Hi,

I suspect my Landis & Gyr RWB2 Programmer to be faulty as my HW is working fine but I have no CH. I have tested the room thermostat, pump and 3 way valve which are all working fine.

Does anyone know which contacts I can short on the backplate to bypass the programmer and see if the CH fires up to confirm if it is the programmer at fault?

Thanks
Rod
 
Sponsored Links
Does anyone know which contacts I can short on the backplate to bypass the programmer and see if the CH fires up to confirm if it is the programmer at fault?
Terminal 4 is the CH ON terminal; so if you link this to the L terminal you will bypass the CH side of the programmer and the boiler should then work (providing it is not something else ;) )
 
Terminal 4 is the CH ON terminal; so if you link this to the L terminal you will bypass the CH side of the programmer and the boiler should then work (providing it is not something else ;) )

Thanks, that worked a treat :D

I'm off to buy a new programmer now.

Thanks
Rod
 