new consumer unit
Reply with quote Thanks

I was looking to install a new unit as the one that i have is forty years old.
I have run new ring circuit cables and new lighting circuit cable and they are ready to connect to the consumer unit, but i want to install a new con.unit.(10 mcbs)
Any info, on disconnecting the old one.
Please note that i am not an electrician and the quotes that i have received are a joke?
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
mingmong

from United Kingdom

Joined: 12 Sep 2004
Posts: 28
Location: Sheffield,
United Kingdom
Thanked: 0 times

PostPosted: Tue Sep 14, 2004 4:28 pm    Post Subject:
Reply with quote Thanks

How much have you been quoted?
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Tue Sep 14, 2004 4:34 pm    Post Subject:
Reply with quote Thanks

someone is going to have to pull the service fuse

technically you are supposed to get the rec to do it but in reality this is usually both expensive and impractical (or sometimes even impossible when everyone starts to pass the buck)

most electricians i know jup pull it themselves but this is not generally reccomended for diyers

if you are going to do it yourself bear in mind the following points
1: there may be exposed live parts during and after pulling so take care to only touch plastic parts

2: make sure there is no current flowing by turning off the main switch first to prevent arcing
Back to top
 Alert Moderators
dingbat

from United Kingdom

Joined: 29 Sep 2003
Posts: 2205
Location: West Midlands,
United Kingdom
Thanked: 0 times

PostPosted: Tue Sep 14, 2004 4:54 pm    Post Subject:
Re: new consumer unit
Reply with quote Thanks

staffy wrote:
... the quotes that i have received are a joke?


I usually charge in the region of £250-350, depending on the number of circuits, accessibility, etc. By the time you've disconnected, tested everything, sorted out any snags, mounted and connected up the new unit, done the live tests, written out certificates and tidied up it can easily be the best part of a day's work in some properties. Your electricity company may well quote £400-500. How far out are your quotes?
Back to top
 Alert Moderators
benjiman

from United Kingdom

Joined: 21 Jul 2004
Posts: 157
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue Sep 14, 2004 7:36 pm    Post Subject:
Reply with quote Thanks

plugwash wrote:
someone is going to have to pull the service fuse


A friend of mine said he done his one without pulling the service fuse. He needed new cables as the old ones were too short.

He took out the live (and neutral) cable that comes from the consumer unit and goes in a box with a lid on it. This has a seal, which he broke. Then he unscrewed the old live cable that goes into this box and pulled it out. Same with neutral.

Then first connected the new cables (L and N) into the new consumer unit. Then connected the ends of the new live and neutral cables into the box.

All this done while everything was still live.

Is this safe to do and should it be done like this? Or do most pros play it safe and pull the fuse so everything is dead?

BTW what is arcing?
Back to top
 Alert Moderators
kai

from United Kingdom

Joined: 15 Aug 2004
Posts: 729
Location: United Kingdom
Thanked: 5 times

PostPosted: Tue Sep 14, 2004 7:52 pm    Post Subject:
arcing..
Reply with quote Thanks

Arcing is where an electrical spark jumps across live metal.

Or when a cable gets hit by an JCB digger etc, and a mighty BANG results, as happened the other day where I worked.

Back to top
 Alert Moderators
fubar

from United Kingdom

Joined: 27 Aug 2004
Posts: 108
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue Sep 14, 2004 8:05 pm    Post Subject:
Reply with quote Thanks

benjiman wrote:

All this done while everything was still live.

Is this safe to do and should it be done like this? Or do most pros play it safe and pull the fuse so everything is dead?


It is not safe to work on live equipment. There is a common mis-conception that electricans always work on live equipment - in fact they rarely do and only when there is absolutely no alternative.

A pro would choose to pull the main fuse.

Quote:

BTW what is arcing?


Arching is when electricity jumps an air gap. The greater the voltage and current, the greater the distance that can be jumped.

--
Michael
Back to top
 Alert Moderators
Damocles

from United Kingdom

Joined: 14 Sep 2004
Posts: 1291
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue Sep 14, 2004 8:55 pm    Post Subject:
Reply with quote Thanks

Breakdown voltage of air is about 1KV/mm (yeah,well I had to look it up, but thought that was about right).

So if you keep the live more than 0.5mm away from any other conductor, then it should not arc. But god help you if it gets any closer, because once the arc has started the air will ionise and then its arc welders-R-us.

Turn off the power.(by pulling fuse, or getting it pulled). Even if you have, still work on it as if it was live. One day it may be. Use insulated tools (screwdriver shafts!). Think about which wire to disconnect first. Disconnect the end feeding the power first.

