Downlights cpc - EIC - Bonding
Reply with quote Thanks

Replacing a consumer unit with 17th edition with 2 RCDs

On Testing R1+R2 on lights, the downlights do not have continuity of cps, the cpc wires have been cut short on each light connection/interconnection. (I get R1+R2 reading in the last room which does not have downlights). The downlight are made of metal have only 2 wires on the block connection supplied running to the 240v lights (I presume these are class II). There are also low voltage IP44 downlights lights in the shower room with cpc interconnection cup off again at transformers. DO I need to reconnect the CPCs?

I have plenty of Electrical Installation certificate.. Can I still use them - there is no room to put the 2nd RCD on it or do I need to get new one. Any recommendation for computer recommended certificate software.

Lastly, There is no need for bonding in the bathroom as all the circuits will be on RCD. I am not sure if, however, I still need to bond the metal work, e.g. radiator, hot and cold water pipes; even thought these do not need to be bonded to the electric circuit in the bathroom. Somewhat, I get confused by what I have read.


Thanks
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
baldelectrician

from United Kingdom

Joined: 27 Jul 2005
Posts: 479
Location: Ayrshire,
United Kingdom
Thanked: 3 times

PostPosted: Sun Apr 05, 2009 5:53 pm    Post Subject:
Reply with quote Thanks

You should have an earth at every lighting point. Whether the earth connects to the light or stays in a choc box is a side issue. All items require an earth at the outlet. The cable requires earth continuity also
[/img]
Back to top
 Alert Moderators
scarypants

from United Kingdom

Joined: 26 Mar 2009
Posts: 174
Location: Yorkshire,
United Kingdom
Thanked: 0 times

PostPosted: Sun Apr 05, 2009 5:59 pm    Post Subject:
Reply with quote Thanks

The manufactures instructruction regarding downlights normally state no cpc needed, as they are double insulated plus as they will be in a chain should not effect another lighting circuit. . I always do connect the cpcs up in connection blocks though.
I have plenty of Electrical Installation certificate.. Can I still use them - there is no room to put the 2nd RCD on it or do I need to get new one. Any recommendation for computer recommended certificate software.
You continue on another sheet and page number it.
Is there any electrical circuits in the bathroom to sup bond?
SPS
Back to top
 Alert Moderators
GaryMo

from United Kingdom

Joined: 03 Jul 2007
Posts: 2751
Location: Manchester,
United Kingdom
Thanked: 17 times

PostPosted: Sun Apr 05, 2009 6:04 pm    Post Subject:
Reply with quote Thanks

scarypants wrote:
The manufactures instructruction regarding downlights normally state no cpc needed, as they are double insulated plus as they will be in a chain should not effect another lighting circuit.


No CPC required to the luminaire but 411.3.1.1 still applies.
For me this would have been a code 2 defect on the PIR that I would have carried out prior to changing the consumer unit.
Back to top
 Alert Moderators
scarypants

from United Kingdom

Joined: 26 Mar 2009
Posts: 174
Location: Yorkshire,
United Kingdom
Thanked: 0 times

PostPosted: Sun Apr 05, 2009 6:15 pm    Post Subject:
Reply with quote Thanks

GaryMO
Would this not come under a deviation from BS7671 as Manufacturers Instruction have revelant approved standards
SPS
Back to top
 Alert Moderators
GaryMo

from United Kingdom

Joined: 03 Jul 2007
Posts: 2751
Location: Manchester,
United Kingdom
Thanked: 17 times

PostPosted: Sun Apr 05, 2009 6:22 pm    Post Subject:
Reply with quote Thanks

scarypants wrote:
GaryMO
Would this not come under a deviation from BS7671 as Manufacturers Instruction have revelant approved standards
SPS


I wouldn't have said so. The MI will state something along the lines of class 2 or all insulated so a CPC isn't required to be connected to the luminaire. This doesn't mean that BS7671 shouldn't be followed with regards to the cables supplying the luminaries.
You may even measure voltage on the unconnected CPC's due to capacitive coupling.

