Hi. Help please. Central heating ok but no hot water. On h/w mode the pump runs but can't hear the boiler fan and burner does not light. No fault lights showing just the green light to confirm h/w mode. Water pressure and flow is fine. The pins on the diverter valves pop out ok and as far as I can see the microswitches ok. have tried over riding them by connecting the wires together but this makes no difference. Am I right in assuming that the pcb is faulty? If I take off the temp sensor wires the panel shows them as faulty so I am assuming they are ok
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52863
Location: London,
United Kingdom
Thanked: 3326 times

PostPosted: Tue Feb 24, 2009 1:09 am Reply with quote

On top of the diverter valve there is a smaller pin which operates a switch when there is flow round the system.

You will probably find the pin is not reliably operating the switch in the DHW mode.

Check and to test activate the switch manually.

Tony
Back to top
 Alert Moderators
ChasW1

from United Kingdom

Joined: 23 Feb 2009
Posts: 11
Location: Aberdeenshire,
United Kingdom

PostPosted: Tue Feb 24, 2009 10:08 am Reply with quote

Agile wrote:
On top of the diverter valve there is a smaller pin which operates a switch when there is flow round the system.

You will probably find the pin is not reliably operating the switch in the DHW mode.

Check and to test activate the switch manually.

Tony


Hi. Thanks for suggestion. The pins on both diverters work ok and have tried activating both manually. The one on the top works ok on CH mode and the one on the side works on DHW mode. Have tried manually operating CH mode switch when running DHW only and makes no difference
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52863
Location: London,
United Kingdom
Thanked: 3326 times

PostPosted: Tue Feb 24, 2009 11:10 am Reply with quote

The one on the top is NOT a CH switch!

It is a system flow switch and has to operate in either mode before the boiler is allowed to proceed to ignite the gas.

If the top one really is operating on CH, then I agree that it may be the PCB but it would be better if you first accept what I have advised you and then recheck the system switch before you consider spending about 100 on a new PCB.

Tony
Back to top
 Alert Moderators
ChasW1

from United Kingdom

Joined: 23 Feb 2009
Posts: 11
Location: Aberdeenshire,
United Kingdom

PostPosted: Tue Feb 24, 2009 1:08 pm Reply with quote

Agile wrote:
The one on the top is NOT a CH switch!

It is a system flow switch and has to operate in either mode before the boiler is allowed to proceed to ignite the gas.

If the top one really is operating on CH, then I agree that it may be the PCB but it would be better if you first accept what I have advised you and then recheck the system switch before you consider spending about 100 on a new PCB.

Tony


Hi Tony. Thanks for reply. Have tried a bypass on flow switch when in DHW mode and it has no effect. If I run both DHW & CH with bypass still in place it does not run. However, if I then shut off DHW flow the DHW piston retracts and CH runs. As soon as I reinstate the flow the DHW actuator piston moves out, the microswitch kicks in and it cuts the gas and the fan. As soon as I stop the flow the piston retreats and CH back on. I have also tried a similar bypass on the DHW switch. I assume its not the temp sensor as no fault lights show until I disconnect the actual sensor itself. Diff to check out as don't have a meter.

Charles
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52863
Location: London,
United Kingdom
Thanked: 3326 times

PostPosted: Tue Feb 24, 2009 1:16 pm Reply with quote

I think that your description may be a little confused because talking of just a "flow switch" can mean anything.

Your fault seems to be either the DHW flow switch, the PCB or the DHW sensor is low resistance. Thats last unusual but keeps the gas off because it thinks its hot enough!

You can substitute a 10k resistor for the DHW sensor.

OR

Get a simple test meter! Its not really possibly to fix a boiler without one.

There is also a strong possibility that the DHW flow switch has failed! Its a change over switch and it may not be operating fully!

Tony
Back to top
 Alert Moderators
ChasW1

from United Kingdom

Joined: 23 Feb 2009
Posts: 11
Location: Aberdeenshire,
United Kingdom

PostPosted: Tue Mar 03, 2009 4:46 pm Reply with quote

Agile wrote:
I think that your description may be a little confused because talking of just a "flow switch" can mean anything.

Your fault seems to be either the DHW flow switch, the PCB or the DHW sensor is low resistance. Thats last unusual but keeps the gas off because it thinks its hot enough!

You can substitute a 10k resistor for the DHW sensor.

OR

Get a simple test meter! Its not really possibly to fix a boiler without one.

There is also a strong possibility that the DHW flow switch has failed! Its a change over switch and it may not be operating fully!

Tony


Hi Tony

Thought I would let you know the outcome. I ordered a PCB and DHW sensor. It turned out to be just the sensor. Anyway I decided that I may as well replace the board as I had bought it. So did that today & would you believe that that the boiler would not run!! The first two neons on the display were flashing. So put the old board back in and all was well. Presume so called new board faulty.

Many thanks for your help

Charles
Back to top
 Alert Moderators
namsag

from United Kingdom

Joined: 12 May 2004
Posts: 9909
Location: United Kingdom
Thanked: 321 times

PostPosted: Tue Mar 03, 2009 9:02 pm Reply with quote

When new board fitted you have to hold it at reset position for 3 seconds , sometimes more than once.
Back to top
 Alert Moderators
ChasW1

from United Kingdom

Joined: 23 Feb 2009
Posts: 11
Location: Aberdeenshire,
United Kingdom

PostPosted: Tue Mar 03, 2009 10:33 pm Reply with quote

namsag wrote:
When new board fitted you have to hold it at reset position for 3 seconds , sometimes more than once.


Hi. Thanks for that. I did try a reset but in view of what you advise I will pop the board back in & try again.
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52863
Location: London,
United Kingdom
Thanked: 3326 times

PostPosted: Tue Mar 03, 2009 11:38 pm Reply with quote

Agile wrote:


Get a simple test meter! Its not really possibly to fix a boiler without one.

Tony


A 15 test meter would probably have saved you the cost of the PCB !

Tony
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
hot water problem - Baxi combi 80 eco 5 360 Sat Dec 27, 2008 11:50 am
Baxi combi 105e won't supply hot water to shower? 11 700 Sun Dec 14, 2008 4:43 pm
BAXI 105e combi - hot water/heating problem 11 2700 Tue Sep 18, 2007 9:03 am
combi boiler baxi maxflow? low hot water flow 3 780 Fri Mar 25, 2005 9:13 pm
No hot water coming from tap. Baxi 105e combi 3 560 Sat Jan 09, 2010 12:04 pm


 