If i was even remotely considering moving live wires capable of supplying 500A for a short period, I would be damn sure that if I was stuffing thick unbending copper cables through a small hole into a plastic box, that there was absolutely nothing else inside it which was connected to anything else. That way, even if the live end hit anything, it could not short out. That any switches inside the aforementioned plastic box were off.

You need to take care with thick tough cables that the screws are really pressing tight and holding the cables properly.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16485
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Tue Sep 14, 2004 10:09 pm    Post Subject:
Reply with quote Thanks

Yes. I agree with Fubar.

Please, DIY'ers, DON'T work live, and get your REC to pull the fuse. You can always have an isolator fitted so you don't have to get them back every five minutes.

Working live unprotected and untrained is absolute madness.

In 17 years, I have worked live 3 times, and NEVER on the main tails. Always wearing the proper kit, boots gloves, rubber mat etc.. and fully insulated tools.

Here is my isolator:

Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Wed Sep 15, 2004 6:32 am    Post Subject:
Reply with quote Thanks

bad termination of those tails to the meter though

i see stripped sheath......
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Wed Sep 15, 2004 7:10 am    Post Subject:
Reply with quote Thanks

afaict the main reason for working live is to add a cuircuit in a situation where it would cause huge disruption to turn off the DB/CU

or for working on (spurring off attaching something to a spur etc) a cable outside when that cable is supplying lots of stuff and would cause hige distruption to isolate (this is afaict the main reason recs work live)
Back to top
 Alert Moderators
daveaspy

from United Kingdom

Joined: 14 Sep 2004
Posts: 26
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Sep 15, 2004 10:04 am    Post Subject:
Reply with quote Thanks

How should tails be terminated/stripped? I am guessing you should have a little bit of the red/black showing inside the enclosure and only the grey outer insulation showing outside the enclosure?
Back to top
 Alert Moderators
breezer

from United Kingdom

Joined: 03 Jan 2003
Posts: 23346
Location: Sussex,
United Kingdom
Thanked: 5 times

PostPosted: Wed Sep 15, 2004 12:01 pm    Post Subject:
Reply with quote Thanks

that is correct

__________________
Do you like music Mr Finch?
Forum = Opinions
Back to top
 Alert Moderators
staffy

from United Kingdom

Joined: 14 Sep 2004
Posts: 2
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Sep 16, 2004 12:29 pm    Post Subject:
Reply with quote Thanks

Sorry for taking so long to reply WORK WORK WORK

I was quoted in the region of £600-£750 and when i asked how much to rewire the whole house, the quote was £2000-£3500.
Excuse me for being stupid but it is only a 3 bed-semi.
Do you recommend pulling the service fuse and if so what precautions can i take,and what safety precautions or checks to make sure that everything is in order before doing so. icon_rolleyes.gif
[/quote]
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21985
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu Sep 16, 2004 2:02 pm    Post Subject:
Reply with quote Thanks

staffy wrote:
I was quoted in the region of £600-£750 and when i asked how much to rewire the whole house, the quote was £2000-£3500.

Not necessarily OTT - it depends a lot on where you are, and how easy it is to access the infrastructure in your house. But it is possible that the guy didn't want the job - it's fairly common for tradesmen to give daft quotes rather than say "no", for some reason...
How many quotes did you get?

Quote:
Excuse me for being stupid but it is only a 3 bed-semi.

I don't think you realise how much can be involved.

Quote:
Do you recommend pulling the service fuse

No, but...

Quote:
and if so what precautions can i take,and what safety precautions or checks to make sure that everything is in order before doing so. icon_rolleyes.gif

Think about how you will fix a mechanically strong (i.e. not a polythene bag) insulating cover over the exposed fuse terminals while you're working
Make sure everything is off (i.e. main switch(es) on the CU(s))
Make sure that you have good access to the fuse, and that it will pull out cleanly when you go for it.
Having cut the seals and pulled the fuse, securely fit the cover you've made.
When putting it back in, again make sure everything is off.

I take it that you have done proper continuity, loop resistance and insulation tests on the new circuits that you've installed?

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2, 3  Next
Page 1 of 3

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
consumer unit getting hot 10 420 Fri Nov 02, 2007 1:25 pm
Replacing CONSUMER UNIT queries 6 780 Fri Nov 02, 2007 6:47 pm
consumer unit mounting 2 640 Sat Nov 03, 2007 9:12 pm
Consumer unit fuseway / ring-main 33 1620 Fri Nov 02, 2007 12:54 pm
Installation on Consumer unit in new build detached garage 2 660 Fri Nov 02, 2007 10:37 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.