Customer has the above oil fired boiler which was locking out.
Turned out to be the motor found replacement and fitted. Started boiler, fan run, ignition no main burner, then to lock out.
Reset a couple of times still no main burner and fan would not start icon_eek.gif

Stripped off pump tried reset and fan starts every time, so stripped pump down, was clean didnt look worn so replaced on motor, then tried fan and would not kick in, pump seems to be stopping it, now believe this is what took out original motor.

Cured this by nipping plate on rather than tightening down, several resets later buner still not firing icon_confused.gif icon_confused.gif

Removed injector feed pipe from pump run it and no fuel coming, then tried solenoid found this to be getting power though appears not to be working. With solenoid still off gave fan a quick run and fuel came into the chamber icon_razz.gif


So oil chaps and fonts of knowledge does anyone know the part number, I assume, as I dont know, the pump and solenoid come as one part.

Its a Riello G7Q burner made for Boulter.

Or has anyone got a manual for a Boulter Camray Quartet icon_wink.gif
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
oilman

from United Kingdom

Joined: 16 Sep 2003
Posts: 7965
Location: United Kingdom
Thanked: 26 times

PostPosted: Wed Oct 24, 2007 6:34 pm Reply with quote

There are two commpn pumps, one for the RDB burners and one for the G series the one you need is the 3007811. If you ring Riello you can get a CD full of burner information, otherwise Worcester might supply a Quartet manual.
Back to top
 Alert Moderators
clf-gas

from United Kingdom

Joined: 02 Mar 2007
Posts: 3453
Location: Lancashire,
United Kingdom
Thanked: 63 times

PostPosted: Wed Oct 24, 2007 6:44 pm Reply with quote

oilman wrote:
There are two commpn pumps, one for the RDB burners and one for the G series the one you need is the 3007811. If you ring Riello you can get a CD full of burner information, otherwise Worcester might supply a Quartet manual.


Thanks oilman, will give Burty a try and will Speak to Mike at Riello tomorrow. icon_wink.gif

Does the pump and solenoid come as one or is there a part number for solenoid.

Thanks for info icon_wink.gif
Back to top
 Alert Moderators
Terrywookfit

from Antarctica

Joined: 19 Jul 2007
Posts: 2327
Location: Antarctica
Thanked: 270 times

PostPosted: Wed Oct 24, 2007 6:49 pm Reply with quote

Coil is not supplied with pump !!
Very reliable though! I dont normally change with pump!!
Coil is two stage ! Lifting coil and holding coil !!
Back to top
 Alert Moderators
clf-gas

from United Kingdom

Joined: 02 Mar 2007
Posts: 3453
Location: Lancashire,
United Kingdom
Thanked: 63 times

PostPosted: Wed Oct 24, 2007 6:53 pm Reply with quote

Terrywookfit wrote:
Coil is not supplied with pump !!
Very reliable though! I dont normally change with pump!!


Thats whats confusing me Terry icon_confused.gif Have you ever had that though, Pump taking out the motor icon_question.gif
Back to top
 Alert Moderators
oilman

from United Kingdom

Joined: 16 Sep 2003
Posts: 7965
Location: United Kingdom
Thanked: 26 times

PostPosted: Wed Oct 24, 2007 6:58 pm Reply with quote

No, cos when the pump jams the motor, it locks out in the end
Back to top
 Alert Moderators
Terrywookfit

from Antarctica

Joined: 19 Jul 2007
Posts: 2327
Location: Antarctica
Thanked: 270 times

PostPosted: Wed Oct 24, 2007 7:02 pm Reply with quote

Only when the shaft seal leaks and knackers the bearing!!

Had a few on RDB burners that chew up drive dog though !!

Dog turns on pump shaft and jams motor!!

I always replace dog with pump !!
Back to top
 Alert Moderators
clf-gas

from United Kingdom

Joined: 02 Mar 2007
Posts: 3453
Location: Lancashire,
United Kingdom
Thanked: 63 times

PostPosted: Wed Oct 24, 2007 7:04 pm Reply with quote

oilman wrote:
No, cos when the pump jams the motor, it locks out in the end


Umh! Motor was definately Knackered, pump definately jarring new motor and solenoid appears to be stopping fuel to injector.

Will source new pump and sol tomorrow..
Back to top
 Alert Moderators
Terrywookfit

from Antarctica

Joined: 19 Jul 2007
Posts: 2327
Location: Antarctica
Thanked: 270 times

PostPosted: Wed Oct 24, 2007 7:07 pm Reply with quote

What was oil pressure before and after coil operated ??
Back to top
 Alert Moderators
clf-gas

from United Kingdom

Joined: 02 Mar 2007
Posts: 3453
Location: Lancashire,
United Kingdom
Thanked: 63 times

PostPosted: Wed Oct 24, 2007 7:13 pm Reply with quote

Terrywookfit wrote:
What was oil pressure before and after coil operated ??


