PostPosted: Thu Jul 10, 2008 2:22 pm Reply with quote

I'm sorry if this is something that has already been answered.
I have a Potterton Suprima 80 boiler.
Lately my central heating wont come on but the hot water works ok. The thermostat in the hall comes on but the boiler doesn't fire up.
Sometimes when the hot water and central heating is on the radiators warm up. But only when the hot water is on.
I've checked out the PCB but all the solder connections look ok
I've also noticed a steady drip from an overflow pipe out the back (don't know where it is coming from). It looks like it drips all night but stops in the day. don't know whether it is related to the heating problem.
Would be grateful if anyone has any advice.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
EliteHeat

from United Kingdom

Joined: 28 Jan 2006
Posts: 1094
Location: London,
United Kingdom
Thanked: 2 times

PostPosted: Thu Jul 10, 2008 3:49 pm Reply with quote

Check your motorised valve(s) first. Almost certainly duff.
Back to top
 Alert Moderators
Softus

from United Kingdom

Joined: 21 Oct 2004
Posts: 19558
Location: United Kingdom
Thanked: 9 times

PostPosted: Fri Jul 11, 2008 12:26 am Reply with quote

Sausage wrote:
I've also noticed a steady drip from an overflow pipe out the back (don't know where it is coming from). It looks like it drips all night but stops in the day. don't know whether it is related to the heating problem.

Well it isn't a good sign.

Have you checked the system pressure?

What does it read when the system is cold?

What does it read when the system is hot?
Back to top
 Alert Moderators
garrymum

from United Kingdom

Joined: 16 Sep 2004
Posts: 653
Location: Leeds,
United Kingdom
Thanked: 5 times

PostPosted: Fri Jul 11, 2008 8:21 am Reply with quote

EliteHeat wrote:
Check your motorised valve(s) first. Almost certainly duff.


Maybe the motor in the motorised valve. I had the same problem years ago, water fine, CH not working. Replaced the motor in the valve and that cured it. Worth trying, it's only a cheap part ( 13 from screwfix)

http://www.screwfix.com/prods/28670/Plumbing/Central-Heating-Controls/Drayton-Synchronous-Motor
Back to top
 Alert Moderators
Softus

from United Kingdom

Joined: 21 Oct 2004
Posts: 19558
Location: United Kingdom
Thanked: 9 times

PostPosted: Fri Jul 11, 2008 5:17 pm Reply with quote

Would any of the people who think it's a MZV care to explain how that accounts for water dripping out an overflow pipe (sic.)?

Diagnosis consists of more than just listing various parts you've replaced in the past. icon_rolleyes.gif
Back to top
 Alert Moderators
uselessFCUK

from United Kingdom

Joined: 05 Jan 2005
Posts: 119
Location: United Kingdom

PostPosted: Fri Jul 11, 2008 11:23 pm Reply with quote

Sausage wrote:
I've also noticed a steady drip from an overflow pipe out the back (don't know where it is coming from). It looks like it drips all night but stops in the day. don't know whether it is related to the heating problem.


Quite likely your cold water storage cistern float valve passing... water used in the day keeps the level at or around desired level, yet when not in use the valve passes enough water to creep the level to the overflow point. Depending on type of valve; replace seal.

icon_question.gif

Regards
UF
Back to top
 Alert Moderators
Sausage

from United Kingdom

Joined: 02 Apr 2004
Posts: 12
Location: United Kingdom

PostPosted: Sat Jul 12, 2008 10:14 am Reply with quote

I'll get a new motor a replace.
Just to check. The boiler will only fire-up when the motorised valve has moved to the correct position. Is there some feedback to the boiler?
Back to top
 Alert Moderators
Softus

from United Kingdom

Joined: 21 Oct 2004
Posts: 19558
Location: United Kingdom
Thanked: 9 times

PostPosted: Sat Jul 12, 2008 11:32 am Reply with quote

Sausage wrote:
I'll get a new motor a replace.

Oh. My. God.

Why are you going to do that? Is the existing motor faulty?

Quote:
Just to check. The boiler will only fire-up when the motorised valve has moved to the correct position. Is there some feedback to the boiler?

It isn't "feedback". The boiler is provided with an electrical supply termed a 'demand for heat' via the programmer, a thermostat, and the switch in the motorised valve.

Have you carried out any tests, at all, of any sort?
Back to top
 Alert Moderators
Sausage

from United Kingdom

Joined: 02 Apr 2004
Posts: 12
Location: United Kingdom

PostPosted: Sat Jul 12, 2008 6:13 pm Reply with quote

No I haven't carried out any checks.
If you can list a few I will have a go.

Currently in order to get the heating on I have pushed the manual overide slider into a locked position (bottom of motorised valve). When the hot water is then switched on the water is also pumped into the radiators.

