Under floor heating control programmer burnt out
Reply with quote Thanks

A client who I am working for has a problem with her electric underfloor heating about 20msq under travertine marble in a basement kitchen.

After the cold weather last week she returned to her house to find the programmer had burnt out internally with carbon staining all over the pcb.
The 2.5mm cable from the consumer unit had the insulation sheathing melted around the contacts at the back too.

The unit is on a 20amp mcb and also an rcd. These had not tripped.
The wiring in the control box which is fed by the programmer for the underfloor circuits appears all correct and undamaged.

Any ideas as to what may have caused this to happen please?

The system was installed over a year ago and used on a daily basis during the colder months for about 8hrs a day.

Thanks
Pete
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
sparkyspike

from United Kingdom

Joined: 14 Jan 2007
Posts: 1673
Location: Sussex,
United Kingdom
Thanked: 17 times

PostPosted: Thu Jan 15, 2009 10:52 pm    Post Subject:
Reply with quote Thanks

Do you know how many watts the mat runs at? If it's a 200W per sqm mat, was it fitted with a contactor? The contactor would allow more current to be used than the thermostat could otherwise handle. If a contactor hasn't been fitted, then the thermostat could have been overloaded, hence burning itself out. The 20A mcb or rcd would not necessarily trip.

Has a 13A fcu been fitted, or a 20A DP switch?

__________________
Are those my feet?
Back to top
 Alert Moderators
Fluffster

from United Kingdom

Joined: 05 Jul 2006
Posts: 971
Location: London,
United Kingdom
Thanked: 2 times

PostPosted: Fri Jan 16, 2009 8:35 am    Post Subject:
Reply with quote Thanks

Thanks Spike much obliged.
I will advise her.
There is only a 20amp mcb no dp switch or fused switch inline either.

Pete
Back to top
 Alert Moderators
sparkyspike

from United Kingdom

Joined: 14 Jan 2007
Posts: 1673
Location: Sussex,
United Kingdom
Thanked: 17 times

PostPosted: Fri Jan 16, 2009 9:17 pm    Post Subject:
Reply with quote Thanks

Ok. If there's no fuse other than the 20A mcb, then it is likely to be a 4kW (17A) system, which will require a contactor. The thermostats you get in those programmers can only handle up to 13-15 amps. As the installer omitted the DP switch, then he probaby omitted the contactor too!

__________________
Are those my feet?
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21986
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Fri Jan 16, 2009 11:34 pm    Post Subject:
Reply with quote Thanks

Did the installer provide a certificate to say that it had been done in compliance with BS 7671?

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Burnt Cooker Control Unit 3 220 Mon Jul 07, 2008 7:12 pm
Recurring electric shower fuse problem – burnt fuse holder 7 1000 Thu Nov 22, 2007 4:28 pm
Burnt electic shower switch 24 1740 Thu Dec 06, 2007 10:02 am
Burnt tails 11 680 Fri Oct 19, 2007 3:30 pm