Dont know Terry never checked to be honest icon_redface.gif

I am convinced that the pump is now working as when removed sol/valve and ran motor oil came through.

So think solenoid is not lifting valve from seating to allow oil to injector.

This is a very small movement aint it.
Back to top
 Alert Moderators
oilman

from United Kingdom

Joined: 16 Sep 2003
Posts: 7965
Location: United Kingdom
Thanked: 26 times

PostPosted: Wed Oct 24, 2007 7:14 pm Reply with quote

If the motor ran without the pump, how did you diagnose the motor was faulty? Did you measure the motor capacitor?

Solenoid works the other way round it closes to send full pressure to the nozzle
Back to top
 Alert Moderators
clf-gas

from United Kingdom

Joined: 02 Mar 2007
Posts: 3453
Location: Lancashire,
United Kingdom
Thanked: 63 times

PostPosted: Wed Oct 24, 2007 7:35 pm Reply with quote

oilman wrote:
If the motor ran without the pump, how did you diagnose the motor was faulty?


Could hear on resetting that the fan was jamming, stripped off fan cover and tried to turn by hand, no joy, pressed reset and tried kick starting fan would not run, removed pump still no joy

Replaced fan motor and fan started on first two attempts, then would only run if I kick started it, took off pump and fan started every time un-aided.

So dodgy pump took out first motor icon_question.gif

Stripped pump, seemed fine seemed to pump when on motor without solenoid valve attached.

Quote:
Solenoid works the other way round it closes to send full pressure to the nozzle




Im used to a gas one opening icon_redface.gif


Will replace pump and valve as this is one of my good customers who will not mind the part throughing as long as his diners are warm.
Back to top
 Alert Moderators
oilman

from United Kingdom

Joined: 16 Sep 2003
Posts: 7965
Location: United Kingdom
Thanked: 26 times

PostPosted: Wed Oct 24, 2007 8:12 pm Reply with quote

Sounds as if the capacitor has dropped in value. I measure these every couple of years as it saves unnecessary callouts.
Back to top
 Alert Moderators
clf-gas

from United Kingdom

Joined: 02 Mar 2007
Posts: 3453
Location: Lancashire,
United Kingdom
Thanked: 63 times

PostPosted: Wed Oct 24, 2007 8:55 pm Reply with quote

I`ll measure that when im there though dont think its that.

Convinced the pump was at fault in first and second instance, and first motor definately goosed, just had it in my workshop.

Will update post when have it working tomorrow, (he types wishfully)
Needs to be working before I jet off to Canada for Halloween.

Cheers oilman, icon_wink.gif

and Terry icon_wink.gif
Back to top
 Alert Moderators
clf-gas

from United Kingdom

Joined: 02 Mar 2007
Posts: 3453
Location: Lancashire,
United Kingdom
Thanked: 63 times

PostPosted: Thu Oct 25, 2007 4:59 pm Reply with quote

oilman wrote:
Sounds as if the capacitor has dropped in value. I measure these every couple of years as it saves unnecessary callouts.


Welldone oilman, Cap was down icon_wink.gif

Anyway fitted new pump (57) improvised with a cap on the van (6 uF instead of 4 uF) fan and burner starting and firing first time every time, customer happy its working.

Speaking with him today he said on witnessing the motor not running just humming, "thats how it starts all the time, it buzzes then click then I here the fan start". So I now think icon_eek.gif the cap being low would,nt kick in the motor, this in turn burnt out the motor icon_exclaim.gif

Now what took out the pump icon_question.gif

Anyway its running now, intend to fit correct cap on return from Canada.


Thanks again oilman & Terry.

PS, would you have the part number for capacitor icon_question.gif ,,,,,,,I Know Iam a cheeky sod icon_lol.gif icon_lol.gif
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Boulter Camry Quartet with Riello 40 locked out 8 200 Sat Mar 12, 2011 1:02 pm
Camray Quartet broken 22 280 Sat Feb 16, 2013 3:16 pm
Camray Quartet 9/110 6 160 Wed Dec 01, 2010 5:38 pm
Camray Quartet 3 760 Tue Jan 08, 2008 3:40 pm
Camray Quartet 90/110 Oil Bolier Lockout Problem 20 1980 Fri Oct 29, 2010 8:50 am


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.