rwb2 programmer w/ mid position?


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
  View previous topic :: View next topic  
Author Message
drbenway

from United Kingdom

Joined: 28 Apr 2009
Posts: 11
Location: Yorkshire,
United Kingdom
Thanked: 0 times

PostPosted: Fri Jun 26, 2009 6:59 pm    Post Subject:
rwb2 programmer w/ mid position?
Reply with quote Thanks

Greetings

help much appreciated

edited-- sorry for new long post

I bought a new [white] siemens rwb2e to replace an existing landis gyr rwb2

we have a pumped /gravity[?] fed ch/hw system, gas boiler, room stat, cylinder thermostat. the system also has an immersion heater in the cylinder

edit; in the photo below I now realise there is a valve.



edit*

I've read further and wanted to add some info.

what has been confusing me is;

there are 2 flats with identical heating/hw systems

one flat has the original landis gyr programmer. it has a wire on "1" in the programmer

the other flat has had a new siemens rwb2 installed some time ago. but the wire on "1" in the programmer has been removed. a hand written note is also taped to the switch for the immersion heater, saying "do not use". I now think this may be a red herring which prompted my original question.


So now my question becomes,

is this a mid position system, so the programmer should be on 16 not 10?

why would someone remove the "1" wire? how would this effect operation?


any help much appreciated

thanks very much
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Llan1observer

from United Kingdom

Joined: 10 Nov 2008
Posts: 49
Location: United Kingdom
Thanked: 0 times

PostPosted: Sat Jun 27, 2009 9:43 am    Post Subject:
Reply with quote Thanks

the 10 programme position is normally
used when the hot water is on a gravity system. In this
case it is not possible to have CH without HW

The 16 programme position is normally used on a fully
pumped system using 2 or 3 port valves, thus allowing
independent control of HW and CH.

if the pic is of your system it looks like a fully pumped system

No1 is used to bypass cylinder stat when satisfied to continue controling pump & boiler
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 3169
Location: Sussex,
United Kingdom
Thanked: 71 times

PostPosted: Sat Jun 27, 2009 9:57 am    Post Subject:
Reply with quote Thanks

The valve in the picture could be either a diverter or a mid-position; you can't tell from the photo. The diverter allows water to enter from the pump and then exit to one side or the other; the mid position also allows the water to exit from both sides at the same time.

It could be that you have a diverter valve, which does not need a wire connected to terminal 1 of the RWB2. The mid position valve does need the connection.
Back to top
 Alert Moderators
drbenway

from United Kingdom

Joined: 28 Apr 2009
Posts: 11
Location: Yorkshire,
United Kingdom
Thanked: 0 times

PostPosted: Sat Jun 27, 2009 2:30 pm    Post Subject:
Reply with quote Thanks

thanks all for the replies

I'll be taking a look at this again tomorrow, and will report back with more info

thanks
Back to top
 Alert Moderators
drbenway

from United Kingdom

Joined: 28 Apr 2009
Posts: 11
Location: Yorkshire,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jun 28, 2009 5:48 pm    Post Subject:
Reply with quote Thanks

the valves in both flats are honeywell v4073a1039 sundial Y plan diverter valves.

However the new siemens programmer [installed by a plumber] was set on 16, not 10, which explains some of the confusion/issues. [this is in the flat that had the 1 wire removed]

I've installed the other new siemens [set on 10] now in the second flat, and its working fine.

Ill now go ahead and install them in all the other flats

Just a note-- wickes had the siemens on clearance at a tenner a pop, and the digital siemens programmer [wickes H09? iircc] also

thanks for all the help.
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Sun Jun 28, 2009 5:58 pm    Post Subject:
Reply with quote Thanks

I noticed my local Wickes is doing something similar - looks like a bargain
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 3169
Location: Sussex,
United Kingdom
Thanked: 71 times

PostPosted: Mon Jun 29, 2009 9:31 am    Post Subject:
Reply with quote Thanks

drbenway wrote:
the valves in both flats are honeywell v4073a1039 sundial Y plan diverter valves.

One query resolved. icon_wink.gif

Quote:
However the new siemens programmer (installed by a plumber) was set on 16, not 10, which explains some of the confusion/issues. (this is in the flat that had the 1 wire removed).

