PostPosted: Wed Feb 11, 2009 1:28 pm Reply with quote

Hi, I have a couple question regarding the preparation of the sub-floor for underfloor heating, I hope someone can help me.

I will be having UFH installed in my kitchen, it is a suspended timber floor, the finished surface is to be tiled.

I intend to prepare the floor myself, the plan being to remove the existing floor boards (to reduce the final overall build-up) and screw 18mm ply directly to the joists, with a further 10mm on top, running in the other direction, staggering joints as suggested by the BS.

1)
Will this provide a stiff enough base (considering I have removed the original floor boards) for my tiling? Or do I need a thicker ply build-up?

2)
What build up is required above the ply, ie screed or insulation mats?

I expect the answer my depend on whether I am having electric or hot water - Ideally I would like hot water as I have heard it is a 'more even heat' any advice on this and how it would effect the base required would also be much appreciated.

Thanks in advance for your help.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
John506

from United Kingdom

Joined: 14 Nov 2006
Posts: 1341
Location: Merseyside,
United Kingdom
Thanked: 69 times

PostPosted: Wed Feb 11, 2009 2:20 pm Reply with quote

Whilst I can only help you with your first question.

I would screw all the existing floorboards down as much as you can (watching you dont hit pipes or wires) and lay the ply ontop of that, countersinking screws along the joists, then between the screws in the joist, another load of screws into the floorboards.

First though I would check all pipework under the floorboards is all strong soldered joints as removing the floor for leaks etc will be a PAIN!

Try and make the gap between each screw 6inches north, south, east & west, to ensure the board is nice and tight

When we have done this for bathroom floors which are also being tiled, the boss has gone and bought a big saver tub of 1000 2inch screws and we do use a hell of alot just to be sure.

We have never put down a second layer and the tiles have all been fine, as long as it is solid then you are good to go.

And between joints in the ply, screw screws either side every 2 inches.
Back to top
 Alert Moderators
swidders

from United Kingdom

Joined: 19 Jan 2009
Posts: 1410
Location: Manchester,
United Kingdom

PostPosted: Wed Feb 11, 2009 7:23 pm Reply with quote

wjrc wrote:
Hi, I have a couple question regarding the preparation of the sub-floor for underfloor heating, I hope someone can help me.

I will be having UFH installed in my kitchen, it is a suspended timber floor, the finished surface is to be tiled.


You need to decide now if it's wet or electric since wet goes under with insulation and screed between joists etc, whereas electric doesn't and can go within adhesive used for floor tiles

wjrc wrote:

I intend to prepare the floor myself, the plan being to remove the existing floor boards (to reduce the final overall build-up) and screw 18mm ply directly to the joists, with a further 10mm on top, running in the other direction, staggering joints as suggested by the BS.


T&G flooring sheets will be more solid and enable you not to have to have joints on joists
wjrc wrote:

1)
Will this provide a stiff enough base (considering I have removed the original floor boards) for my tiling? Or do I need a thicker ply build-up?
depends on joist spacings but sounds like overkill
wjrc wrote:

2)
What build up is required above the ply, ie screed or insulation mats?

I expect the answer my depend on whether I am having electric or hot water - Ideally I would like hot water as I have heard it is a 'more even heat' any advice on this and how it would effect the base required would also be much appreciated.

Exactly - screed will go on insulation (kingspan or cellotex) between joists if wet system
Back to top
 Alert Moderators
MadAlicesDad

from United Kingdom

Joined: 05 Nov 2008
Posts: 144
Location: United Kingdom
Thanked: 1 time

PostPosted: Wed Feb 11, 2009 8:34 pm Reply with quote

Can't comment on how to tile on board, but from my experience, don't expect UFH to heat the room significantly! I suspect if it were left running all day it would warm the room slightly, but if you're running it off the radiator timer, then you may find you need a second heat source in the room.
I've just fitted water UFH under a timber floor in the dining room. 75mm kingspan between joists, pipe clipped to kingspan, 22mm chipboard panels and laminate floor on top. Be aware that chipboard is a very good insulator! Don't know about ply.
It does heat the floor so your feet don't get cold, but it is certainly not a replacement for a radiator.

Mike
Back to top
 Alert Moderators
Dan_Robinson

from United Kingdom

Joined: 01 Jul 2007
Posts: 28716
Location: Hertfordshire,
United Kingdom
Thanked: 4588 times

PostPosted: Wed Feb 11, 2009 8:40 pm Reply with quote

My living room is nice and toasty thanks...

Your flooring might be too thick though. You will be getting 70W/m. But you don't need as much oomph as you would with a rad.



Try Uponor System12...

Otherwise it all depends on your pipe spacings...
Back to top
 Alert Moderators
MadAlicesDad

from United Kingdom

Joined: 05 Nov 2008
Posts: 144
Location: United Kingdom
Thanked: 1 time

PostPosted: Wed Feb 11, 2009 9:03 pm Reply with quote

Lucky you! Glad your experience is better than mine.
I suspect that the boards are thicker than necessary, but as the main aim was to replace the springy rotten Victorian timbers, strength was more important than conductivity!
At the weekend when it's on full time it's a lot better, but during the week when it's only a couple of hours morning and evening, you barely notice it other than as a foot warmer. That said, even with thinner boards and tighter pipe spacing etc, I still don't see how UFH mounted under* the floorboards can heat the air in a room as quickly as a normal convector radiator when used as an alternative to a radiator for only an hour or two at a time.