The water coming out of the overflow pipe out the back has been happening for a few months. The lack of CH has only just happened.

If there are any checks which I can carry out before changing the motor please let me know.
Back to top
 Alert Moderators
MANDATE

from United Kingdom

Joined: 06 Mar 2003
Posts: 2290
Location: Manchester,
United Kingdom
Thanked: 129 times

PostPosted: Sat Jul 12, 2008 7:29 pm Reply with quote

If the valve does not move from the HW position when power is applied, it is most likely the motor at fault. But first make sure power is being applied.
The programmer supplies power to the room stat, then the room stat ( when turned up) provides power to the MZV.
If power is there on the relevent wire you know room stat is functioning and prolem is within valve.
Have you tried removing the actuator head off the valve spindle to see if the spindle is too stiff. You will struggle if you don't get more familier with your MZV and how it functions and the wiring.
There's a lot been written on here on 3 port valves and related problems
icon_rolleyes.gif
Back to top
 Alert Moderators
Sausage

from United Kingdom

Joined: 02 Apr 2004
Posts: 12
Location: United Kingdom

PostPosted: Mon Jul 14, 2008 10:35 pm Reply with quote

Thanks for the information.
I have taken some measurements from the junction box.

There are 9 terminals being used.
Below is the relevant measurements from each of the terminals.

OFF HW ON CH ON
1 240V 240V 240V
2 0.3V 0.3V 240V
3 Gnd Gnd Gnd
4 Gnd Gnd Gnd
5 240V 180V 240V
6 27.2V 240V 23V
7 0V 240V 0V PUMP
8 23.4V 240V 23.4V
9 Earth Earth Earth

I hope someone can confirm the fault by these measurements.
One more thing, there is also a buzzing noise coming from the motorised valve. Perhaps another indicator that something is up with it.
Back to top
 Alert Moderators
MANDATE

from United Kingdom

Joined: 06 Mar 2003
Posts: 2290
Location: Manchester,
United Kingdom
Thanked: 129 times

PostPosted: Tue Jul 15, 2008 9:53 pm Reply with quote

without knowing what is connected to what at the terminals your measurements don't mean much.
Beside any earth and neutral wires your MZV should have 3 other wires.
These are usually white, grey and orange wires (if its a modern 3 port valve). The room stat, when turned up should make the white wire live and confirms everything ok up to the MZV.
It's the white that drives the motor over the first half of the full range
If you set the programmer to HW only all power to the motor is removed and the motor unwinds to the rest position by the return spring.
If you now put programmer to CH only the motor should move and you should be able to hear it move or if you have the head removed you should be able to see it move.
When the valve reaches mid way, power is switched from white wire to grey wire. motor then continues along second half of range.
During the second half a micro switch is operated and allows power out of the MZV through the orange wire to light boiler.
Question is? is the motor moving or not. and dont forget a stiff spindle could also be the cause.
So its, power at the white wire? remove head stiff spindle? does motor move to CH position? if not replace motor if it does micro switch faulty replace actuator head.
I would not worry about the buzzing sound. In the CH only position the motor comes up against a stop so although it's not turning it is energised to keep it there.
Likewise in the mid position a modified voltage holds the motor against the return spring.
icon_rolleyes.gif
Back to top
 Alert Moderators
Sausage

from United Kingdom

Joined: 02 Apr 2004
Posts: 12
Location: United Kingdom

PostPosted: Sun Aug 17, 2008 6:39 pm Reply with quote

Sorry for very late reply.

Just to let you know, changed the motor in the motorised valve and everything is working great.

Thanks for the advice.
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52973
Location: London,
United Kingdom
Thanked: 3343 times

PostPosted: Sun Aug 17, 2008 6:44 pm Reply with quote

Softus wrote:
Would any of the people who think it's a MZV care to explain how that accounts for water dripping out an overflow pipe (sic.)?



Well he claims its all OK now so perhaps it is?
Back to top
 Alert Moderators
spacethegas

from United Kingdom

Joined: 23 Jun 2008
Posts: 1214
Location: Wiltshire,
United Kingdom
Thanked: 2 times

PostPosted: Sun Aug 17, 2008 9:39 pm Reply with quote

guaranteed to sort out the overflow leak.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Central Heating doesn't work unless hot water stat cold 16 160 Tue Apr 09, 2013 6:59 pm
Central heating - doesn't work in the afternoon/evening 2 80 Mon Nov 21, 2011 3:53 pm
Power Cut last night now central heating doesn't work! 14 220 Sat Oct 26, 2013 10:10 am
Central heating just doesn't work properly anymore. 8 120 Fri Dec 28, 2012 5:58 pm
Central heating doesn't work after removing a radiator 2 80 Sun Apr 22, 2012 12:56 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.