Terminating SWA in a Consumer Unit


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
elfreddo

from United Kingdom

Joined: 04 Nov 2004
Posts: 28
Location: United Kingdom

PostPosted: Mon Nov 22, 2004 7:19 am Reply with quote

Thoughts Please,
I'm about to install a 20A radial circuit to an supply an extension.
For the ease of installation the feed will come directly from the CU and be run though the garage wall in 2.5mm 3 core swa to a plastic termination box (ip56) on the extension wall. From here the it will be terminated using 2.5 T&E to feed the necessary power outlets inside.
My query is what is the best way to terminate the SWA to take the tails in the CU.
Cheers
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
dw3101

from United Kingdom

Joined: 19 Aug 2004
Posts: 350
Location: Leeds,
United Kingdom
Thanked: 2 times

PostPosted: Mon Nov 22, 2004 10:35 am Reply with quote

You sound like you dont know what you are doing and the cable sizes dont sound correct.

If you are adding an additional consumer unit I would use larger cable circa 10 - 16mm. You can terminate the gland directly into a metal clad consumer unit.

The other end should be terminated into a metal clad switch fuse which you can then run the tails from, or teminate into an adaptable box and then run 10mm T&E or similar to the existing consumer unit.

David
Back to top
 Alert Moderators
elfreddo

from United Kingdom

Joined: 04 Nov 2004
Posts: 28
Location: United Kingdom

PostPosted: Mon Nov 22, 2004 4:10 pm Reply with quote

Let me explain further,
The power for the extension will be supplied from a spare 20A mcb in the existing cu (in the garage) This will then be run in the form of a radial. Because the cable has got to go outside for 5 meters then back into the extension I was going to use SWA instead of 2.5 t&e run in conduit.
Should i terminate the swa in a plastic or metal adapable box and how?
Cheers
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 48268
Location: London,
United Kingdom
Thanked: 1816 times

PostPosted: Mon Nov 22, 2004 4:53 pm Reply with quote

elfreddo wrote:
Should i terminate the swa in a plastic or metal adapable box

Yes, as you'll find it very hard to teminate it directly in the CU, they are usually too crowded. And, if plastic, too flimsy. So use a box - metal is best.

Quote:
and how?

With a SWA gland, of course, just as you would have done if you were terminating it in the CU....
Back to top
 Alert Moderators
Paul_C

from United Kingdom

Joined: 19 Nov 2004
Posts: 2137
Location: United Kingdom
Thanked: 139 times

PostPosted: Mon Nov 22, 2004 6:29 pm Reply with quote

A galvanized or black enamel 3 x 3" adaptable box with 20mm knockouts is ideal for this purpose. You can terminate the SWA with a 20mm gland into the box, then run T&E to it from the panel.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 25246
Location: Cheshire,
United Kingdom
Thanked: 445 times

PostPosted: Mon Nov 22, 2004 7:22 pm Reply with quote

What I do with insulated CU's is as follows:

I terminate the SWA into a galv through box, making sure the tails are plenty long enough to reach the CU terminals required.

Then I fix the through box to the CU: Having drilled a suitable hole, I fix the galv box to the cu with a bush. All that then remains is to wire the conductors up to the CU and run an earth tag to the galv box, not forgetting a lid!

I prefer this method, especially for larger circuits, as you don't have to join T & E to the SWA (another unwanted junction).

Of course, some CU's are not suitable for this method, as you cannot remove the lid once the galv box is fixed.......
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 48268
Location: London,
United Kingdom
Thanked: 1816 times

PostPosted: Mon Nov 22, 2004 8:58 pm Reply with quote

securespark wrote:
Of course, some CU's are not suitable for this method, as you cannot remove the lid once the galv box is fixed.......

Use a bit of conduit instead of a bush?

If you use the flexible stuff you'd have complete freedom regarding the relative positions of box & CU.

Note to anyone reading this thread - this technique is for 3-core SWA, not 2....
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 8560
Location: United Kingdom
Thanked: 228 times

PostPosted: Mon Nov 22, 2004 10:12 pm Reply with quote

also depending on how long this run is you might want to run something a bit bigger than 2.5mm
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
16mm SWA cable terminating at Consumer Unit ? 4 5940 Fri Jan 28, 2005 1:17 pm
Terminating SWA 21 500 Mon Sep 19, 2011 8:08 pm
Terminating an incoming SWA Cable 12 300 Tue Oct 18, 2011 10:09 pm
Terminating a live cable under floorboards 21 460 Tue Nov 13, 2012 1:50 pm
Terminating Cables 18 620 Mon Aug 22, 2011 8:20 am


 