Can someone please check my diagram. Please!
thanks for getting back to me jj.
another question please.
the instructions on the spot lights say i need to use 10mm cable.
to down size from the original cable do i use a junction box?
also from the third light (i.e before the spotlights) can i put a junction box in place so i can take the cable to another bedroom?
All junction boxes need to be accessible. Never heard of 10mm cable being used in a lighting circuit.
If you compare 12 to 230 volt lamps at 1.5mm for 230v and 10mm for 12v and 50w lamps in both and say 10 meters of cable.
230v = 0.217A = 63mV volt drop
12v = 4.16A = 183mV volt drop
with 1.5mm cable 12v = 1.2V volt drop
Looking at those figures I can see why 10mm cable would be recommended however one has to consider how close the inverter or transformer is from the lamp!
If as in my bathroom a single unit supplies 4 lamps with separate cable to each lamp the 4mm would be ample but if daisy changed then the 10mm would make sense.
4 lamps equal spread on 10 meters of 10mm cable will mean last lamp has a 0.36 volt drop at 12 volt this is quite a lot.
Good reason for using GU10 where permitted instead.
10mm makes me think an error has been made - GU10 are 230v?
10mm is the size which you would normally use for an electric shower, bit on the big side for 5 mains 50w lamps!
Is the fan a timed variety?
Are you going to run the supply to the light switch, join the 2 neutrals in there, the 2 earths in there and run L, N & E to each lamp?
The circuit for the bathroom needs to be RCD protected.
This work is notifiable to your LABC under part p of the building regs.
Have you missed a decimal point when reading, e.g. it might be stating that it must be run in a minimum of 1.0mm, which would make sense...
sorry my bad. it is meant to read 1.0mm
thanks for the replies everyone cheers.