Replacing an upstairs ceiling light

This topic originated from the How to page called Replacing a one way light switch with a two way light switch
Click here to return to the page called Replacing a one way light switch with a two way light switch.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
StuartB

from United Kingdom

Joined: 08 Sep 2007
Posts: 5
Location: Manchester,
United Kingdom
Thanked: 0 times

PostPosted: Sat Sep 08, 2007 4:56 pm    Post Subject:
Replacing an upstairs ceiling light
Reply with quote Thanks

There are only 2 wires coming through the ceiling from the loft, one red and one black.
A mains tester screwdriver touching the red wire lit up when the light switch was on, as you would expect.
However when the switch was off, the tester light still glowed but not as bright.
Does this mean that the red wire is live all the time? Why would it be?
For now I have abandoned the job.
Any advice?
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
breezer

from United Kingdom

Joined: 03 Jan 2003
Posts: 23346
Location: Sussex,
United Kingdom
Thanked: 5 times

PostPosted: Sat Sep 08, 2007 4:59 pm    Post Subject:
Reply with quote Thanks

becsue tester screwdrivers are rubbish thats why

__________________
Do you like music Mr Finch?
Forum = Opinions
Back to top
 Alert Moderators
davy_owen_88

from United Kingdom

Joined: 17 Nov 2006
Posts: 1680
Location: West Glamorgan,
United Kingdom
Thanked: 0 times

PostPosted: Sat Sep 08, 2007 5:01 pm    Post Subject:
Re: Replacing an upstairs ceiling light
Reply with quote Thanks

StuartB wrote:
A mains tester screwdriver touching the red wire lit up when the light switch was on, as you would expect.
However when the switch was off, the tester light still glowed but not as bright.
Does this mean that the red wire is live all the time?


No, it just means that neon screwdrivers are crap!

StuartB wrote:
Any advice?


Throw the neon screwdriver in the bin and buy a multimeter.



Anyway, I don't know why you abandoned the job. Just isolate the supply at the consumer unit and change the fitting.

EDIT: Bah! Too slow.


Last edited by davy_owen_88 on Sat Sep 08, 2007 5:08 pm, edited 1 time in total
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12857
Location: Yorkshire,
United Kingdom
Thanked: 22 times

PostPosted: Sat Sep 08, 2007 5:07 pm    Post Subject:
Reply with quote Thanks

Stuart, the red wire that made the neon go dimmer when the switch was turn off - this is (probably) your switch return, it is (probably) a switched live.

By the way, if you're connecting a compact fluorescent light to this wire, expect it to flicker every now and then when switched off. Due to the neon glowing, there is a charge building up on the wire and this will disipate itself across the lamp. Nothing harmful! And its only a very faint flicker.
Back to top
 Alert Moderators
Space cat

from United Kingdom

Joined: 09 Sep 2007
Posts: 1323
Location: Newcastle upon Tyne,
United Kingdom
Thanked: 3 times

PostPosted: Mon Sep 10, 2007 10:04 am    Post Subject:
Reply with quote Thanks

Your neon driver lit up with the switch off because of something in the circuit that's not on your mental diagram, namely capacitive coupling between the cores of the cable going to the switch. A ball park figure for this capacitance is around 100pF per meter so a 10m length is 1nF. That will pass enough current to make a neon glow dimly. If it's big enough it can even make low energy lamps flicker.

But this raises another question; is that light on two way switches? The reason I ask is because a single switch would typically be wired with twin and earth. In this case the earth wire acts as a screen which intercepts the current - unless it's not connected to earth! If you do have two way switches you can get capacitive coupling even with all earths intact.

__________________
Their base is so secret, even the space cats don't know where they are.
Back to top
The following user says thank you to Space cat for this useful post:
Billibuoy (12 Oct)
 Alert Moderators
StuartB

from United Kingdom

Joined: 08 Sep 2007
Posts: 5
Location: Manchester,
United Kingdom
Thanked: 0 times

PostPosted: Mon Sep 10, 2007 11:19 am    Post Subject:
Reply with quote Thanks

Space cat

Thanks for the technical info. - I think I understand the gist.

I'm doing this job for my brother; his house is probably late 60s - the lighting circuit is not earthed! Is this VERY bad?? Should I advise him to have it rewired?

I think the light is part of a 2-way setup - there is a redundant pull-cord
lazy switch. Unfortunately access to the wiring in the loft is very difficult.

Incidentally the reason for the new light fitting is that the previous one failed (it was a low-voltage one but only about one year old); would the constant low current have damaged the transformer?

StuartB
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12857
Location: Yorkshire,
United Kingdom
Thanked: 22 times

PostPosted: Mon Sep 10, 2007 11:22 am    Post Subject:
Reply with quote Thanks

No, the transformer would have dissipated the charge across its windings. Transformers can fail as often as a lightbulb. icon_sad.gif

Not having an earth is not immediately dangerous, however you must NEVER fit metal switches or light fittings to the circuit.
Back to top
 Alert Moderators
StuartB

from United Kingdom

Joined: 08 Sep 2007
Posts: 5
Location: Manchester,
United Kingdom
Thanked: 0 times

PostPosted: Tue Sep 11, 2007 10:23 am    Post Subject:
Reply with quote Thanks

Thanks to everyone who replied.
I now know what to do and have also acquired a multimeter.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Replacing/rewiring upstairs lighting circuit 3 360 Tue May 13, 2008 3:05 pm
upstairs ceiling light 6 200 Fri Mar 13, 2009 6:44 pm
Living Room/Upstairs Landing Light Switch Nightmare 3 280 Wed Mar 05, 2008 11:23 am
Upstairs/Downstairs Light Circuits 4 240 Sun Jul 20, 2008 9:39 pm
light upstairs dimmer switch down stairs 8 480 Sun Jan 07, 2007 8:28 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.