cooker circuit breaker

Joined
15 Nov 2004
Messages
4
Reaction score
0
Country
United Kingdom
I have a new cooker. 6 months ago had it installed. Then it kept tripping. It has gone worse now, so I have left breaker off, and cannot use my cooker. I had an electrician in, he tested the wires, and said I have a very small leakage somewhere. He advised me to get a 40 wirlex breaker, as he said the 32 one is very sensitve for it. Will this not just be covering over the problem, as obviously I have a leakage to earth. Can someone please help me with this, before I cook the christmas Turkey. Thanks again Lisa :cry:
 
Sponsored Links
What kind of leakage did he say it was?

Is the appliance damp?

Is it tripping the MCB or the RCD?

Have you contacted the retailer? Having sold you the goods, they are responsible for any repair or replacement necessary.
 
What is tripping - is it the MCB for the cooker circuit, or an RCD?

Or is the cooker circuit on an RCBO?

It's just that if you have a slight earth leakage (not uncommon with cookers), this will not trip an MCB, but it will trip an RCBO, or the RCD protecting that circuit.

But in that case, swapping it to a 40A device will not solve anything - you'll still have an earth fault, and the RCD, or a 40A RCBO will still trip.

If it is an MCB which is tripping, then this has nothing to do with a very small earth leakage - to put it in perspective, it takes literally more than a thousand times as much current to trip your MCB than the fault current needed to trip an RCD or RCBO.

So I'm not sure that the electrician's advice makes sense....

What is the rating of the cooker, and what is the size of the cable?

Does it trip when any part of it is turned on, or when all of it is in use?

Have you recently added anything else to the circuit, or is there a socket on the control unit into which you plug another appliance?

Have you recently put up any shelves etc in the vicinity of the cable that supplies the cooker?

Did the electrician test the cooker and the cable separately?
 
Sponsored Links
:D Thanks very much for your help on this topic. I am not well up on electrics,and all I know is that he did not test the cooker, he just tested the wires in the cooker socket which showed the small leakage, it trips the red switch in the fuse box, I switch it back on, it does not go for a while then blows again. I did not think that having a 40 a would make much difference. The electrician said that these breakers are very sensitive and will pick up anything. But it still does not solve the problem of the leakage. All around my house the sockets etc were tested, and they came up as reading neutral, which really worries me. A builder who lived here before we bought this house did a bit of diy, and looks like he may have bottched up the witring somehow.No shelves have been fitted near the main wire either :cry: Anyone know any cheap sparkys in oldham :p Thanks again to all. :arrow:
 
hellraiser said:
it trips the red switch in the fuse box
Do you mean the main switch, or one of them , which controls either all of the circuits, or a group of them?
 
Hi again, there are other switches in the box, it just keeps tripping the cooker one on its own lisa
 
Is it an MCB, or an RCBO (does it have a test button, as well as the up/down on/off switch rocker?)
 
Lisa, have you any idea what these guy are talking about? It's all very well throwing terminology like MCB, RCBO etc, etc but does this mean anything to you?

an RCBO (does it have a test button, as well as the up/down on/off switch rocker?)

Does the cooker switch have a test button on it? The reason behind this is that if it's an RCBO (residual current circuit breaker with over current protection) it has two functions. One is to protect against the cooker drawing too much current in case of an overload, the second is to detect a leakage between live and earth as happens when you touch the live parts.

An MCB (main circuit breaker) just provides overload protection.

If there is a leakage current in the cooker it will trip an RCBO.

Here's a typical MCB:

MK5903SX.jpg


Here's an RCBO:

CM93203.jpg


Does this help?
 
IanDB said:
An MCB (main circuit breaker) just provides overload protection.

......................and short circuit protection!!
 
Thankyou this has actually help my question aswell as i was wondering where i would find the circuit box and tell the w for the cooker mine says 240w
 
OK. So go and start a nice new topic of your own, instead of digging up this 10 year old one.:rolleyes:

Do that and someone might answer your question.
 