That raises a new problem. icon_eek.gif

The difference between the 10 and 16 position is that when in the 10 position you cannot have the central heating on without having the HW on. This is relevant when you have pumped heating and gravity hot water.

But you have a fully pumped Y Plan system, which means you can have independent control over Hot Water and Central Heating. For this you have to set the switch to the 16 position, not the 10.

Which brings me to the disconnected wire in terminal 1. The other end of this wire should connect to a terminal which has the grey wire from the valve and a wire from the cylinder thermostat "satisfied" terminal. This is required so the valve can move to the CH only position. At the moment the valve can only be in the HW only position or mid position (HW and CH).

One reason for the strange wiring could be that the valve is faulty (one internal switch broken so the valve cannot move to the CH only position) and the plumber has deliberately hobbled the system so only HW or HW and CH are available.
Back to top
 Alert Moderators
drbenway

from United Kingdom

Joined: 28 Apr 2009
Posts: 11
Location: Yorkshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon Jun 29, 2009 1:30 pm    Post Subject:
Reply with quote Thanks

thanks for the reply

Im not exactly sure what I have! icon_confused.gif

there are 2 water tanks, one small, one large, for each flat. one gravity feeding the hot water,

as expected , the flat with the "one" wire cut, ch doesnt work on the "16" setting, unless you move both hw and ch manually.

on the other flat with the one wire intact, that doesnt work on the 16 either!?

the old programmers [installed circa 1985] , and all rwb2s, were all set on 10, although I couldnt obviously see a way to set them to 16. edit-- I now see the white plastic clip arrangement on the back for the 10/16]

Ill check on that wiring info and report back.

thanks again
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 3169
Location: Sussex,
United Kingdom
Thanked: 71 times

PostPosted: Mon Jun 29, 2009 1:56 pm    Post Subject:
Reply with quote Thanks

drbenway wrote:
Im not exactly sure what I have!
There are 2 water tanks, one small, one large, for each flat. one gravity feeding the hot water,

You are not the only one to be confused.

Gravity HW does not refer to how the water gets to the tap, but how the water in the HW tank is heated. "Gravity heating" depends on the fact that hot water is lighter than cold (lower density to be scientific) so the hot water will rise naturally from the boiler to the HW cylinder, pass through the coil transferring the heat to the water in the cylinder, and then return back to the boiler at a heavier density.

In your case the water leaves the boiler going through the pump and then divides at the valve. One path to the radiators and the other path to the coil in the cylinder. This is fully pumped.

Can you confirm that you have a cylinder thermostat about a thid way up the side of the cylinder. Looks something like this:

Login to view this image
Back to top
 Alert Moderators
drbenway

from United Kingdom

Joined: 28 Apr 2009
Posts: 11
Location: Yorkshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon Jun 29, 2009 7:32 pm    Post Subject:
Reply with quote Thanks

thanks for the reply/info

shouldnt it be called anti-gravity then, as the hot water goes up icon_smile.gif

sorry-- I havent been doing a good job of describing this.

yes it does have a cylinder thermostat.

tomorrow, I'll do a digram of whats there, and see if that helps solve it

but basically, all the flats have been running on a 10 config programmer since new, 25 years ago.

and the CH doesnt work with it in 16 config.

thanks again
Back to top
 Alert Moderators
drbenway

from United Kingdom

Joined: 28 Apr 2009
Posts: 11
Location: Yorkshire,
United Kingdom
Thanked: 0 times

PostPosted: Wed Jul 01, 2009 7:24 am    Post Subject:
Reply with quote Thanks

this is the one with the 1 wire cut [you can see it in the botton lh corner]



and heres the plumbing.



thanks again.
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 3169
Location: Sussex,
United Kingdom
Thanked: 71 times

PostPosted: Wed Jul 01, 2009 10:58 am    Post Subject:
Reply with quote Thanks

drbenway wrote:
this is the one with the 1 wire cut (you can see it in the botton lh corner)

Do you mean the one I have marked?



If so, that's not a wire, it's a cable. How many cores (coloured wires) does it have?

This cable may have nothing to do with your central heating

Are any of the cores connected within the junction box - it's difficult to see?

