I generally test RCBOS at the DB rather than at the end of the circuit, but came across something weird today RCBOs failed when I tested them at the board (even with the circuit connected), but worked fine when I tested them from a point on the circuit.
Completely threw me, it doesn't make sense to me, anyone? |
|
ColJack

Joined: 16 Feb 2007 Posts: 7599 Location: West Midlands, United Kingdom Thanked: 129 times
|
Posted: Wed Sep 02, 2009 7:04 pm Post Subject: |
 |
|
these the MEM ones with the "pod" on them?
the rcd works by a non contact CT round the live wire.. ( as I just explained in another thread ) , so testing at what is in effect the breaker screw will miss out the CT "tube".. __________________ If you make everything idiot proof, evolution will just make a better idiot. |
|
JohnD

Joined: 15 Nov 2005 Posts: 24037 Location: Hampshire, United Kingdom Thanked: 54 times
|
Posted: Wed Sep 02, 2009 7:48 pm Post Subject: |
 |
|
what's "CT"? |
|
ColJack

Joined: 16 Feb 2007 Posts: 7599 Location: West Midlands, United Kingdom Thanked: 129 times
|
Posted: Wed Sep 02, 2009 7:53 pm Post Subject: |
 |
|
sorry, CT is Current Transformer.. ( I think.. )
coils that you put around a wire..
a voltage is induced in the coil relative to the current flowing through the wire.. __________________ If you make everything idiot proof, evolution will just make a better idiot. |
|
Lectrician

Joined: 18 Jul 2004 Posts: 5167 Location: Devon, United Kingdom Thanked: 20 times
|
Posted: Wed Sep 02, 2009 7:54 pm Post Subject: |
 |
|
Current transformer.
This is well known with the MEM RCBO's (even the MCH and ALB off the shelf range rather than field fit pods). |
|