Electric shower switch
I\\\'ve got a Mira shower. The 6kV electric switch seems as though it\\\'s quite difficult to switch on and off, so I think it needs changing. The instructions manual says to use a 40 amp switch but I can only find 35amp at the shops? Can I use this or does anbody know where I can get one? TA.
Joined: 10 Apr 2004 Posts: 1764 Location: Sussex, United Kingdom
Posted: Wed Jun 02, 2004 11:44 pm Post Subject:
Looks like we're talking about a pull-cord or outside-bathroom switch. 45A shouldn't be too hard to find, but Ban, did you really just recommend screwfix???
Joined: 10 Apr 2004 Posts: 1764 Location: Sussex, United Kingdom
Posted: Thu Jun 03, 2004 12:22 am Post Subject:
To clarify....
DI-
Look at the shower, or at it's instruction book. Somewhere you will see it's rating, which will either be stated in watts (anywhere between 5000 watts and 11500 watts) or otherwise termed as kilowatts, therefore anywhere between 5kw and 11.5 kilowatts. Divide the wattage by 230. The figure you come out with is the minimum (in amps) that you can use for a switch or circuit breaker.
Example: my shower here is 8.5kw (8500 watts) - divided by 230 gives me 36.95 amps. So my 40A switch and 40A breaker are fine.