Where does the other end go to?

How many cores does the cable to the cylinder thermostat have and how are they connected.

Unfortunately the original installer has only used a 7 terminal block - an 8-10 terminal block is usually used - so it is impossible to see if it has been wired correctly for a Y plan, which is what you should have.

I can tell you how to rewire the junction box. But first you will have to tell me what each wire of every cable connects at the other end. You will need a 10 terminal strip, or better still a wiring centre (cost about £10).

Also, can you let me know which boiler (make and exact model) you have?
Back to top
 Alert Moderators
drbenway

from United Kingdom

Joined: 28 Apr 2009
Posts: 11
Location: Yorkshire,
United Kingdom
Thanked: 0 times

PostPosted: Thu Jul 02, 2009 8:18 am    Post Subject:
Reply with quote Thanks

thanks very much for the reply/help

the wire/cable in question has just one [red] wire in it. the other end is connected to the 1 terminal on the programmer

[the programmer is right next to the junction/spaghetti box so its easy to see all this].

so, if I understand this correctly, the plumbing is there for a fully pumped system, but the wiring is not/has never been connected correctly. so it wont function on the 16 programme.

thats a real head shaker, as its been like this from new !

my best guess is that when the [new] plumber replaced the programmer, he recognised the "16 position"/pumped plumbing,

he then installed a new junction box [as you suggest] but just did this with it. [which even I can tell does nothing...]



he then left the programmer on 16 position, which obviously didnt work the CH-- unless you manually moved both sliders


anyhoo...

thanks very much for the offer of further help-- it is greatly appreciated, but as we are doing a total rehab of all the flats next year, Im just going to leave them working in the 10 postion for now and deal with it all then.

once again, many thanks
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 3169
Location: Sussex,
United Kingdom
Thanked: 71 times

PostPosted: Thu Jul 02, 2009 8:58 am    Post Subject:
Reply with quote Thanks

drbenway wrote:
the wire/cable in question has just one (red) wire in it. the other end is connected to the 1 terminal on the programmer. (the programmer is right next to the junction/spaghetti box so its easy to see all this.)

Understood. It just looks lime a grey cable which disappears into the wall. I cant see a grey cable going into the programmer; it must be hidden behind the two white ones.

Quote:
if I understand this correctly, the plumbing is there for a fully pumped system, but the wiring is not/has never been connected correctly. so it wont function on the 16 programme.

Correct. There is normally a wire between timer terminal one and the grey valve wire. Why it is not connected is the mystery.

Quote:
he then installed a new junction box (as you suggest) but just did this with it. (which even I can tell does nothing...)



Is the black cable entering at the bottom coming from the motorized valve? If so, that junction box is just a way of extending the black cable up to the other junction box.

Quote:
we are doing a total rehab of all the flats next year, Im just going to leave them working in the 10 position for now and deal with it all then.

It's not difficult to put it right - may take about 30 mins, but I understand the reason for your wanting to delay. Come back, preferably to this topic, when you want to proceed.
Back to top
 Alert Moderators
drbenway

from United Kingdom

Joined: 28 Apr 2009
Posts: 11
Location: Yorkshire,
United Kingdom
Thanked: 0 times

PostPosted: Thu Jul 02, 2009 10:15 am    Post Subject:
Reply with quote Thanks

thanks again

the black wire does indeed come from the valve, but it is [more than] long enough to reach the old [white] junction box. the new [grey] junction box was added recently.

perhaps the [new] plumber thought about rewiring it correctly [when he was changing the programmer], and then changed his mind? who knows!?

your help has been very much appreciated
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Replace RWB2 Programmer with Select 207XL - No Boiler FireUp 2 500 Sat Oct 18, 2008 5:05 pm
Help with landis & gyr RWB2 mechanical programmer 2 5040 Sat Jan 20, 2007 12:56 pm
How Can I Verify My Landis & Gyr RWB2 Programmer Is Faul 2 600 Tue May 27, 2008 10:26 am
Replacing rwb2 with rwb29 8 300 Mon Sep 14, 2009 7:41 pm
Hot water / programmer problem-New mid position valve fitted 9 260 Mon Jan 05, 2009 11:30 pm