Help re broken ring

This topic originated from the How to page called Extending a ring circuit using existing sockets
Click here to return to the page called Extending a ring circuit using existing sockets.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
cords

from United Kingdom

Joined: 24 Nov 2007
Posts: 2
Location: London,
United Kingdom
Thanked: 0 times

PostPosted: Sat Nov 24, 2007 5:54 pm    Post Subject:
Help re broken ring
Reply with quote Thanks

Hi, I asked my builder to put two new double sockets in the living room. He did so but then told me he had broken the ring.. but that it would be ok. Im worried about this. But due to ignorance I dont know what to say to him.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Sat Nov 24, 2007 6:07 pm    Post Subject:
Reply with quote Thanks

Twhack him round the head with the biggest fring pan you can lay your hands on, then refuse to pay him for his work until it has been checked.

Next, employ an electrician to find out wether the work is safe, and if not rectify any problems.

A broken ring is not OK. It could be quite dangerous if left as it is.

__________________
I downlights
Back to top
 Alert Moderators
sparkydude

from United Kingdom

Joined: 10 Aug 2004
Posts: 303
Location: Staffordshire,
United Kingdom
Thanked: 2 times

PostPosted: Sat Nov 24, 2007 6:19 pm    Post Subject:
Reply with quote Thanks

Are you sure he said broken the ring and not broken INTO the ring?

The latter is fine, but the former is dangerous and should be changed

Nick
Back to top
 Alert Moderators
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 4940
Location: Oxfordshire,
United Kingdom
Thanked: 63 times

PostPosted: Sat Nov 24, 2007 7:28 pm    Post Subject:
Reply with quote Thanks

In any event, he should have tested the circuit for continuity, insulation resistance and something called earth fault loop resistance.

the results of the tests he would have noted on the Minor Works Certificate that he would have given you. He did give you one, didnt he icon_wink.gif

__________________
TTC

When you get to the end of your rope, tie a knot and hang on. - F.D.R.
Back to top
 Alert Moderators
sparkydude

from United Kingdom

Joined: 10 Aug 2004
Posts: 303
Location: Staffordshire,
United Kingdom
Thanked: 2 times

PostPosted: Sat Nov 24, 2007 7:36 pm    Post Subject:
Reply with quote Thanks

i would doubt that very much after all a builder doing electrical work is like second nature to him , like me as an electrician piloting the space shuttle icon_biggrin.gif icon_biggrin.gif icon_biggrin.gif icon_biggrin.gif
Back to top
 Alert Moderators
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 4940
Location: Oxfordshire,
United Kingdom
Thanked: 63 times

PostPosted: Sat Nov 24, 2007 7:59 pm    Post Subject:
Reply with quote Thanks

Yup, mix cement - install wiring - bill customer. Definite synergy.

__________________
TTC

When you get to the end of your rope, tie a knot and hang on. - F.D.R.
Back to top
 Alert Moderators
cords

from United Kingdom

Joined: 24 Nov 2007
Posts: 2
Location: London,
United Kingdom
Thanked: 0 times

PostPosted: Sat Nov 24, 2007 8:57 pm    Post Subject:
Thanks
Reply with quote Thanks

Thanks for your advice. He is a twerp, but will do properly if I insist. I just dont want to see that ugly mug again, making choices for me without giving me an option, then the works done. It goes on and on.
Back to top
 Alert Moderators
sparkydude

from United Kingdom

Joined: 10 Aug 2004
Posts: 303
Location: Staffordshire,
United Kingdom
Thanked: 2 times

PostPosted: Sat Nov 24, 2007 9:45 pm    Post Subject:
Reply with quote Thanks

You say he will do it properly if you insist, but as you are here asking a question about broken rings then obviously you do not know how it should be done and are now questioning his abilities therefore i recommend you get an electrician to look at the problem and not a bricklayer, or perhaps you know a carpenter who has a neon screwdriver who can sort it for you.

When a brick wall is built badly you can see it, when a socket is wired wrongly behind the faceplate you cannot , till it goes up in flames as it has been overloaded and is still on the 32A fuse for the ring main .
Nick
Back to top
 Alert Moderators
ricicle

from United Kingdom

Joined: 14 Sep 2006
Posts: 3488
Location: Gloucestershire,
United Kingdom
Thanked: 19 times

PostPosted: Sat Nov 24, 2007 9:51 pm    Post Subject:
Reply with quote Thanks

Taylortwocities wrote:
something called earth fault loop resistance.


Are you sure?........ icon_lol.gif icon_wink.gif

__________________
Empty barrels make the most noise.
Back to top
 Alert Moderators
sparkydude

from United Kingdom

Joined: 10 Aug 2004
Posts: 303
Location: Staffordshire,
United Kingdom
Thanked: 2 times

PostPosted: Sat Nov 24, 2007 9:55 pm    Post Subject:
Reply with quote Thanks

i think he means earth fault loop impedance

not resistance

Nick
Back to top
 Alert Moderators
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 4940
Location: Oxfordshire,
United Kingdom
Thanked: 63 times

PostPosted: Sat Nov 24, 2007 10:41 pm    Post Subject:
Reply with quote Thanks

OK so I'm a bit DC today...

__________________
TTC

When you get to the end of your rope, tie a knot and hang on. - F.D.R.
Back to top
 Alert Moderators
celticrsuperb

from United Kingdom

Joined: 28 Apr 2008
Posts: 7
Location: Glasgow,
United Kingdom
Thanked: 0 times

PostPosted: Tue Apr 29, 2008 5:58 pm    Post Subject:
Reply with quote Thanks

get an NIC EIC approved sparky to sort this pronto
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12858
Location: Yorkshire,
United Kingdom
Thanked: 22 times

PostPosted: Tue Apr 29, 2008 6:00 pm    Post Subject:
Reply with quote Thanks

I think he has. It was 6 months ago, after all.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16491
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Tue Apr 29, 2008 8:13 pm    Post Subject:
Reply with quote Thanks

sparkydude wrote:
i would doubt that very much after all a builder doing electrical work is like second nature to him , like me as an electrician piloting the space shuttle icon_biggrin.gif icon_biggrin.gif icon_biggrin.gif icon_biggrin.gif


No wonder your out of hours call-out bill is huge!!

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Broken ring main or two radials? 2 360 Thu May 11, 2006 6:40 pm
Locating a broken earth in a ring final circuit? 3 560 Sat Mar 31, 2007 7:25 pm
Broken ring.... 2 380 Mon Jul 09, 2007 10:09 am
Broken Ring!! 2 340 Thu Apr 14, 2005 1:51 pm
How to find a broken ring! 9 540 Thu Oct 22, 2009 1:31 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.