PostPosted: Tue Oct 02, 2007 5:09 pm Reply with quote
This is the first time I've done a test on a TT system and I'm a bit stuck on the readings I am getting for loop impedence.
My Ze reading is 9.7 ohms which I think is ok(pretty sure I'm reading regs ok saying 21 ohms max)
The only thing is every reading I am getting from every circuit be it the end of the line or not is 2000 ohms.Its like it reads it and it just keeps giving me that.I am testing with a Fluke tester and there is no way to change the loop setting.
Now do I need to get another loop impedence tester with a setting selector or as I'm reading the regs---having a 100ma RCD protecting every circuit(as impedence reading is so high)is ok and I can just leave the readings I'm getting and write those down(this is a periodic inspection and report)
Any help would be great as NICEIC help line not much assistance thanks!
Back to top
 Alert Moderators
GaryMo
from United Kingdom
Thanked: 165 times
PostPosted: Tue Oct 02, 2007 5:15 pm Reply with quote
If you have a Ze reading of 9.7ohms then why aren't you getting an earth fault loop impedance reading?
What are your R1+R2 readings?
If your R1+R2 readings and Ze test out OK then I would look at borrowing another meter.
Back to top
 Alert Moderators
Albert
from United Kingdom
Thanked: 1 time
PostPosted: Tue Oct 02, 2007 5:21 pm Reply with quote
sorry I do not have much experience testing TT but have with the Fluke, when toy read in continuity 2000 ohm means no continuity. Normally Zs is a live test so the meter will buzzz if ther is no power. As mentioned above I would check again continuity.[/code]
Back to top
 Alert Moderators
unclebubble
from United Kingdom
PostPosted: Tue Oct 02, 2007 5:30 pm Reply with quote
Yeah the installation is energised and working.I haven't done R1+R2 yet it would be a be unreal that every circuit had bad continuity(I know its poss!)
There are 15 circuits on this board so the house is large!One circuit I have just put in is a shower and it is still reading 200 ohms(I have done R1+R2 on this circuit its fine)The tester is telling me I have L N E and it beeps like it normally does when I do a test!I know TT systems are quite rare so I'm well confused perhaps I should just get another meter!!
Back to top
 Alert Moderators
GaryMo
from United Kingdom
Thanked: 165 times
PostPosted: Tue Oct 02, 2007 5:47 pm Reply with quote
Forget it being TT, it won't matter.
You have a Ze of 9.7ohms and an acceptable R1+R2 reading on your shower circuit (out of interest, what was the reading?) so you should see a healthy Zs reading. If not then it's the meter at fault.
Back to top
 Alert Moderators
plugwash
from United Kingdom
Thanked: 257 times
PostPosted: Tue Oct 02, 2007 6:02 pm Reply with quote
where exactly are you taking your Ze reading from?
It sounds to me like there is a fault between where you are taking your Ze reading from and the earth bar of the CU.
Back to top
 Alert Moderators
fireman22
from United Kingdom
Thanked: 10 times
PostPosted: Tue Oct 02, 2007 11:09 pm Reply with quote
what model fluke is it???
Back to top
 Alert Moderators
securespark
from United Kingdom
Thanked: 471 times
PostPosted: Wed Oct 03, 2007 4:14 am Reply with quote
Are you SURE that Ze reading is taken correctly?
Switch the CU isolator off.
Disconnect the main earthing conductor from its terminal.
In effect, you should now have a live, neutral and earth that are not connected to anything.
Now test your Ze from these.
What is the reading now?
Back to top
 Alert Moderators
unclebubble
from United Kingdom
PostPosted: Wed Oct 03, 2007 6:04 pm Reply with quote
Yep I've done everything that everyone suggested the first time around.I am doind the Ze at source(consumer unit)connected and un connected my earth stake is fine I'm getting 63 ohms.
I'm going back tomorrow to try and see if I can solve this prob I'll keep you all posted!
Back to top
 Alert Moderators
fireman22
from United Kingdom
Thanked: 10 times
PostPosted: Wed Oct 03, 2007 10:59 pm Reply with quote
Back to top
 Alert Moderators
Paul Barker
from United Kingdom
Thanked: 853 times
PostPosted: Thu Oct 04, 2007 6:14 am Reply with quote
Then ze is 63 ohms plus you might have a good meter and a bad main earth conductor.
Back to top
 Alert Moderators
Page 1 of 1
Jump to:
very high earth loop impedence zs 28 1320 Mon Mar 23, 2009 8:53 pm
Earth loop impedence 13 920 Fri May 22, 2009 4:22 pm
Earth FAult Loop Impedence 3 600 Sat Oct 13, 2007 1:48 pm
earth loop impedence values 52 2920 Thu Jul 15, 2010 7:43 am
Cooker and high earth loop impedence test 6 1580 Sun Aug 05, 2007 7:43 am
DIYnot
Please read our Privacy Policy. Copyright © 2000-2015 DIYnot Limited.