Joined: 07 Oct 2009 Posts: 4 Location: Lancashire, United Kingdom
|
Posted: Wed Oct 07, 2009 8:55 pm |
|
|
Hi - im trying to work out a problem with my central heating, the room thermostat (drayton RTS1) doesent switch off the heating, even if i turn it right down it has no effect. I can hear it clicking as it you turn it up and down but the heating remains on. I have tried replacing the room stat with the a new one - same make and model and the problem persists. The programmer is a Horstman C21 which replaced a Drayton LP241 about 2 years ok. It is a pumped system. I have noticed that if I remove the programmer from the wall completely and then replace it, it works for a while and then goes back to the same problem, I have checked the connections on the wiring and the contacts and i dont think this is the problem. My next thought is to try replacing the programmer but I was looking to see if anyone had any other thoughts before I spend my money.
Thanks |
|
bengasman

Joined: 28 Jan 2005 Posts: 26964 Location: London, United Kingdom Thanked: 2162 times
|
Posted: Wed Oct 07, 2009 8:59 pm |
|
|
Replacing the horstman with a decent brand would not be a bad idea. |
|
gassafeengineer

Joined: 06 Oct 2009 Posts: 1476 Location: Cumbria, United Kingdom Thanked: 174 times
|
Posted: Wed Oct 07, 2009 9:07 pm |
|
|
should be easy to fix
first you need to make sure you have 240V from your time clock CH ON to the roomstat then from your room stat (when stat is calling for heat) to the brown wire of the CH zone valve and you should now have 240 on grey or the orange wire of the zone valve (one of these will be to permanent live so will always have 240v and the other being the one to fire the boiler (switched live)
now with the heating demand off at the thermostat you should have 240 into your stat and 0v out of the stat leaving 0v to your brown wire and leaving 0v to either the orange or grey (depends on installers preference)
i think you will find in any circumstance you will have 240v on either grey or orange whicj indicates valve is stuck open and operating end switch permanently
hope this helps and isnt to confusing never was any good at writing descriptions |
|
doitall

Joined: 08 Jan 2005 Posts: 16488 Location: Bath, United Kingdom Thanked: 1097 times
|
Posted: Wed Oct 07, 2009 9:36 pm |
|
|
Should be easier than that
Microswitch sticking in an MV gets my vote. |
|
Chilie

Joined: 07 Oct 2009 Posts: 4 Location: Lancashire, United Kingdom
|
Posted: Sat Oct 10, 2009 8:03 pm |
|
|
Gents - thanks for all your ideas - I think i follow you with the wiring but im no electrician - I have a multimeter and the house is on circut breakers so i will have a fiddle and see if I can check the voltage without giving myself a shock!
Assuming one of the suggestions is correct and its either the micro switch or the valve - where do I find them - are we talking the gas valve inside the boiler? |
|
kevplumb

Joined: 18 May 2004 Posts: 23695 Location: Georgia, United States of America Thanked: 916 times
|
|