This is a puma 80 with permanent pilot. The heating can be on for hours without problem. Hot water can be drawn at full capacity without a problem. A little while AFTER drawing hot water when the tap has been shut is when the boiler locks out. Short bursts of hot water have no adverse effect, anywhere from one second to a couple of minutes. The problem appears only after a long shower. The system has been powerflushed and there is no sign of sludge or scale. The diverter valve has been checked and is clean and appears to work fine. The flowswitch and the micro switch have been checked and seem to work fine. Flow and return differential is about 12 degrees and all radiators heat up equally. There is no pressure loss (stays between 1 and 1.5 bar) in the heating system and no leaking taps. The fan, pcb, aav, prv and the overheat stat have been replaced and the system has sufficient inhibitor. The pilot assembly and thermocouple have been checked and work fine. The boiler has been serviced every year. The heating works fine with stat on high as well as low and on full capacity as well as rated down to minimum. Are there any secret parts that can fail in this boiler that are not listed in the manual? Lol.