Outside Cable
Reply with quote Thanks

I am running some armoured cable to some garden lights. Is there any rules as to how deep they need to be under the grass and if they need to be protected. This cable will run off an RCD.

Also will need to split the cable to supply different light to different areas - how best to do that.

Thanks
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
ericmark

from United Kingdom

Joined: 27 Jan 2008
Posts: 2085
Location: Flintshire,
United Kingdom
Thanked: 48 times

PostPosted: Fri Sep 25, 2009 7:13 am    Post Subject:
Reply with quote Thanks

522.8.10 Except where installed in a conduit or duct which provides equivalent protection against mechanical damage, a cable buried in the ground shall incorporate an earthed armour or metal sheath or both, suitable for use as a protective conductor. The location of buried cables shall be marked by cable covers or a suitable marking tape. Buried conduits and ducts shall be suitably identified. Buried cables, conduits and ducts shall be at a sufficient depth to avoid being damaged by any reasonably foreseeable disturbance of the ground.

I would consider 18 inches would comply but the regs don't give a distance.

As to joints there are scotch cast joints able to joint cables below ground but the norm would be to daisy chain and join above ground. Unless libel to flooding an IP44 box is normally good enough above ground with drain which would include the base of a lamp standard.

If you are likely to be flooded then IP68 will be required.

If the garden is attached to domestic premises be aware that Part P will need satisfying.
Back to top
 Alert Moderators
stargazer

from United Kingdom

Joined: 03 Feb 2008
Posts: 361
Location: Hertfordshire,
United Kingdom
Thanked: 3 times

PostPosted: Fri Sep 25, 2009 7:41 am    Post Subject:
Re: Outside Cable
Reply with quote Thanks

Joe100w wrote:

Also will need to split the cable to supply different light to different areas - how best to do that.


I like these


__________________
Some cause happiness wherever they go; others, whenever they go...
Back to top
 Alert Moderators
Joe100w

from United Kingdom

Joined: 04 Apr 2009
Posts: 30
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Sep 25, 2009 5:58 pm    Post Subject:
Reply with quote Thanks

stargazer

What are the red connectors in the connection box. I am not familiar with them. Thanks
Back to top
 Alert Moderators
properleckie

from United Kingdom

Joined: 21 Sep 2009
Posts: 61
Location: Kent,
United Kingdom
Thanked: 9 times

PostPosted: Fri Sep 25, 2009 6:15 pm    Post Subject:
Reply with quote Thanks

the red items are insulating sleeves over the 'line-tap' connectors which can be purchased with the 'pratley' underground joint box shown.
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Fri Sep 25, 2009 7:16 pm    Post Subject:
Reply with quote Thanks

I personally don't rate pratley boxes at all....

__________________
I downlights
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Fri Sep 25, 2009 8:16 pm    Post Subject:
Reply with quote Thanks

Why not?

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Lectrician

from United Kingdom

Joined: 18 Jul 2004
Posts: 5167
Location: Devon,
United Kingdom
Thanked: 20 times

PostPosted: Fri Sep 25, 2009 8:32 pm    Post Subject:
Reply with quote Thanks

Nor me.

If you are going to joint a cable underground, it is likely to be permenant. Wht use a dismountable enclosure?

Just resing joint it - FAR cheaper, and FAR more reliable.

I have never used the pratley boxes, but they bug me. Nothing is water tight under ground. (except a well done resin joint).

Smaller SWA is not that expensive these days, and looping even some distance is not likely to cause that much extra expense, especially when you consider jointing.

Looping also gives you the chance to fault find easily in the future some years down the line.

Preferably you would use lights which accept the looping of SWA, these are unfortunately usually very expensive. The next best thing is a light which has the space to include a GALV trouser box in it's column/enclosure. If you cannot achieve this, a joint at each light is required. An IP rated plastic gewiss type box is good if you can hide it in shrubbery, or dont mind seeing it, otherwise a UG joint, preffereably resin, is needed at each light.
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Fri Sep 25, 2009 9:44 pm    Post Subject:
Reply with quote Thanks

I went to a job where pratley boxes had been used underground. They were all full of water.

Resin joints are the ONLY joints which actually work underground.

Above ground there is no need for a pratley box. A galv conduit box is fine, and they are cheaper and look neater.

__________________
I downlights
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Fri Sep 25, 2009 11:01 pm    Post Subject:
Reply with quote Thanks

Were they the underground type, or the overground ones that stargazer linked to?

If the ones that the makers say are suitable for burial aren't, how come they are on sale? How come nobody selling them gets prosecuted? Why does a company like Pratley, scarcely a newcomer to the market, say that their products are suitable for continuous immersion down to 2m if they are not?

They also sell JBs which they claim are certified for use in explosive atmospheres - is that a lie too? The consequences of that could be catastrophic.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Joe100w

from United Kingdom

Joined: 04 Apr 2009
Posts: 30
Location: United Kingdom
Thanked: 0 times

PostPosted: Sat Sep 26, 2009 9:27 am    Post Subject:
Reply with quote Thanks

Lectrician
What is the resin joint and where can I find more information about the different joints that can be made - nowadays.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Sat Sep 26, 2009 11:23 am    Post Subject:
Reply with quote Thanks




Other brands and other suppliers are available.


__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
ColJack

from United Kingdom

Joined: 16 Feb 2007
Posts: 7599
Location: West Midlands,
United Kingdom
Thanked: 129 times

PostPosted: Sat Sep 26, 2009 3:47 pm    Post Subject:
Reply with quote Thanks

alternatively, you can get some waterproofing "gel" that you can pour into the above boxes ( or the underground ones ) to make double sure they are watertight...

the joint shown is a straight connection.. for lights you would need a joint for 3 cables.. which TLC don't carry by the looks..

__________________
If you make everything idiot proof, evolution will just make a better idiot.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Advice on cable size to supply a caravan. 3 400 Tue Jan 22, 2008 12:33 am
Massive cable under first floor floor board 26 1440 Mon Jan 21, 2008 1:55 pm
Cable Rating to Supply a Hob and an Oven / Microwave 6 620 Fri Jan 18, 2008 6:23 pm
MAINS CABLE 50mm conection ITS HUGE HOW DO I CONNECT IT 7 720 Fri Jan 18, 2008 1:11 pm
cooker cable 10mm 12 960 Tue Jan 22, 2008 3:20 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.