If the luminaries had been supplied as a kit with 2 core cable minus a CPC then it's a totally different story.
Back to top
 Alert Moderators
Joe100w

from United Kingdom

Joined: 04 Apr 2009
Posts: 30
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Apr 05, 2009 6:32 pm    Post Subject:
Reply with quote Thanks

I would reconnect the cpc continuity on the downlights.

Any Views on that bonding issue for the bathroom . Does metalwork still require bonding.

PIR means ....?

All help has been very much appreciated icon_biggrin.gif icon_biggrin.gif
Back to top
 Alert Moderators
scarypants

from United Kingdom

Joined: 26 Mar 2009
Posts: 174
Location: Yorkshire,
United Kingdom
Thanked: 0 times

PostPosted: Sun Apr 05, 2009 6:37 pm    Post Subject:
Reply with quote Thanks

GaryMo,
If the luminaries had been supplied as a kit with 2 core cable minus a CPC then it's a totally different story.
What if they had not been supplied by 2 core but had no earth terminal connection? because that's what I was assuming by the original post, I know it's wrong to assume but there you go!
SPS[/quote]
Back to top
 Alert Moderators
scarypants

from United Kingdom

Joined: 26 Mar 2009
Posts: 174
Location: Yorkshire,
United Kingdom
Thanked: 0 times

PostPosted: Sun Apr 05, 2009 6:42 pm    Post Subject:
Reply with quote Thanks

joe100w
read regulation 701.415.2 that will explain it to you?
SPS
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Sun Apr 05, 2009 7:39 pm    Post Subject:
Reply with quote Thanks

No, not really.

Infact, it has nothing to do with this situation at all.

__________________
I downlights
Back to top
 Alert Moderators
scarypants

from United Kingdom

Joined: 26 Mar 2009
Posts: 174
Location: Yorkshire,
United Kingdom
Thanked: 0 times

PostPosted: Sun Apr 05, 2009 8:03 pm    Post Subject:
Reply with quote Thanks

Joes100w question about bonding bathrooms!
I think so!
Back to top
 Alert Moderators
Joe100w

from United Kingdom

Joined: 04 Apr 2009
Posts: 30
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Apr 05, 2009 8:05 pm    Post Subject:
Reply with quote Thanks

scarypants

you are right. The lights came with 2 core connections. Hence the cpc cannot be connected to the light. I was thinking more about the continuation to cpc within the downlights circuits.

This has more to do with if the lights were changed one day. Also the book Snag1 - it appears any unsused wires/cables need to be connected to earth/cpc instead of just being cut off - as good practice.


reread 701.415.2 and reference to regulation 411.3.1.2 where all the main bonding are present.

I take it that No bonding at all is required in this case. In case I am wrong do let me know
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Sun Apr 05, 2009 8:09 pm    Post Subject:
Reply with quote Thanks

scarypants wrote:
Joes100w question about bonding bathrooms!
I think so!


Sorry, I only saw the post above yours about the missing CPC.

I apologise icon_redface.gif

__________________
I downlights


Last edited by RF Lighting on Sun Apr 05, 2009 8:11 pm, edited 1 time in total
Back to top
 Alert Moderators
scarypants

from United Kingdom

Joined: 26 Mar 2009
Posts: 174
Location: Yorkshire,
United Kingdom
Thanked: 0 times

PostPosted: Sun Apr 05, 2009 8:11 pm    Post Subject:
Reply with quote Thanks

Joe100w
Thats why I connect the CPCs up as mentioned previously,
If all case be true, no bonding is need.
SPS
Back to top
 Alert Moderators
scarypants

from United Kingdom

Joined: 26 Mar 2009
Posts: 174
Location: Yorkshire,
United Kingdom
Thanked: 0 times

PostPosted: Sun Apr 05, 2009 8:12 pm    Post Subject:
Reply with quote Thanks

R F Liighting, I thought so no worries>
SPS
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Wiring downlights from existing ceiling rose 5 1200 Tue Apr 15, 2008 9:29 am
GU10 Downlights earth connection 5 360 Fri Apr 11, 2008 6:40 pm
Installing downlights...need a bit of help!! 15 920 Tue Apr 29, 2008 10:37 am
downlights 4 260 Mon May 05, 2008 6:06 pm
Kitchen downlights question 2 260 Sun May 11, 2008 9:11 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.