IT radial circuit


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
garlicbread

from United Kingdom

Joined: 24 Jun 2008
Posts: 16
Location: Manchester,
United Kingdom
Thanked: 0 times

PostPosted: Sat Jul 04, 2009 12:22 pm    Post Subject:
IT radial circuit
Reply with quote Thanks

can anyone tell me with regards to a radial circuit which will have IT equipment on it, what do you do with the last socket regarding the cpc, obviously on a ring all sockets will have 2 separate cpc's to terminate in separate earting terminals, but what about the last socket on a radial. Is it just a case of linking them.
also im struggling to find out the correct procedure when it comes to earthing galv steel back boxes. if there is a fixed lug on the back box, is a link between socket and back box not required? Struggling to find anything in the regs
cheers
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4538
Location: United Kingdom
Thanked: 10 times

PostPosted: Sat Jul 04, 2009 12:31 pm    Post Subject:
Reply with quote Thanks

Quote:
but what about the last socket on a radial. Is it just a case of linking them.


Just to clarify, you are not talking about 2no. radial circuits are you?... just the one? (before someone comes in, skim reads the post and goes off down the wrong track!)

Recessed boxes in the wall do not require an earth flylead to the front plate as long as they have at least one fixed lug (this does not work the other way... a front plate cannot be earthed by screws from an earthed box)
Back to top
 Alert Moderators
garlicbread

from United Kingdom

Joined: 24 Jun 2008
Posts: 16
Location: Manchester,
United Kingdom
Thanked: 0 times

PostPosted: Sat Jul 04, 2009 12:33 pm    Post Subject:
Reply with quote Thanks

yeah just 1 No radial
Back to top
 Alert Moderators
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4538
Location: United Kingdom
Thanked: 10 times

PostPosted: Sat Jul 04, 2009 12:53 pm    Post Subject:
Reply with quote Thanks

In that case, you'll need a separate earth wire from the DB (minimum size 4mm˛), if its a circuit for something like a data cabinet, take the 4mm˛ earth through the FCU, but dont terminate it there, have it come out and follow the flex to the cabinet and have it bolted to an ECP on the equipment. If its for a socket outlet circuit, then take it to the last socket so that the cpc is effectivly a ring, and do as you would on a ring; use separate terminals
Back to top
 Alert Moderators
garlicbread

from United Kingdom

Joined: 24 Jun 2008
Posts: 16
Location: Manchester,
United Kingdom
Thanked: 0 times

PostPosted: Sat Jul 04, 2009 12:55 pm    Post Subject:
Reply with quote Thanks

cheers thanks for the info
Back to top
 Alert Moderators
Chri5

from United Kingdom

Joined: 19 Jan 2007
Posts: 1827
Location: London,
United Kingdom
Thanked: 28 times

PostPosted: Sat Jul 04, 2009 12:56 pm    Post Subject:
Reply with quote Thanks

Standard radial without high integrity earthing (seperate CPC in addition to the one in TE).

Last socket will just have the 1 x CPC, the sockets may have 2 x earth terminals but they WILL link via metalwork manufactured in to the socket.

Good practice is to have a earth 'strapper' cable between the metal back box earth terminal and the socket in ADDITION to the earth that connects via the box -> fixed lug -> screw.

It's a better earthing method and although unlikely, the screw making the earth could become loose, rust, break or be changed for a nylon screw.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
radial circuit 8 400 Thu Feb 16, 2006 4:03 pm
cooker point to radial circuit 3 680 Sun Feb 12, 2006 8:22 pm
Junction boxes on cooker radial circuit 3 3160 Mon Feb 27, 2006 10:29 pm
Ring & Radial circuit regs 6 960 Wed Mar 22, 2006 11:36 pm
Testing of radial circuit,which feed an ring final circuit 21 1100 Tue May 20, 2008 11:13 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.