metal shed


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
garlicbread

from United Kingdom

Joined: 24 Jun 2008
Posts: 16
Location: Manchester,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jul 05, 2009 10:58 am    Post Subject:
metal shed
Reply with quote Thanks

house is on a tn-s system, what is the best way to go, regarding earthing arrangmetns for the shed, can the shed be earthed through the armoured cable supplying power to the shed via the consumer unit in the house or does it have to be locally earthed using a rod.
shed is 10m from house
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Sun Jul 05, 2009 12:30 pm    Post Subject:
Reply with quote Thanks

Is the shed an extraneous conductive part?

__________________
I downlights
Back to top
 Alert Moderators
ColJack

from United Kingdom

Joined: 16 Feb 2007
Posts: 7599
Location: West Midlands,
United Kingdom
Thanked: 129 times

PostPosted: Sun Jul 05, 2009 2:40 pm    Post Subject:
Reply with quote Thanks

given the title of "metal shed" then I recon it is..

__________________
If you make everything idiot proof, evolution will just make a better idiot.
Back to top
 Alert Moderators
garlicbread

from United Kingdom

Joined: 24 Jun 2008
Posts: 16
Location: Manchester,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jul 05, 2009 2:58 pm    Post Subject:
Reply with quote Thanks

so should it have a separate 10mm2 earth to the shed, would having the shed on a TT system cause problems?
Back to top
 Alert Moderators
ericmark

from United Kingdom

Joined: 27 Jan 2008
Posts: 2085
Location: Flintshire,
United Kingdom
Thanked: 48 times

PostPosted: Sun Jul 05, 2009 3:07 pm    Post Subject:
Reply with quote Thanks

I would say it's position in relationship to houses would decide the best option. Where a group of houses have gardens totally surrounded by them then a shed in that garden would be better earthed using the TN-C-S supply in order any item powered from shed or house have the same earth.

However where the shed is at the end of a garden backed onto with open fields then a TT supply may be more appropriate.

However this would be worked out by whoever was signing the "Installation Certificate" as the designer of the system who would be likely same person who would issue the LABC completion certificate and is not really a DIY job.

See here Electrical installations outdoors: a supply to a detached outbuilding for more info.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Wiring in a Metal shed 12 400 Tue Jun 30, 2009 6:48 pm
metal shed supply...earthing? 10 600 Sun May 11, 2008 10:00 am
What glands to connect conduit to metal clad socket/switch? 16 780 Sat Apr 12, 2008 5:34 pm
Metal Lampost TNCS 4 240 Sun May 18, 2008 4:15 pm
Metal ceiling rose 9 340 Sun Apr 06, 2008 5:30 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.