Ideal Icos knocking - low water pressure?

Goto page 1, 2, 3  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
pjblink

from United Kingdom

Joined: 16 Aug 2009
Posts: 26
Location: West Midlands,
United Kingdom

PostPosted: Wed Sep 30, 2009 10:00 pm Reply with quote

Hey guys,

I've recently moved into a coach house (all on one floor), and we immediately are having trouble with the central heating. Some of the radiators were heating up well and proper, but others weren't. I switched off the ones that were heating up, and the others did indeed heat up.

We've only been in a few days, and the boiler is knocking shortly after lighting up. A video is uplolading, i'll post soon...

Now to my very basic knowledge, this seems to point towards low pressure in the system? I am trying, but can't for the life of me find a pressure gauge. I've taken the front off the boiler, been up in the loft etc, all around the tank - but can't find one. Nor can i seem to find a loop to re-pressurise the system. Under the sink is a large mix up of wires and tubes from the washing machine, i havn't yet decoded these.

The other issue i have is that the central heating (havn't set the water to heat up yet) seems to also be heating up the water. I set the tank thermostat at 50C and the water is getting well above that. The motorised valve (3 way - Danfoss) doesn't seem to have any "spring" in it. When i moved in, it was set at manual. I can switch it to auto, but there is nothing to pull it in that direction... It also seems to be fitted upside down, on the side of the unit it points down "A - Heating" and up "B - Hot Water". On the piping it's fitted to, A is up into the ceiling, and B is down, into the tank.

The only other thing is that there is a pipe going up, with a white knurled knob on the end. When i undo this, i can read a gauge of bar readings, 0.6,0.5,0.4 etc. What is this for?

Any thoughts on helping us?

Cheers, Patrick
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 23673
Location: Georgia,
United States of America
Thanked: 918 times

PostPosted: Wed Sep 30, 2009 10:07 pm Reply with quote

Quote:
The only other thing is that there is a pipe going up, with a white knurled knob on the end. When i undo this, i can read a gauge of bar readings, 0.6,0.5,0.4 etc. What is this for?


auto bypass valve icon_wink.gif



Login to view this image

fill loop icon_wink.gif


Last edited by kevplumb on Wed Sep 30, 2009 10:10 pm, edited 1 time in total
Back to top
 Alert Moderators
davebgas

from United Kingdom

Joined: 09 Feb 2009
Posts: 2043
Location: London,
United Kingdom
Thanked: 254 times

PostPosted: Wed Sep 30, 2009 10:08 pm Reply with quote

Tank In loft = open system and not pressurised. Hence no gauge. Check system has water in it and the pump speed is on full.
3port valve set up is A to rads, B to cylinder. But should be set to auto as manual is used for filling and draining.
Just to clarify though, this is an ICOS? And you definately have tanks in the loft with a ballcock? Only ask as there are 2 variatants of the Icos, a system or heat only.
Back to top
 Alert Moderators
kevindgas

from United Kingdom

Joined: 28 Mar 2006
Posts: 5690
Location: Southampton,
United Kingdom
Thanked: 467 times

PostPosted: Wed Sep 30, 2009 10:32 pm Reply with quote

davebgas wrote:

Just to clarify though, this is an ICOS? And you definately have tanks in the loft with a ballcock? Only ask as there are 2 variatants of the Icos, a system or heat only.

and they are both s****!
Back to top
 Alert Moderators
pjblink

from United Kingdom

Joined: 16 Aug 2009
Posts: 26
Location: West Midlands,
United Kingdom

PostPosted: Wed Sep 30, 2009 10:34 pm Reply with quote

Cheers for the responses guys icon_smile.gif

Definately an Icos. Tanks in the roof, not sure on ballcock, didn't delve too deep. A large bath sized tank on it's side, as well as a small cistern sized tank beside it.

Pump speed was on 2/3, i put it up to 3/3 which has made no difference (can hear speed difference in pump though).

How do i check system has water in it? Bled all the radiaters etc, no air in there. How does the auto bypass valve work, and how should it be set?

Is the fact that the arrows on the mechanical valve plastic point in opposite directions to that on the pipes it's fitted to an issue?
Back to top
 Alert Moderators
pjblink

from United Kingdom

Joined: 16 Aug 2009
Posts: 26
Location: West Midlands,
United Kingdom

PostPosted: Wed Sep 30, 2009 11:06 pm Reply with quote

Video of boiler in action can be seen here:



And this is the mechanical valve:

Back to top
 Alert Moderators
gas4you

from United Kingdom

Joined: 23 Feb 2007
Posts: 17633
Location: Norfolk,
United Kingdom
Thanked: 756 times

PostPosted: Thu Oct 01, 2009 7:05 am Reply with quote

No circulation and the boiler is over heating.
Back to top
 Alert Moderators
davebgas

from United Kingdom

Joined: 09 Feb 2009
Posts: 2043
Location: London,
United Kingdom
Thanked: 254 times

