Combi Boiler Low Pressure when cold, high pressure when hot.


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
Trebor2Go

from United Kingdom

Joined: 02 Dec 2009
Posts: 9
Location: United Kingdom

PostPosted: Wed Dec 02, 2009 7:15 pm Reply with quote

I have a Vaillant Turbomax Plus 828e.

All radiators are bled.

When the system is cold the bar pressure reads 0.8, but when running it climbs over the recommended 2.0 bar, reaching 2.2-2.3 bar, last year it never peaked above 1.5 when hot - any ideas why it should change this year.

Thanks
Trebor

http://www.imagesetting.com/


Last edited by Trebor2Go on Sun Feb 20, 2011 10:58 pm, edited 1 time in total
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 23673
Location: Georgia,
United States of America
Thanked: 918 times

PostPosted: Wed Dec 02, 2009 7:16 pm Reply with quote

expansion vessel needs recharging

see FAQ
Back to top
 Alert Moderators
Trebor2Go

from United Kingdom

Joined: 02 Dec 2009
Posts: 9
Location: United Kingdom

PostPosted: Wed Dec 02, 2009 7:26 pm Reply with quote

Ahh, is the 'expansion vessel' a green rubber bag you inflate slightly with a bicycle pump ?
Back to top
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 23673
Location: Georgia,
United States of America
Thanked: 918 times

PostPosted: Wed Dec 02, 2009 7:38 pm Reply with quote

no see here
Back to top
 Alert Moderators
Trebor2Go

from United Kingdom

Joined: 02 Dec 2009
Posts: 9
Location: United Kingdom

PostPosted: Wed Dec 02, 2009 7:53 pm Reply with quote

Hi, thanks for the reply, I remember now, a few years ago Vaillant instructing me to simply use my bike pump, and to let a bit of pressure out before hand.
Your FAQ suggests 'repressuring', - do I need to go through all that just to put a bit of pressure back in ?
Back to top
 Alert Moderators
MANDATE

from United Kingdom

Joined: 06 Mar 2003
Posts: 2288
Location: Manchester,
United Kingdom
Thanked: 128 times

PostPosted: Wed Dec 02, 2009 10:50 pm Reply with quote

[quote="Trebor2Go";p="1427617"] do I need to go through all that just to put a bit of pressure back in ?[/quote]
And what about the excess water? Where will it go?
Back to top
 Alert Moderators
Trebor2Go

from United Kingdom

Joined: 02 Dec 2009
Posts: 9
Location: United Kingdom

PostPosted: Thu Dec 03, 2009 9:32 am Reply with quote

OK, well I found someone had turned the heating temperature dial up to full, which I hadn't noticed, would this have caused the Pressure dial to read above 2.0 Bar ? the temp. dial is at the 3/4 position now.

I still investigated the Expansion/Pressure Vessel, when I pressed the 'tyre valve' in no water (apart from maybe some condensed moisture) came out, but also no air seemed to come out either though - should I have expected a hiss of air at all ?
With the system hot I connected a bicycle pump and pumped 5-10 times.
Now when running hot the bar pressure measures roughly 0.75 Bar.
When cold bar pressure is reading 0.25 Bar.

I'm confused, the systems not leaking (not that I know of) - so where has all that water/pressure gone since pumping the bike pump. I know the min cold pressure should be much higher than 0.25bar. The installation manual doesn't give any Min. Bar Values for cold, is it 1.1 Bar ??
Back to top
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 23673
Location: Georgia,
United States of America
Thanked: 918 times

PostPosted: Thu Dec 03, 2009 9:35 am Reply with quote

follow the link and repressurise it PROPERLY first

then see what happens icon_idea.gif icon_idea.gif
Back to top
 Alert Moderators
Trebor2Go

from United Kingdom

Joined: 02 Dec 2009
Posts: 9
Location: United Kingdom

PostPosted: Thu Dec 03, 2009 10:58 am Reply with quote

Thanks Kev,
If thats the procedure then I'll do it, let you know, mustn't forget my Fernox inhibitor, I've had some in the workshop for a few years, does it go off ?
Back to top
 Alert Moderators
MANDATE

from United Kingdom

Joined: 06 Mar 2003
Posts: 2288
Location: Manchester,
United Kingdom
Thanked: 128 times

PostPosted: Thu Dec 03, 2009 12:54 pm Reply with quote

The water won't have gone anywhere (unless you have a leak).
Water does not compress, air does!, You've pushed a bit more air in the air side and its pressure rises slightly. You've not created a larger air space for the excess volume of water, because you can't, until you remove some of the existing water.
The vessel is there to accommodate the extra volume as the water expands. The extra depends on the total volume of water in your system and the rise in temperature.
A system where the pressure starts at 1bar and rises to 2bar is normal. The problem arises when the higher pressure reaches 3bar which is when the pressure relief valve operates. So you would not want to start at 2bar and rise to 3bar.
Back to top
 Alert Moderators
Trebor2Go

from United Kingdom

Joined: 02 Dec 2009
Posts: 9
Location: United Kingdom

PostPosted: Fri Dec 04, 2009 9:07 am Reply with quote

I followed the procedure, much better, but I'm unsure of the pressure in the expansion vessel - its roughly 10psi, the system only seems to expand by 1 Bar when its running hot ... does that sound OK - or could I have pumped too much air in.
Back to top
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 23673
Location: Georgia,
United States of America
Thanked: 918 times

PostPosted: Fri Dec 04, 2009 9:12 am Reply with quote

sounds about right icon_wink.gif
Back to top
 Alert Moderators
Trebor2Go

from United Kingdom

Joined: 02 Dec 2009
Posts: 9
Location: United Kingdom

PostPosted: Fri Dec 04, 2009 10:07 am Reply with quote

Cheers Kev, last question, I've dropped about 20 litres out of the system (its got 8 rads in a Semi detached house) to do what was required, the system already had rust inhibitor in it, but I've only topped up with fresh water - should I put some more inhibitor in - or will it be OK as it is.
Back to top
 Alert Moderators
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 23673
Location: Georgia,
United States of America
Thanked: 918 times

PostPosted: Fri Dec 04, 2009 10:10 am Reply with quote

put some in you can't overdose it

unless you go really silly
Back to top
 Alert Moderators
Trebor2Go

from United Kingdom

Joined: 02 Dec 2009
Posts: 9
Location: United Kingdom

PostPosted: Fri Dec 04, 2009 10:31 am Reply with quote

Top tip ... will put some in. Cheers.

http://www.imagesetting.com/
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
High pressure cold supply - which boiler is best? 3 260 Fri Jan 16, 2009 5:26 pm
Gravity fed cold and high pressure hot - mixer tap? 3 60 Sun Jul 15, 2012 9:32 am
combi boiler - pressure gauge too high and overflowing 4 1940 Fri Mar 11, 2011 7:08 pm
Vaillant Combi Boiler -High Pressure? How get down? 11 38360 Sun Jun 11, 2006 3:21 pm
Combi Boiler with High Mains Water Pressure 2 360 Wed Feb 03, 2010 10:38 am


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.