter tails instead of using SWA?
Back to top
 Alert Moderators
plugwash
from United Kingdom
Thanked: 251 times
PostPosted: Tue Jun 08, 2004 10:19 pm Reply with quote
tails would probablly be ok but they should be protected from damage
a worst case allowed TT is 200 ohms this will allow just over an amp to flow in the case of a short to earth (obviosuly until this fault is disconncted your entire earth system will be live so it should happen asap)
so either a rcd is essential OR it would have to be a bloody good TT (like big mats burried below the water table)
with a ROD you will not manage it
Back to top
 Alert Moderators
ban-all-sheds
from United Kingdom
Thanked: 1951 times
PostPosted: Wed Jun 09, 2004 3:07 pm Reply with quote
Particularly with a rod in a dry location - ryanj, what do you mean by the term "crawlspace"?
Back to top
 Alert Moderators
ryanj
from United Kingdom
PostPosted: Wed Jun 09, 2004 9:35 pm Reply with quote
Crawlspace - Small area under the floorboards of the ground floor.
Back to top
 Alert Moderators
plugwash
from United Kingdom
Thanked: 251 times
PostPosted: Wed Jun 09, 2004 9:38 pm Reply with quote
it would be an insanely stupid place to put a rod
to get a usable earth the rod needs to be at least partially in wet soil
Back to top
 Alert Moderators
ryanj
from United Kingdom
PostPosted: Wed Jun 09, 2004 10:57 pm Reply with quote
Fine, I'll use multiple earth rods in the back garden to try and keep the resistance low.
Back to top
 Alert Moderators
Goto page 1, 2  Next
Page 1 of 2
Jump to:
consumer unit positioning 5 740 Fri Oct 17, 2003 10:11 pm
New Cooker Circuit Install - Positioning of controls 2 5720 Fri Aug 17, 2007 10:44 am
Positioning of lights 2 300 Thu Oct 04, 2007 11:33 am
Positioning of bathroom underfloor heating controls 2 1460 Tue Nov 14, 2006 9:13 pm
cooker hood isolation switch positioning 2 1080 Tue Jun 28, 2005 9:46 am
DIYnot
Please read our Privacy Policy. Copyright © 2000-2015 DIYnot Limited.