* Uponor System12 mounts above the floor boards!

Mike
Back to top
 Alert Moderators
Dan_Robinson

from United Kingdom

Joined: 01 Jul 2007
Posts: 28716
Location: Hertfordshire,
United Kingdom
Thanked: 4588 times

PostPosted: Wed Feb 11, 2009 9:08 pm Reply with quote

I know - I have fitted System12...

My underfloor is on a suspended timer floor with 18mm floorboards, aluminium spreaders and 75mm Kingspan.

You can't expect it to heat the room with only a few hours morning and evening. Underfloor works at low levels for a long time. Mine is on an independent zone with a CM67NG.
Back to top
 Alert Moderators
MadAlicesDad

from United Kingdom

Joined: 05 Nov 2008
Posts: 144
Location: United Kingdom
Thanked: 1 time

PostPosted: Wed Feb 11, 2009 9:26 pm Reply with quote

Dan_Robinson wrote:

You can't expect it to heat the room with only a few hours morning and evening. Underfloor works at low levels for a long time.

I know that now, I just wanted to warn the OP!
Mike
Back to top
 Alert Moderators
wjrc

from United Kingdom

Joined: 27 Nov 2006
Posts: 5
Location: United Kingdom

PostPosted: Thu Feb 12, 2009 9:24 am Reply with quote

Thanks for the replies but I'm still a bit confused.

Is a typical build-up:
insulation between the joists, then board on top, then UFH (wet), then screed, then tiles

MadAlicesDad, does this mean the pipes clip directly onto the insulation between the joists with the chipboard on top? Wouldn't it be bad to have the chipboard - a good insulator between the heat source and the floor?

Quote:
I've just fitted water UFH under a timber floor in the dining room. 75mm kingspan between joists, pipe clipped to kingspan, 22mm chipboard panels and laminate floor on top. Be aware that chipboard is a very good insulator! Don't know about ply.


I think i need to do some more research on the basics - any pointers

Thanks for the help
Back to top
 Alert Moderators
swidders

from United Kingdom

Joined: 19 Jan 2009
Posts: 1410
Location: Manchester,
United Kingdom

PostPosted: Thu Feb 12, 2009 11:14 am Reply with quote

wjrc wrote:
insulation between the joists, then board on top, then UFH (wet), then screed, then tiles



Insulation between joist, set 25mm below top level of joist, UFH clipped to this passing through notches, light sand and cement screed (1 to 8 cement/sand) to act as heat spread, then boards on top.

Research this.
Back to top
 Alert Moderators
MadAlicesDad

from United Kingdom

Joined: 05 Nov 2008
Posts: 144
Location: United Kingdom
Thanked: 1 time

PostPosted: Fri Feb 13, 2009 11:29 pm Reply with quote

wjrc wrote:

Is a typical build-up:
insulation between the joists, then board on top, then UFH (wet), then screed, then tiles

No. in our case it was insulation, screed, boards, laminate
wjrc wrote:

MadAlicesDad, does this mean the pipes clip directly onto the insulation between the joists with the chipboard on top? Wouldn't it be bad to have the chipboard - a good insulator between the heat source and the floor?



Yes and yes. The latter point seems to have been overlooked by the sellers of UFH though!
However, although it's not as good as I'd hoped, I'm glad it's there as it keeps your feet warm on an otherwise cold floor.
Mike
Back to top
 Alert Moderators
njk

from United Kingdom

Joined: 21 Nov 2007
Posts: 46
Location: Hertfordshire,
United Kingdom
Thanked: 10 times

PostPosted: Sat Feb 14, 2009 11:09 am Reply with quote

Hi,

Have a look at this
http://www.uponorhousingsolutions.co.uk/literature/LiteratureDownloads/2_Systems/01%20-%2015mm%20&%2016mm%20Install%20Guide%20-%20Domestic%20Systems.pdf

We have used this system for about 8 years and it works brilliantly.
The system 12 from Uponor is very good, only drawback is it considerably more expensive.

In regards to controls, I always treat UFH as a separate zone, i.e. it's own room stats, programmer and zone valve. As previously stated, it should stay on for much longer and on a lower heat.

Tiling wise, we use 18mm ply, screwed in at every 200mm, ditra mat http://www.schluter.co.uk/matting.aspx ) on top and then tiles.

The only ufh I have come across that didn't work properly is either the house not being properly insulated and the heatloss being to great or the installation not being correct.

Lolli
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Underfloor heating conundrum - return hot and feed cold? 9 160 Wed Nov 02, 2011 9:32 pm
Laying Underfloor heating Pipes 2 60 Wed Oct 19, 2011 8:02 am
Underfloor Heating and Dry Mix Cement + Sand Question 2 20 Mon Oct 17, 2011 2:21 pm
Wet underfloor heating - strange problem 2 60 Sun Nov 06, 2011 4:30 pm
Gas boiler cycling on and off with underfloor heating 6 60 Mon Nov 07, 2011 11:14 am


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.