Posted: Fri Jul 09, 2004 7:15 am Post Subject: |
 |
|
So long as the redundant cable is sound and has the required insulation resistance and cpc ('earth') continuity it should be usable. (are you able to check these?) Your circuit protective device should be rated larger than the design current (the current drawn by your immersion heater) and smaller than the current-carrying capacity of the cable. A 30 A breaker suggests it's either a BS3871 or a plug-in fuse replacement. If it's the former you may find it impossible to replace, but a 6mm cable should carry more than 30A in most domestic situations so you can leave that as is. (Although, ideally, you'd replace it with a breaker closer to your design current.)
You should have local isolation at the business end. A fused connection unit not only gives you local isolation and fusing, it also allows you to de-rate and connect the heat-resistant flex you'll no doubt be using between the fcu and the immersion.
(If in doubt, get somebody to check it all out for you professionally) |
|
yushoo

Joined: 09 Jul 2004 Posts: 2 Location: United Kingdom Thanked: 0 times
|
Posted: Fri Jul 09, 2004 8:03 am Post Subject: Fuse/Cable Relationship |
 |
|
Thanks dingbat for the quick reply. As you suggested the breaker is a plug-in fuse replacement. Will follow your advice and thanks again for your help. |
|