Hi everyone.
I have the above condensing boiler with a hot water cylinder. For the past few weeks it has been coming up with an F1 fault. the manual says ignition. It only does this now and again.
I had a local CORGI come and have a look. He said it was common on glowworms and asked if anyone had been and altered the gas. We have been here a year and not in that time. He used a gas analyser and said it was ok. He also changed an electrode (looked like a little spark plug). He did say that the fault may persist.
He was right and we are back to having some F1 faults and having to reset the boiler. Any ideas as to what else may be causing this. Don't want the boiler breaking down over xmas and i know the engineer is working away.
Thanks
Paul |
|
| Back to top |
|
|
|
If you do not want to see this advert, click here to login or if you are new click here to join free. |
 |
fitz1

Joined: 24 Nov 2004 Posts: 1983 Location: Merseyside, United Kingdom Thanked: 18 times
|
Posted: Tue Dec 18, 2007 10:23 pm |
|
|
Get someone to check the governor on the gas meter.Also is there a similar time zone in which it happens. |
|
| Back to top |
|
|
|
 |
petit_pablo

Joined: 18 Nov 2007 Posts: 5658 Location: Lincolnshire, United Kingdom Thanked: 748 times
|
Posted: Tue Dec 18, 2007 10:29 pm |
|
|
Many things can cause the F1 fault.
Low rate can drop out if incorrectly set as can high rate.
Condensate backing up to the heat exchanger
Moisture getting on the spark electrode.
or, PCB.
Id personally check all the above 1st though. Board would be a last resort |
|
| Back to top |
|
|
|
 |
fitz1

Joined: 24 Nov 2004 Posts: 1983 Location: Merseyside, United Kingdom Thanked: 18 times
|
Posted: Tue Dec 18, 2007 10:34 pm |
|
|
did one earlier this year with similar fault . everything checked out o.k except the governor on the meter . was steady , but would suddenly jump to about 28 to 30 mb. transco changed gov and all was o.k. |
|
| Back to top |
|
|
|
|
|
 |
paul-hutt

Joined: 18 Dec 2007 Posts: 3 Location: United Kingdom
|
Posted: Tue Dec 18, 2007 10:37 pm |
|
|
Thanks for your reply. Wife said earlier it came up with a ? F13 fault.
How can i check out what pablo suggested (not the pcb-obviously)
I'll also ask transco to check the meter govenor |
|
| Back to top |
|
|
|
 |
Rob

Joined: 14 Aug 2006 Posts: 3611 Location: London, United Kingdom Thanked: 187 times
|
Posted: Tue Dec 18, 2007 10:44 pm |
|
|
Have this boiler indoors  Had the intermittant F1 aswell till my mum made me fix it.
I found the graphite seals were leaking and replaced. Corgi job. All ok since. |
|
| Back to top |
|
|
|
 |
paul-hutt

Joined: 18 Dec 2007 Posts: 3 Location: United Kingdom
|
Posted: Tue Dec 18, 2007 11:01 pm |
|
|
Graphite seals - i suppose these seal the burner in place.
Approx how much to replace?? |
|
| Back to top |
|
|
|
 |
petit_pablo

Joined: 18 Nov 2007 Posts: 5658 Location: Lincolnshire, United Kingdom Thanked: 748 times
|
Posted: Tue Dec 18, 2007 11:15 pm |
|
|
All the things i mentioned are corgi teritory im afraid, as is the door seal. The originals were rubber on early models and some perish. I found these perishing can cause F5 faults too but that another story! |
|
| Back to top |
|
|
|
|
|
 |
|
|