Downlighter wiring
Reply with quote Thanks

Hi, can anyone help me?

I'm going to install 6 downlighters in my kitchen. I plan to daisy chain them together from a 20a junction box using 1mm twin and earth lighting cable. My questions are...

1. Is the 1mm cable suitable for 6 downlights (50W bulb)

2. The fittings are double insulated and 'should not be earthed'. Should I simply snip off the earth core and leave it?

3. The actual connection box on the fitting is small and it is really difficult to connect 2 cores into each 'terminal'. So I bought some 15A connector strip blocks and planned to make the daisy connection in to one side, and take another short length of cable from the other side to the fitting. Is that a sensible/safe idea? Or should I squeeze them into the terminal as best as possible?

Many thanks for all reponses!
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 4940
Location: Oxfordshire,
United Kingdom
Thanked: 63 times

PostPosted: Sat Nov 24, 2007 7:36 pm    Post Subject:
Reply with quote Thanks

Firstly, all electrical work in a kitchen is notifiable under Building regulations Part P. Your best route would be to get a registered spark to fit and certify the work.

You could do it yourself and notify your LABC before work starts but your post does indicate that you'll never get through their inspection.

Your specific questions:
1. Is the 1mm cable suitable for 6 downlights (50W bulb)

It depends on the csa of the remainder of the lighting circuit and the supply fuse. If the rest is in 1.5mm and the supply fuse is 10amps then you gotta keep it all in 1.5mm

2. The fittings are double insulated and 'should not be earthed'. Should I simply snip off the earth core and leave it?

No you dont snip it. What on earth do you think its for (earth, geddit?)? Its there so the fuse blows if the cable gets damaged. Also you will have to check the Earth Fault loop Impedance at the end of the run after you finish so it can be certified. You cant do this if the earth isnt continuous.

3. . The actual connection box on the fitting is small and it is really difficult to connect 2 cores into each 'terminal'. So I bought some 15A connector strip blocks and planned to make the daisy connection in to one side, and take another short length of cable from the other side to the fitting. Is that a sensible/safe idea? Or should I squeeze them into the terminal as best as possible?

All connections must be in enclosed boxes and must be accessible. get some small round termination boxes or use the choc box enclosures.
You must not just stick them in term strip and stuff them back up the ceiling.

I hope you've got a fire alarm in your house, you might need it.

__________________
TTC

When you get to the end of your rope, tie a knot and hang on. - F.D.R.
Back to top
 Alert Moderators
quailtrailblue

from United Kingdom

Joined: 27 Oct 2006
Posts: 14
Location: Cambridgeshire,
United Kingdom
Thanked: 0 times

PostPosted: Sat Nov 24, 2007 8:21 pm    Post Subject:
Reply with quote Thanks

Hi TTC, thanks for your helpful comments. I had no idea that electrical work has to be inspected, the wiring diagrams say 'easy to fit'.....

Taylortwocities wrote:


Your specific questions:
1. Is the 1mm cable suitable for 6 downlights (50W bulb)

It depends on the csa of the remainder of the lighting circuit and the supply fuse. If the rest is in 1.5mm and the supply fuse is 10amps then you gotta keep it all in 1.5mm

The cable is actually 1.5mm, my mistake. I have no idea what the core surface area(??) is, but I can check.

2. The fittings are double insulated and 'should not be earthed'. Should I simply snip off the earth core and leave it?

No you dont snip it. What on earth do you think its for (earth, geddit?)? Its there so the fuse blows if the cable gets damaged. Also you will have to check the Earth Fault loop Impedance at the end of the run after you finish so it can be certified. You cant do this if the earth isnt continuous.

There is no provision for any earth connection on the fitting...??? which leaves a lonely earth core. The wiring diagram states that it must not be earthed....

3. . The actual connection box on the fitting is small and it is really difficult to connect 2 cores into each 'terminal'. So I bought some 15A connector strip blocks and planned to make the daisy connection in to one side, and take another short length of cable from the other side to the fitting. Is that a sensible/safe idea? Or should I squeeze them into the terminal as best as possible?

All connections must be in enclosed boxes and must be accessible. get some small round termination boxes or use the choc box enclosures.
You must not just stick them in term strip and stuff them back up the ceiling.

I hope you've got a fire alarm in your house, you might need it.
Back to top
 Alert Moderators
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 4940
Location: Oxfordshire,
United Kingdom
Thanked: 63 times

PostPosted: Sat Nov 24, 2007 10:39 pm    Post Subject:
Reply with quote Thanks

And BMW adverts say "easy to do 120mph"

I'm not surprised that you dont know. The govt brought in substantial legislation and has done a p*ss poor job of making people aware of it.

Details here: http://www.diynot.com/wiki/electrics:part_p:diy_electrical_work_and_the_law

If u need a registered spark look at www.competentperson.co.uk for someone in your area.

__________________
TTC

When you get to the end of your rope, tie a knot and hang on. - F.D.R.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
downlighter wiring help 2 800 Fri Apr 14, 2006 8:35 pm
Interesting Downlighter wiring.....with Piccies 3 880 Wed Mar 12, 2008 10:16 am
Downlighter Wiring to avoid fire risks 2 560 Sun Nov 18, 2007 10:12 pm
Wiring 4 off Low Voltage Downlighter Transformers 6 600 Sun Sep 11, 2005 8:25 pm
Halogen downlighter wiring 5 800 Thu Jul 15, 2004 5:15 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.