daren j

from United Kingdom

Joined: 02 Jul 2004
Posts: 7
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Jul 02, 2004 9:21 pm    Post Subject:
consumer unit
Reply with quote Thanks

can anyone please help me , i am wanting to change my old consumer for a new one and move it at the same time but, the circuit tails i.e 2.5 and 1.5 are to short thease will end up in a cavity wall and be plasterd over after joining wot is the correct method to extened thease please, i have the main power before the consumer turned of. i would be very greatfull of your help icon_cry.gif
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Sat Jul 03, 2004 12:59 am    Post Subject:
Reply with quote Thanks

1) Cables should not be run in wall cavities

2) This topic has been covered several times before - do a search for terms such as extending, joining, crimping, crimp, crimps....

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
daren j

from United Kingdom

Joined: 02 Jul 2004
Posts: 7
Location: United Kingdom
Thanked: 0 times

PostPosted: Sat Jul 03, 2004 8:29 am    Post Subject:
Reply with quote Thanks

thanks m8 had a look allthought some contradicted others i think as it is only 1 ring main i will crimp them and put them in a plas box surface mounted for accesabilaty,thank again
Back to top
 Alert Moderators
Howarth

from United Kingdom

Joined: 05 Jan 2005
Posts: 1
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Jan 05, 2005 4:00 pm    Post Subject:
Re: consumer unit
Reply with quote Thanks

i would also like to change my old consumer unit for a new one one in one out please help thank you icon_sad.gif
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Wed Jan 05, 2005 4:07 pm    Post Subject:
Reply with quote Thanks

Do you know about the new electrical-related provisions of the Building Regulations?

What do you know/not know about what's involved in replacing a CU?

Do you have an isolation switch before the CU?

Do you have a TT supply, or TN-S/TN-C-S?

I'm not saying that you can't do this, but I do feel, given what you asked, that there is a great deal that you don't yet know, and what is worse, probably don't realise that you don't know...

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
2scoops0406

from United Kingdom

Joined: 20 Jan 2004
Posts: 4866
Location: Buckinghamshire,
United Kingdom
Thanked: 1 time

PostPosted: Wed Jan 05, 2005 5:36 pm    Post Subject:
Reply with quote Thanks

B-A-S Salvador Dali ?
Back to top
 Alert Moderators
daren j

from United Kingdom

Joined: 02 Jul 2004
Posts: 7
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Jan 05, 2005 6:49 pm    Post Subject:
Reply with quote Thanks

HI THERE HAPPY NEW YEAR TO ALL. CAN ANYONE GIVE ME ADVICE I HAVE AN exsisting CONSUMER pannel AND IT IS TT EARTH.THE MAINS INTO THE PROPERTY HAS BEEN REPLACED BEFORE I HAD MOVED IN.THERE IS A nuetral AND A PHASE.THE PHASE GOTO THE SERVICE HEAD VIA A 60AMP FUSE THE n IS GOING TO A MULTI BLOCK SEALED,I WOULD LIKE TO GO p.m.e . THE MAINS COME INTO THE HOUSE FROM THE GROUND. I WAS TOLD THAT IF IT COMES FROM ABOVE THIS COULD BE A PROB IF A TREE FOR EXAMPLE FELL ON THE NEUTRAL LINE AND CUT THROUGH THIS WOULD LEAVE NO EARTH. WOULD YOU LEAVE IT TT OR GO pme. AND SHOULD I reconect THE TT EARTH WITH THE PME ..THANKS
Back to top
 Alert Moderators
ChrisRogers

from United Kingdom

Joined: 28 Oct 2003
Posts: 171
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Jan 05, 2005 7:25 pm    Post Subject:
Reply with quote Thanks

Could you please not use capitals, it is considered shouting
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu Jan 06, 2005 12:47 am    Post Subject:
Reply with quote Thanks

Eddie M wrote:
B-A-S Salvador Dali ?

Indeed.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu Jan 06, 2005 12:51 am    Post Subject:
Reply with quote Thanks

darenj - a switch from TT to TN-C-S/PME is not something you can do. The doing of it, and the decision over whether it should be done, is the province of your DNO.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu Jan 06, 2005 12:53 am    Post Subject:
Reply with quote Thanks

ChrisRogers wrote:
Could you please not use capitals, it is considered shouting

Nice of him to highlight his spelling mistakes by using lower case, though....

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
mildmanneredjanitor

from Hong Kong

Joined: 28 Nov 2003
Posts: 1017
Location: Hong Kong
Thanked: 0 times

PostPosted: Thu Jan 06, 2005 12:59 am    Post Subject:
Reply with quote Thanks

ban-all-sheds wrote:
ChrisRogers wrote:
Could you please not use capitals, it is considered shouting

Nice of him to highlight his spelling mistakes by using lower case, though....

icon_razz.gif

__________________
Could it be Rosemary - the telephone operator?
Back to top
 Alert Moderators
ChrisRogers

from United Kingdom

Joined: 28 Oct 2003
Posts: 171
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Jan 06, 2005 11:03 am    Post Subject:
Reply with quote Thanks

ban-all-sheds wrote:
ChrisRogers wrote:
Could you please not use capitals, it is considered shouting

Nice of him to highlight his spelling mistakes by using lower case, though....


maybe he just wants to speak quietly at those points so no one can hear him make the mistake?!
Back to top
 Alert Moderators
daren j

from United Kingdom

Joined: 02 Jul 2004
Posts: 7
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Jan 07, 2005 10:06 am    Post Subject:
Reply with quote Thanks

thanks for the help i will contact them. i would just like to add that i thought you were here to help no to take the mick out of people. spelling has never been a strong point of mine but then i can imagine that you guys are the best at every thing. don't mean to sound nasty i am greatfull for your advice but i don't see the point to it. . icon_evil.gif
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Sat Jan 08, 2005 12:49 pm    Post Subject:
Reply with quote Thanks

daren j wrote:
thanks for the help i will contact them. i would just like to add that i thought you were here to help no to take the mick out of people. spelling has never been a strong point of mine but then i can imagine that you guys are the best at every thing. don't mean to sound nasty i am greatfull for your advice but i don't see the point to it. . icon_evil.gif

Sorry - I wasn't really taking the **** - not seriously, or in a nasty-meaning way, anyway. The point about you shouting was quite correctly made, and I just found it curious that the only words that you hadn't shouted were the misspelled ones.....

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Replacing CONSUMER UNIT queries 6 780 Fri Nov 02, 2007 6:47 pm
consumer unit mounting 2 640 Sat Nov 03, 2007 9:12 pm
Garage Consumer Unit Supply 3 580 Mon Nov 05, 2007 3:16 pm
consumer unit getting hot 10 420 Fri Nov 02, 2007 1:25 pm
Consumer unit fuseway / ring-main 33 1620 Fri Nov 02, 2007 12:54 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.