PostPosted: Thu Oct 01, 2009 8:58 am Reply with quote

Check the pump is running ok
Back to top
 Alert Moderators
shambolic

from United Kingdom

Joined: 25 Aug 2008
Posts: 1528
Location: United Kingdom
Thanked: 407 times

PostPosted: Thu Oct 01, 2009 2:28 pm Reply with quote

Defo overheating either a blockage, airlock, or pump not working.
Advisable not to try and use as you may burst the heat exchanger !
Back to top
 Alert Moderators
izzy eckerslike

from United Kingdom

Joined: 26 Oct 2007
Posts: 79
Location: Worcestershire,
United Kingdom

PostPosted: Thu Oct 01, 2009 4:11 pm Reply with quote

Exactly what we had after our spanky new icos HE24 was fitted by warmfront, it only did it on hot water only not with heating on. The clonking lasted about 3 mintutes then all went silent

It is only air & sounds worse than it is but in our case after two visits they discovered it was the gate valve on the return pipe from the hot water cylinder closed off to much. Instantly cured by opening the valve a bit more
Back to top
 Alert Moderators
davebgas

from United Kingdom

Joined: 09 Feb 2009
Posts: 2043
Location: London,
United Kingdom
Thanked: 254 times

PostPosted: Thu Oct 01, 2009 4:18 pm Reply with quote

Do NOT assume it's just air!!! Check the pump!!! From the picture this is not a new ICOS as the user control is different. Listen to shambolic as he works for Ideal!!!
Back to top
 Alert Moderators
petit_pablo

from United Kingdom

Joined: 18 Nov 2007
Posts: 7240
Location: Lincolnshire,
United Kingdom
Thanked: 1229 times

PostPosted: Thu Oct 01, 2009 4:42 pm Reply with quote

When you bled the radiators did water come out forcibly / dribble out or no air or water?

There could well be a blockage in the cold feed if the water just dribbled out or nothing came out.

See its been abused by BG at somepoint judging by the stickers on boiler!
Back to top
 Alert Moderators
gas4you

from United Kingdom

Joined: 23 Feb 2007
Posts: 17633
Location: Norfolk,
United Kingdom
Thanked: 756 times

PostPosted: Thu Oct 01, 2009 6:55 pm Reply with quote

This is the original M3080
Back to top
 Alert Moderators
shambolic

from United Kingdom

Joined: 25 Aug 2008
Posts: 1528
Location: United Kingdom
Thanked: 407 times

PostPosted: Thu Oct 01, 2009 9:34 pm Reply with quote

As said by a couple of observant peeps on here this boiler is an m3080 original icos and is probably seven years old!!
(lasted this long FFS) Hope this satisfies you lot icon_lol.gif
But it will be an external fault of air, pump, or circulation probs but get someone to check as it could cause irreprable(sp) damage to boiler also get it checked and serviced including sump cleaned electrodes checke insulation panels condense checked etc if not yo could be in for more trouble icon_confused.gif icon_confused.gif
Back to top
The following user says thank you to shambolic for this useful post:
pjblink (1 Oct 2009)
 Alert Moderators
shambolic

from United Kingdom

Joined: 25 Aug 2008
Posts: 1528
Location: United Kingdom
Thanked: 407 times

PostPosted: Thu Oct 01, 2009 9:43 pm Reply with quote

izzy eckerslike wrote:
Exactly what we had after our spanky new icos HE24 was fitted by warmfront, it only did it on hot water only not with heating on. The clonking lasted about 3 mintutes then all went silent

It is only air & sounds worse than it is but in our case after two visits they discovered it was the gate valve on the return pipe from the hot water cylinder closed off to much. Instantly cured by opening the valve a bit more

Had the same today with a He 36 mexico fitted to a n old system with an oil fired boiler. installer left the pump and motorised valves on the return and also left the old 22 mm primaries!!!!
Cust has had them out 10 times in the last 10 months due to noise and other problems.
i went today and spent the time getting to know the system and more importantly getting to knwo the customers.
Now TBH this was not a boiler problem but it looked bad as fault only occured since our boiler fitted(no pros with old oil boiler)

On questioning cutomer they had a noise problem on and of and the installer came out to sort several times.
They have not had any noise since last installer call out but they also have had poor HW and no heat to lounge which has 2 fan heaters.
the installer had solved the noise problem by turning the boiler stat to 42 degrees!!!
Bingo no more overheating but **** all heat and hw!!!
I despair sometimes
so my advice was boiler ok But 36 kw through 22mm primaries disnae really work please read instructions
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2, 3  Next
Page 1 of 3

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Worcester bosch combi boiler pipes knocking, pressure drop.. 4 1100 Tue Dec 22, 2009 3:22 pm
Knocking/vibrating hot water pipes 2 5140 Sun Mar 04, 2007 10:07 pm
main water pipe knocking 8 100 Sat Dec 17, 2011 11:55 am
Pipes knocking when no water is running and boiler off !! 12 180 Wed Sep 14, 2011 8:46 am
Knocking noise whenturning on hot water - BG C1 combi boiler 9 1780 Fri Dec 07, 2007 5:37 pm


 